Shop electrical plug height

Dustmaker Mike

Howdy all. Well I am about to start wiring my new shop I started last year. It is 16 x 20 on the back of the garage. I have a few questions about the electrical.

220 in the floor for the TS and 220 in the garage for the dust collector and air compressor. Maybe an extra 220 in a wall for?

How high would you put the 110 plugs from the floor?

How many on one 20 amp breaker? I was thinking 3 maybe 4

How many on the 20 foot wall?

How many on the 16 foot wall?

I plan on at least two plugs in the ceiling for the air filter one will be on a timer the other plug is for the fan in the heater both on there own breaker.

What else should I wire for?

Stero Internet intercom. The walls are all open right now

I am planing on putting compressed air in the walls also how high for the air drops?

Thanks Mike

Re: Shop electrical plug height

#2

Re: Shop electrical plug height

Jerry Gibbs

I would put the wall plugs about 4 1/2' so you can lean a 4 x 8 sheet on its side and still be below the plug.

Re: Shop electrical plug height

#3

Re: Shop electrical plug height

Jesse Cloud

Jerry's got it right. Don't put the outlets too low as they would prevent storing stuff and you would have to bend down a little, probably into cramped space.

The # and location of circuits depends totally on what equipment you are running and your plans/dreams for upgrades. I have a 220 each for DC, tablesaw, bandsaw, and jointer. Thinking about a planer upgrade that would need 220 as well. Yeah, you can share plugs, but its a PITA.

Remember amperage for lighting - it adds up.

Re: Shop electrical plug height

#4

Re: Shop electrical plug height

Galen Vetterick

Outlets for garage or shop should be 18" from the floor. They should be 6" above any bench height or counter you may have against the wall. No Code that I remember on this location unless there is update to handicaped requirements. I know our city requirement is the 18" for garage.

I'd put four on the 20 foot wall and three on the 16 unless you know the layout of your shop equipment and locate to suit.

The number of outlets on a 20 amp circuit depends on your equiment layout and amp draw of each. Code allows more in a home that what you do in a good shop knowing your power requirements and what machines you may operate at the same time.

I suggesst you split each outlet and put each half on a seperate circuit. More wiring but saves the extension cord to run two power tools near the same location.

Re: Shop electrical plug height

#5

bench receptacles

Bill Tindall

I like plugs dropped from the ceiling over my bench. It gets router cords and the like up and more out of the way. It think it best to plug machines in close to the floor. When in doubt put plugs low for it is then easy to raise them if desirable.

When I wired (in ceiling)I put a 18" loop of wire in between all the receptacles so that an additional drop could be made as needed. I have used almost ever one of them. It is said as a joke, but doubling what ever you think you need may not be excessive over time.

Re: Shop electrical plug height

#6

McKinneyMike

Re: bench receptacles

McKinneyMike

In my shop all outlets are positioned at 50" from the floor to the bottom of the outlet box. I have outlets ever 4 feet along any one wall, with doubles around my work bench area. I did not daisy chain outlets, rather I leap frog to every other outlet so that I do not have two adjacent outlets on the same circuit breakers. I placed 6 outlets per breaker. Lights are on their own breakers.

All wiring was 12/3 Romex and breakers are 20amp each. 220V lines to tablesaw, bandsaw, jointer and planer are all 10/3 Romex on 20 or 30amp breakers.

Re: Shop electrical plug height

#7

Outlets are cheap

Thomas Skaggs, Foothills of Mount Level

A good friend of mine gave me advice that was helpful. He said "hey....outlets are cheap...install lots of them". So most of my outlets are above the floor and have a partner above bench height.

Workshops evolve...outlet locations today may not be where you need them in the future. So having many around the room allow you to re-arrange the shop in the future and know that outlets will not be a constraint.

Tom

Re: Shop electrical plug height

#8

Ceiling Plugs

Al Goldstein

I agree with Bill on plugs in the ceiling. I have several over my bench.

My machine tools are on casters and are lined up along the walls. I have six ceiling plugs evenly distributed over the central area in my shop so I can plug in any machine tool no matter where it is without dripping over electrical wires.

Since I installed the ceiling plugs I have a lot of unused extension cords.

Re: Shop electrical plug height

#9

Re: Shop electrical plug height

Carol Reed, Strawberry, AZ

Hi, Mike,

My 2 cents.

I had to add an extra 220 for the lathe. What future tools can you envision?

Plugs in one shed went 54" off the floor and circuits were leapfrogged every 4 feet. Found that to be useless. Too many wound up behind something! in the new shed, they will be 4 plex boxes just under upper cabinets which will be french cleated to the walls. Each box will have two circuit, clearly marked. I marked the breaker number right on the outlet. I know what it is without even removing the cover. Stuff on the benches and counters won't cover them at that height and for open areas, you can lean stuff against the wall. At least one shouldl be near the door so an extension cord can be used outside.

So far I only have one 220 breaker. If I planned on an air compressor I'd put in too. As it si I am unlikely to run teh table saw and teh lathe at tehsame time. :)

How many you put on each wall depends what else is along the wall. I'd want a couple within easy reach of the bench(es) and a couple more wherever the assembly area winds up. Not fond of ceiling drops. I am too short. LOL!

Separate circuits for heaters, of course. And for air compressors. For anything that runs the same time as other tools.

Ton of lights. I mean, a ton of lights!

For audio, I'd go wireless. Or some outlets up really high to power audio equipment and clocks.

I would not put compressed air IN the walls. What a mess to find a leak - and they will happen. Not to mention drain drops for the air lines. Again the air drops would be located just under the upper cabinets for the same reason as the outlets. And one near the door.

As I said, my two cents and that only answers your specific questions.

Re: Shop electrical plug height

#10

Agree on the air...

John in NM

Unless you're going to put in type K copper, run the compressed air outside the wall. There's just something about air pipes, they're dying to leak :D

Re: Shop electrical plug height

#11

Re: Shop electrical plug height

Howard Norman

My first shop, one side of a two car garage, had 110 outlets every five feet because the wiring was done using thinwall conduit which comes in 10' lengths. There were two 110 v circuits along the wall. There were additional outlets, included by the builder along the end wall. The outlets were leapfrogged so that no two adjacent outlets were on the same circuit. In the twenty years that I used that shop I always had enough 110 v outlets. In y current shops, one upstairs and one in the basement, I have decreased the distance to about four feet between outlets. This time I used PVC conduit. I have always placed shop outlets at about 50-52" above floor level I have always used #12 wiring with 20 amp breakers for outlet circuits for 110v/

Re: Shop electrical plug height

#12

Re: Shop electrical plug height

Gary Camp Bend, Oregon

I really agree with Carol on height, and fourplex boxes, with 2 seperate ckts in each box, clearly marked @ 4 feet apart. and near the door or even a couple daisy chained through the outside wall.

glc

Re: Shop electrical plug height

#13

Re: Additional Thoughts on Outlets

Barry

The National Electric Code used to specify no more than 6' between outlets along walls. I'd use that as an absolute bare minimum. Above a built-in workbench, I'd put outlets on every other stud. It's a PIA to have to plug and un-plug cords. Grinders, stationary belt sanders, router tables all need an outlet. In my 24' X 24' garage/shop, I have a 220 v on each wall, each on a separate circuit. If I were doing it again, I'd put two (2) on each wall. I'm already sharing a 220 v for my tablesaw/lathe and air compressor/planer. Just remember it's a lot easier to do it now than to retro-fit later. Outlets are relatively cheap, the benefits of having too many.......priceless!

Re: Shop electrical plug height

#14

We should all have you up to...

Galen Vetterick

a 400 Amp Main Breaker Distribution Panel by now!!!

Oh and dont' forget the fridge for the cold beer!

Re: Shop electrical plug height

#15

Re: Additional Thoughts on Outlets

FredD

The history behind the 6 foot rule for residential outlets was because lamps come with just a six foot power cord.

A couple of thoughts aboput outlets in a shop .

First and foremost are the hazards associated with "cheap outlets: , don't use them.

For the boxes , use steel and for the outlet covers , use steel.

For the outlet height , the suggestions by a couple for posters to keep them above four feet for panel clearance is a good idea. For the 120 Volt outlets , either a panel GFIC or individual ones that protect all of the outlets downstream in a circuit . especially if you have some cheaply made radio's or small appliances that have a current leak.

FredD

Re: Shop electrical plug height

#16

Re: Shop electrical plug height

Barry Irby

I agree with those who want you to put them above the four foot level to allow for leaning a sheet of plywood on the wall.

I have my outlets along the front of what passes for a work bench. Much better for the cord to hang down in front and not come from behind the bench. I think some dangling form the ceiling might be a good idea, but I don't have them.

The local code has always been enforced to have outlets every 12' because cords were traditionally 6' long. Never heard of anyone putting residential outlets every 6'. However, in a shop I think every four or five feet would be great. I also like the idea of using double boxes and you can use 12/3 with Ground to run two separate circuits in the boxes.

There is nothing in the residential code that specifies how many outlets you may have per circuit. It used to be that outlets were counted as 1 1/2 amps each or three amps for a duplex receptacle. Now they tell me that has been dropped from the code and you can have as many as you want. Think that through and provide several different circuits to avoid overloading any of them. But, putting a few outlets in your favorite part of the shop on one circuit and then putting a bunch in other places you are unlikely to use is an invitation to over load the favorites. Mix'em up.

I moved my Air Compressor and DC into a little exterior closet. Its great, except there is only one outlet and they share it. If I fire off the DC just as the compressor cuts in and then start a tool that is on the same circuit it probably trips the breaker. Its the startup surge. If I let any of them run up to speed first, it does not happen. There is a slow leak in compressor circuit and I turn the breaker off when I leave the shop. Not a good practice. I should put in a switch. If I turn on the breaker, flip on the DC and start a tool all in one motion, that's when the breaker may trip. I often "learn" the breaker is off when I try to start the DC and nothing happens. If I leave the DC on and flip the breaker that usually starts the Air Compressor because it has leaked down. (So, I need a switch and to find that leak.)

Re: Shop electrical plug height

#17

Re: Additional Thoughts on Outlets

Barry

One outlet every 6' is not nearly enough, in my opinion. Using cheap outlets is false economy. I didn't use outlets that were especially cheap when I built my garage over 30 years ago, but I replaced them all last summer. Several of them just fell apart in my hands. I used better quality this time. As for the cover plates, I didn't use metal, but the plastic ones are very tough. The boxes are metal.

Re: Shop electrical plug height

#18

Re: Shop electrical plug height

Bill Turpin in WNC mountains

Do not use the outlets with spring-loaded wire grab. Use the ones that require a screwdriver! Make sure that NO lights are on an equipment circuit. You do not want to be in the dark after the tablesaw trips the breaker with an overload. Put in TWICE as many outlets as you think you need.

Pipe all air lines with a slope downhill to a drain port. Take air taps off the top of the main pipe.

Have a mix of incandescent and flourescent fixtures. Install a telephone tap if you still use a landline. Install several outside outlets. Check code to see if ALL outlets must be groundfault. Outlets in floor are serious sawdust traps. Deddicated spot tools with a 90� plug may need the outlet installed upside down (ground on top) to make wire hang properly. Use a switch with enclosed timer so that you can walk to house before lights go out. An outlet strip on the side of workbench can be very handy. Be sure your sharpening area is OVER lighted.

Re: Shop electrical plug height

#19

Thanks All keep them coming

Dustmaker Mike

I am off to talk to the inspector this week and will be buying the material this weekend. I will have an electrican hook up to the main panel and I will do the rest.

What else should be in the wall before I close it. I will be using spary foam for insulating the area so I will also run a few empty 3/4 PVC pipes to allow me to run wha ever else after the walls are done. I will get some pic's up this week or next I hope.

Re: Shop electrical plug height

#20

Re: Thanks All keep them coming

del schisler

I didn't read all the post's. Did you run a phone wire ? Or a coax wire. You never know you may not have a use for it now but I have both run in my shop. Maybe some day want a cooler and tv. who know's cold beer after the work and may be some tv?? May surve as a get a way ?

Re: Shop electrical plug height

#21

Re: Thanks All keep them coming

Frank Grambo

Mike,

I assume the spray foam you are talking about will cover the sheathing and will almost fill out the 2x's. Is that foam something a private person can buy and apply or is it reserved for "other folks" ?

Frank on Chestnut Hill

Re: Shop electrical plug height

#22

Re: Thanks All keep them coming

Larry in NW OHIO

Mike One thing I just thought of when I wired my shop a couple years ago, like a few said, put outlets on the wall in back of where the workbench will be. Make sure they are about 6" higher than the bench and when you put in the workbench you can run a wire from one of the wall plugs and put plugs at the front on your bench and tie the two or more together. Make them handy. Larry

Re: Shop electrical plug height

#23

Foam *LINK*

Dustmaker Mike

I am going to have a company come and do it I think. I will wait and see the cost. If it is to much then I will do it myself. There is a company in NJ called Tiger Foam that will sell you the kits to do this yourself. I have already sprayed foamed the area around the rim joist in my house and it makes a big differance. If th ewalls are open like mine thne it is an easy process if they are closed then it takes a bit more work. I have figured out the SQ footage I need to complete the job as well as cost of meterial so if the local company is close to that number then they have the job if they are way high then I have a bit more work on my plate.

Just a Happy customer


Tiger Foam

Re: Shop electrical plug height

#24

Re: Thanks All keep them coming

Larry Clinton Sr.

Mike I built a 30' X 30' shop about 5 years ago - before I retired. My sons and I built it, I had worked as an Engineer for about 40 years and contracted on the side so the only outside labor used was for the concrete floor finish. As has been mentioned, outlets are cheap. I installed a 100 amp ITE breaker box (the largest I could find) fed underground from my houses 200 amp entrance.

I installed an outlet 4' 6" above the floor on every other stud on all walls (I used 2X6 studs on 16 center) with about 4 outlets on a breaker. This height allows you to stack plywood without covering the outlets and is not a bad height for over the bench outlets. I also installed 220 outlets for my Air compressor, welder and dust collector system. I installed extra 220 outlets at the corners of each wall (2 per corner) and one in the center of each wall for future tools. As I upgraded the tools I really needed the 220's as my new planer, joiner, Unisaw, Lathe are all 220V. All my 220V outlets are 30 amp except a 50 amp for the welder. I installed one outlet on the ceiling for the garage door opener, however I should have added a second as I changed the opener to an "I-drive" which is powered directly over the door itself. I installed 4 rows of outlets in the ceiling which are switched by 4 switches located at the entry door. My florescent lights are suspended by chain and plugged into the ceiling outlets which makes it real easy to replace one. I then installed 5 or 6 incandescent porcelain fixtures on the ceiling with 3 way switches at the entry and the garage door. I really wish I had added outlets located right beside the garage and entry doors for those times I want to clean up tools (sanders etc) right outside the doors. When I installed the wall outlets, I staggered the feeds so that a breaker didn't feed all the outlets in a row over the benches. This allows you to plug in tools next to each other without overloading the breaker. I purchased a case of outlet boxes (144) and a few extra. I did use the cheapest outlets as I figure most won't be used much and the ones that do wear out are very easy to replace with high quality outlets. I haven't had to replace any yet. I have always left a "loop" of wire over ever outlet so that I can pull in at least a foot of new wire if an outlet overheats and damages the wire. I leave at least 6" of stripped wire in every box making it easy to install and replace outlets and switches. I used every breaker opening in my entrance box. - I did install the box in a raised portion of the wall so I can add a secondary box if needed for more circuits. I have a second story in my shop which holds my furnace/central air and wood storage. I have a drop ladder with a 3 way light switch down stairs and upstairs. The lighting is installed like the lower floor. I have only 3 or four outlets up there as it isn't a work area (with a dedicated line to my furnace). I did intend to install outside outlets (bought them - but never installed them). I may end up installing some later although it is much harder as the entire shop is finished in drywall. I used 12/2 with ground for all 120V wiring with 20 amp breakers (using a 20A GFI outlet at the start of each feed line) and 10/3 with ground and 30 amp breakers for all 220V wiring (except the welder). My idea of wiring the shop is that if you question whether you may want an outlet at a location - INSTALL ONE - The cost is minor compared to the problems you will have if you need to add one after the shop is finished. All my machines are on casters except the dust system and lathe so I can configure the shop for the projects I am doing ( and move the woodworking tools out of the way if we need to work on a vehicle or other project). So far the layout has worked well.

Re: Shop electrical plug height

#25

Re: Whoops forgot one thing.

Larry Clinton Sr.

I also installed a light switch and circuit at the entrance door for an outside security light (motion sensor type), I would have installed one at the garage door except it is already lit by a motion sensor light mounted on the house. The one at the entry door makes it convenient as it comes on when you leave the shop at night and hopefully it is a deterent to those who covet my tools.