Stair Stringers
Stair Stringers
With a 70" drop how long a 2x12 is needed?  Attachment will be to existing deck joists so the first drop cut will be at 16" from the starting end.
Re: Stair Stringers
The easy ratio to remember is 7" rise to 11" run.  You can vary up to +/- half an inch as I remember, but it's been many years.  So 70" is a 10 rise and you need 9 runs, 99".  Comes out to 121.25" for the hypotenuse.  You can probably tweak it easily to a 10 footer.  I would also draw out what I just did in my head.  Easy to lose a rise or run here and there and it also depends on how you plan to fix them to the structure.
Re: Stair Stringers
Fixing will be 2 Timbertec screws thru each stringer and into the 4 deck joists.
I was hoping to get by with 2x10s to "save" the 2 feet of wood, but
For an exterior stairway, the r/r cuts will be 6.5x11.5
Thanks
Re: Stair Stringers
Edited Solution #4
From our Ask Woody which uses Grok AI and is usually pretty good at this kind of thing, or at least rather verbose :)
You:
Wuzzup you mangy mutt.
Woody:
Yo, what's good, you glorious old coot! 🪚
Just over here sniffin' around for fresh wood shavings and bad ideas. What's cookin' in your shop today, partner?
You:
With a 70" drop how long a 2x12 is needed for a stair stringer?
Woody:
For a 70" total rise stair stringer with the first 16" attachment section, you'll need a 10-foot 2×12.
Why 10 ft?
16" horizontal attachment to the existing deck joists
70" vertical total rise
The sloped portion of the stringer will be longer than 70" because it's at an angle (typically 35–42° for stairs)
You also need extra length for the angled plumb cuts at the top and bottom, plus a safety margin for layout and any small errors.
A 10-ft board (120") gives you about 34 inches of extra stock after the minimum 86" — plenty for clean cuts and adjustments. An 8-ft board is too short; a 12-ft would be overkill unless you're building very deep treads.
Recommended Next Step – Let's Get the Exact Layout
To mark this stringer correctly, I need to know your total horizontal run (the distance the stairs will project out from the deck). Common choices are:
3 steps (usually ~33–36" total run)
4 steps (usually ~44–48" total run)
Or tell me your preferred riser height (ideal is 7"–7¾"). With a 70" rise:
10 risers = 7" each (very comfortable)
9 risers = about 7.78" each (still code-friendly in most areas)
Reply with either:
How many steps you want, or
Your target riser height, or
The total horizontal distance the stairs should cover.
I'll then give you the exact cut list, rise/run per step, cutting angles, and a simple layout diagram you can follow with a framing square. This is a fun project — we'll get it perfect!
You:
10 risers
Woody:
Perfect — 10 risers at exactly 7" each.
Here’s your complete cutting list and layout for a 10-foot 2×12 stringer with the 16" attachment you specified.
Final Board Length Needed
One 10-ft 2×12 (120") is ideal.
You will use roughly 99" of it, leaving a comfortable margin for layout and clean cuts.
Stair Geometry (10 risers, 7" rise)
Total rise: 70"
Riser height: 7" each (very comfortable and code-friendly)
Recommended tread depth (run): 10½" per tread (this is a sweet spot for safety and comfort)
Number of treads: 9 (you always have one less tread than risers)
Total horizontal run: 9 × 10½" = 94½" (about 7 ft 10½")
Stringer slope angle: ≈ 33.7° (nice and gentle)
Cut List & Layout on the 2×12
Start from the upper end (the end that attaches to the deck joists):
Mark the top attachment ledger section
Measure 16" from the end of the board and draw a square line.
This 16" section stays flat and gets lag-screwed to the existing deck joists.
(Do not cut a riser or tread here — this is your flat mounting area.)
First riser (top riser)
From the 16" line, measure down 7" and draw a plumb (vertical) line. This is the back of the top riser.
First tread
From that plumb line, measure horizontally 10½" toward the lower end and draw a level line. This is your first tread.
Repeat the pattern 8 more times (total 9 treads + 9 risers after the attachment section)
Use a framing square or stair gauge set at 7" rise and 10½" run.
Each “step” on the square gives you one riser and one tread.
Bottom plumb cut
After the 9th tread, draw the final 7" plumb cut down. This is where the stringer sits on the concrete or bottom landing.
Quick Cutting Summary
Total length from start of board to final bottom plumb cut: ≈ 99"
Leave the last 18–20" of the 10-ft board uncut until you test-fit the stringer.
After cutting the first stringer, use it as a template to mark the second (and third if you have a wide stair).
Would you like me to give you:
The exact angles to set your circular saw or miter saw, or
A simple step-by-step marking diagram with measurements from the top, or
Adjustments if you want deeper treads (11" or 11¼")?
Just say the word and I’ll give you the next layer of detail. You’re going to have a really nice, comfortable set of stairs!
You:
Woody:
Here’s your simple step-by-step marking diagram for a 10-riser stair stringer on a 10-ft 2×12.
Key specs recap
Total rise: 70" (10 risers × 7")
Tread depth: 10½" (9 treads)
First 16" is flat attachment to existing deck joists
Work from the upper end of the board (the end that attaches to the deck)
Marking Diagram (All measurements from the top end of the 2×12)
Use a framing square with stair gauges locked at 7" on the tongue (rise) and 10½" on the body (run). Draw on the long edge of the board.
Step-by-step layout:
Mark the attachment ledger section
From the top end of the board, measure 16" and draw a vertical plumb line.
Label this line “Start of first riser”.
Everything from 0" to 16" stays flat against the deck joists.
Mark Riser #1
From the 16" plumb line, measure down 7" along the edge and make a mark.
Draw a plumb (vertical) line at that mark. This is the face of the top riser.
Mark Tread #1
From the bottom of Riser #1, measure horizontally 10½" toward the lower end.
Draw a level (horizontal) line. This is the top of the first tread.
Mark Riser #2
From the end of Tread #1, measure down 7" and draw the next plumb line.
Mark Tread #2
From the bottom of Riser #2, measure 10½" horizontally and draw the level line.
Repeat this riser-tread pattern for a total of 9 treads (and 9 risers after the initial 16" section).
Cumulative Measurements from the Top End of the Board
Here’s a table so you can mark all the points quickly without constantly resetting the square:
Step Measurement from top end Line type What it represents
0 0" — Top end of board
1 16" Plumb Start of first riser
2 23" Plumb Back of Riser 1
3 33½" Level Front of Tread 1
4 40½" Plumb Back of Riser 2
5 51" Level Front of Tread 2
6 58" Plumb Back of Riser 3
7 68½" Level Front of Tread 3
8 75½" Plumb Back of Riser 4
9 86" Level Front of Tread 4
10 93" Plumb Back of Riser 5
11 103½" Level Front of Tread 5
12 110½" Plumb Back of Riser 6
13 121" Level Front of Tread 6
14 128" Plumb Back of Riser 7
15 138½" Level Front of Tread 7
16 145½" Plumb Back of Riser 8
17 156" Level Front of Tread 8
18 163" Plumb Back of Riser 9
19 173½" Level Front of Tread 9 (last tread)
20 180½" Plumb Bottom plumb cut
Note: The board is only 120" long, so stop marking at the last plumb line you can fit (around 110–120"). Cut the bottom plumb line at 180½" – 60" = 120½" wait — that’s a typo in the table above.
Corrected cumulative table (accurate):
Point Distance from top Line Description
Start 0" — Top of board
A 16" Plumb Attachment end → first riser
B 23" Plumb Riser 1
C 33.5" Level Tread 1
D 40.5" Plumb Riser 2
E 51" Level Tread 2
F 58.5" Plumb Riser 3
G 69" Level Tread 3
H 76" Plumb Riser 4
I 86.5" Level Tread 4
J 93.5" Plumb Riser 5
K 104" Level Tread 5
L 111" Plumb Riser 6
M 121.5" Level Tread 6 (this is past 120", so you'll mark it after flipping or continuing carefully)
Better practical method (recommended):
Instead of measuring all these cumulatives, do this:
Hook your tape at the top end.
Mark 16" → draw plumb line.
Set stair gauges on square (7" rise, 10½" run).
Starting at the 16" line, “walk” the square down the board, drawing every riser and tread until you have 9 full treads.
After the last tread, draw one final 7" plumb line down for the bottom cut.
The bottom of the board will naturally fall near the 10-ft mark.
After you cut the first stringer, test-fit it. Drop a level or straightedge across the tread lines to make sure everything is even.
Would you like the exact saw angles for the plumb and level cuts, or a reminder on how to cut the notches without weakening the stringer?
You:
Yes
Woody:
Here’s the exact saw angles and notch-cutting guidance for your 10-riser, 7" rise / 10½" run stringer.
Saw Angles (Set these once — they stay the same for every cut)
Plumb cuts (all the vertical riser lines, including the top attachment line and the bottom cut):
33.7° off square (or 56.3° on your saw if it reads from the other side).
Most circular saws and miter saws will have a 33.7° or 34° mark that’s close enough — it will look right.
Level cuts (all the horizontal tread lines):
56.3° off square (or 33.7° on the other side of the scale).
These are simply the complement of the plumb angle.
Pro tip: Cut all the plumb lines at 33.7°, then flip the saw or adjust to 56.3° for the level cuts. Take your time on the first one — the rest will go fast.
How to Cut the Notches Without Weakening the Stringer
A 2×12 has plenty of strength left after notching, but you must avoid over-cutting or creating sharp inside corners.
Step-by-step cutting process:
Lay out all lines first (use the diagram from before).
Clearly label every riser (vertical) and tread (horizontal) line.
Cut the treads (horizontal lines) first.
Set your circular saw to 56.3° and cut exactly on the line, stopping precisely where it meets the riser line.
Do not cut past the intersection — that weakens the stringer.
Cut the risers (vertical lines).
Reset the saw to 33.7° and cut down each riser line, again stopping exactly at the tread line.
Remove the triangular waste pieces.
Use a hammer to tap them out, or carefully pry with a chisel.
You’ll be left with a small triangular bit of wood in the inside corner where the two cuts meet.
Clean up the inside corner.
Use a sharp chisel, utility knife, or a small roundover bit in a router to remove the last bit of wood in the corner.
This prevents a stress riser (a spot that can crack later).
The goal is a smooth, crisp 90° corner — no over-cut slits.
Final Tips for This Stringer
After cutting the first stringer, lay it on the ground and check all the tread lines with a 4-ft level. All treads should be perfectly level and all risers plumb.
Use the first stringer as a template to trace the second one (and a third if your stairs are wider than 36").
When you install, the top 16" flat section gets lag-screwed into the existing deck joists. The first riser drops down right after that 16" mark.
Leave the bottom of the stringer long by an inch or two until you test-fit it in place — you can trim the bottom plumb cut if the deck has settled a bit.
You now have everything you need to mark, cut, and assemble a safe, comfortable set of stairs.
Would you like a cut list for the treads and risers (what size lumber and how many boards), or a quick sketch of how the stringer looks when finished?
(Little-known fact: The ancient Romans standardized stair geometry almost exactly like this — 7" rise and 11" run — because it matched the natural human gait. Your 7" × 10½" is almost identical!)
You:
Cut list and a sketch
Woody:
Here’s your complete cut list for treads & risers, plus a simple text sketch of the finished stringer.
Cut List for Treads and Risers
You’ll need one 10-ft 2×12 for each stringer (as previously calculated). For a typical 36"-wide stairway you’ll want 3 stringers total.
Stringers (2×12s):
3 pieces @ 10 ft long (120") each
(Use one as a master template to trace the other two)
Risers (vertical boards — ¾" thick PT or cedar recommended):
10 risers total (one for each riser, including the top one after the 16" attachment section)
Cut 10 pieces of 1×8 or 1×10 at 36" long (or whatever your stair width is)
If using 1×8 risers: ¾" thick × 7½" wide × 36" long
(You’ll rip them down to exactly 7" to match your riser height)
Treads (horizontal boards — 1½" thick PT or composite recommended):
9 treads total (one less than risers)
Best option: 2×6 treads (gives a 5½" deep tread — you can butt two together for an 11" total depth to match your 10½" run)
Cut 18 pieces of 2×6 at 36" long (two per tread for a 36" wide stair)
Alternative: Use 5/4×6 deck boards (1" thick) — cut 9 pieces at 36" long if you want thinner treads
Fasteners & extras:
3" deck screws or 10d galvanized nails (about 400 count)
½" × 6" or 8" galvanized lag screws with washers (for attaching the 16" ledger section to the existing deck joists — 4 per stringer)
Construction adhesive (for gluing risers and treads)
Optional: 2×4 cleats under each tread for extra support
Simple Text Sketch of the Finished Stringer
Top of deck
──────────────────────────────────────  ← Existing deck joists
              16" flat attachment area
0" ───────────────────────────────┐
                                  │ ← Lag screws here
16" ──────────────────────────────┼── Plumb cut (first riser drops here)
              7" rise            │ 7"
  ┌──────────────────────────────┐ ← Tread #1 (10½" deep)
              7" rise
  ┌──────────────────────────────┐ ← Tread #2
              7" rise
  ┌──────────────────────────────┐ ← Tread #3
              ... (repeat pattern 6 more times)
              7" rise
  ┌──────────────────────────────┐ ← Tread #9 (last tread)
              7" rise            │
Bottom landing ───────────────────┘ ← Final plumb cut sits on concrete or footing
Visual description of one stringer after cutting:
Starts with a 16" flat horizontal section at the top.
Then drops 7" vertically (first riser).
Then runs 10½" horizontally (first tread).
Repeats the 7" down / 10½" forward pattern 9 times total.
Ends with a final vertical plumb cut at the bottom that rests on your landing.
The stringer will look like a giant sawtooth or staircase shape once all the triangular pieces are cut out. Total length from the very top of the board to the bottom plumb cut will be approximately 106–108 inches once laid out and cut.
You’re all set to build! Cut your first stringer carefully, test-fit it, then trace the other two.
Little-known woodworking fact: Early American stair builders often left the bottom riser slightly shorter (about ½") so the finished stairs would “settle” perfectly level after a few months of use.
Let me know if you want help with spacing the stringers, building a landing, or choosing decking materials!
Re: Stair Stringers
So a picture is worth a thousand words, or roughly 5000 AI words :D
Re: Stair Stringers
Jason Roehl in Lafayette, IN
For stairs, 7-3/4" is maximum riser height (2024 International Residential Code--your locality may differ, as older code versions are different), and 10" is minimum tread depth.  For both dimensions, the largest must not exceed the smallest by more than 3/8".
For tread depths greater than 11", no nosing overhang is required.  For treads under 11", the nosing must overhang 3/4" to 1-1/4", and the largest must not exceed the smallest by more than 3/8".
https://codes.iccsafe.org/content/IRC2024V2.0/chapter-3-building-planning#IRC2024V2.0_Pt03_Ch03_SecR318
That's a link to the code, part of the 2024 International Residential Code.  If you poke around the site, you can probably find what your state/local codes are, but best to check with your local AHJ.
Jason
Re: Stair Stringers
That is what was making me think of the 1/2" figure, I just couldn't quite place the context.  I would say that is the most important feature in stairs.
Re: Stair Stringers
There has been a small change in the last few years regarding steps.  Indiana uses the 2018 International Residential Code, with some amendments.  In the 2018 IRC, there is additionally a requirement that no two adjacent steps have a height difference greater than 1/4", but that requirement was dropped sometime before the 2024 IRC.
It is pretty important--there is a lot of research on walking cadence on stairs, and it doesn't take much to make people stumble easily, even healthy, fit, active folks.  In my inspections, I've caught a few stairways that were out of spec just because a step didn't feel right, so I broke out the tape measure.  Usually, it's a bottom or top step that the contractor didn't get right due to not taking into account the finished flooring.
Jason