Powermatic 3520 208 single or three phase opinions

Posts

Powermatic 3520 208 single or three phase opinions

#1

Powermatic 3520 208 single or three phase opinions

walta

According to the label on the lathe it is very flexible.

200-240 Volts 1 or 3 Phase your choice.

My concern is at the KC symposium some of the lathes performance was noticeable weaker when feed 208 single phase.

Any Powermatic 3520 users feeding it 208 single phase?

Walt

Re: Powermatic 3520 208 single or three phase opinions

#2

Re: Powermatic 3520 208 single or three phase opin

john lucas

I didn't know you could run it on 3 phase. It is a 3 phase motor but the inverter takes single phase in and converts it to 3 phase. Maybe the new ones are wired differently.

Re: Powermatic 3520 208 single or three phase opinions

#3

Re: Powermatic 3520 208 single or three phase opin

Dick Coers

I thought most everyone fed it single phase. Nearly all VFDs will accept single or 3 phase input.

Re: Powermatic 3520 208 single or three phase opinions

#4

Do you even have a 3 phase feed???

Chuck Jones - West Tennessee

I sure don't where I live. Checked into it a few years ago and the utility company said they would be glad to run 3 phase to my farm for $60,000. I told them I was just joking.

Re: Powermatic 3520 208 single or three phase opinions

#5

Re: Powermatic 3520 208 single or three phase opin

Philip Duffy

My original USA made is run on 1ph, and has done so for over 20 years without an hesitation on need for power.

Re: Powermatic 3520 208 single or three phase opinions

#6

Re: Powermatic 3520 208 single or three phase opin

Bill Turpin in WNC mountains

I would think that the real problem was LOW voltage. Homes are commonly fed with 208v 1 phase. This works well with modern motors. Take the temporary wiring at symposiums and perhaps too many machines on one circuit the voltage starts to drop. If voltage drops 10%, the motor drops out also. My PM, purchased in 2009, 70' from the panel, will take your arm off at the elbow. The drop is #6, aluminum, that is what I already owned! Unless you are in a commercial power district you will not get 3ph at a reasonable price. Reasonable would still be 2 to 3 grand plus! As our public schools shut down their shop programs, 3 phase machines were available. They sold for pennies because they were 3phase.

Re: Powermatic 3520 208 single or three phase opinions

#7

Re: Powermatic 3520 208 single or three phase opin

Ron Bauer

Phase converters are available if one must have 3 PH at the motor without using a VFD that is fed with single PH. The best are rotary but are pricy in the 3 HP range. You can use static (cheaper) but they must be oversized because they start the motor on three legs then basically run in single phase on only two legs.

Re: Powermatic 3520 208 single or three phase opinions

#8

Dennis in Southern Oregon

Re: Powermatic 3520 208 single or three phase opin

Dennis in Southern Oregon

There seems to be a bit of confusion here. 208 volts is the voltage between any one phase to neutral of a 240V three-phase feed. It normally would not be available in any other context. With single-phase service you normally would have available only 120V or 240V.

Re: Powermatic 3520 208 single or three phase opinions

#9

Jesper, Denmark

Re: Rather good summary......

Jesper, Denmark

http://en.wikipedia.org/wiki/Three-phase_electric_power

Typical supply to US domestic consumers is in reality two phase ¨220 volt phase to phase and around 130 volt phase to neutral/common. The neutral is usually grounded at the entry and/or transformer.

Modern EU practice is to supply three phase 400 volt, which provides ¨230 volt phase to neutral, which is also grounded both at the entry and the transformer. Distribution is typically 10 kV mast mounted to local transformers and underground loal distribution at 400 volt.