My new shop in my new home in Portland doesn't have 220 wiring. My 2 hp Oneway requires it. My question....what size wire should be used between the breaker box and the shop outlet. It'll be about a 50 ft. run.
From what I know what determines the awg of copper electrical wire is not the Voltage but the amperes. 14AWG Carries 15 Amp, 12 carries 20 amp, 10 Awg is rated for 30 Amp,110 or 220 does not matter. Usually the minimun Awg used in a 220 circuit is 12 Awg. 220 can go a much longer way without a drop in Voltage compared to 110V.
I wish it could be like in Europe where there is anly 230V.
I would go for 10 gauge. The differences in cost for various wire sizes are trivial compared to all the other costs. However, wire larger than 10 gauge is a bear to work with in small boxes.
I pulled over 6 gauge wire (from a 60 amp breaker), which went into a sub-panel with 2 each 20 amp 110 runs with 12 outlets, one 20 amp 220 run with a single outlet and one 20 @ 220V heater
All my 110 outlets are actual 15/20 amp outlets (not 15 amp like most home ones).
I've never popped a breaker, even when we have been running the following equipment simultaneously (like today)
* DC (1 hp Delta 110v)
* Band-saw (2HP Grizzly 220V)
* Jet 1220 (1HP 110V)
* 8 @ 80 watt double-tube 4 ft lights.
* radio
I'm certain the garage refer and freezer cycled at least once during the day.
I doubt you would ever regret serious wiring to the shop.
Most EU houses are supplied with three phase current as standard, so 220 volt single phase and 380/400 volt three phase, which is really handy for loads largr than 1 HP.
On the other hand, I miss the 60 Hertz, which is providing better speed ranges for 2 and 4 pole motors.
Oneway says on their 2400 series page near bottom that a 25A breaker should be used with 2 or 3HP lathes so they don't trip out under prolonged heavy cuts where the VFD may supply extra current to the motor.
In a normal (I think in a truly dedicated, intermittent load circuit the breaker size can be increased for smaller wire) case a 25A breaker would dictate #10 wire and you could even use a 30A breaker.
Unless you really like long, hogging cuts, I'd bet you'd get by with #12 and a 20A breaker but the incremental cost of the wire isn't worth running the risk of needing to do it over and you also would have a 30A, 240V line into the shop for future expansion.
Edit: I have a 2HP 20" General with VFD and only run it off a 15A, 240V circuit and have never tripped the breaker. Do some pretty good cuts but usually on green wood only.
Wally, I have a 2 HP Stubby lathe. When I installed electricity 15 years ago, I ran #12 wire on a 20A, 220V circuit. I have nevr tripped the breaker due to overload. Wire run is about 40 feet.
A year or so ago I measured the line current drawn by the 2 HP motor on my PM 3520 which operates at 220 V. For the test, I mounted a 12" diameter dry bowl blank and made a cut with a 5/8" bowl gouge.
With normal cutting, throwing fairly long strings of shavings, the current was in the 3 to 4 amp range. Only when I made the heaviest cut I could manage would the current go up to as high as 5 amps. When the lathe was running free, the current was in the range of 1 amp.
The calculated current for a 2 HP motor operating at 75% efficiency on 220V is about 9 amps. Based on my observations, I believe the current requirement is often overstated.
I used AWG #12 to run the power to my lathe, a distance of at least 35 feet. It has worked well. ~Doc
The breaker is there to protect the wiring. The NEC determines what amperage is safe to run in particular wire size, based on number of wires in the conduit or cable etc.
So if a 10 AWG wire is OK for 25 Amps, then the breaker must be 25 Amps or smaller. You must not install a larger rated breaker without also using large wire size.
I run an Agazzani band saw and a Vicmarc VL 300, both 3HP (2200 kW) on two circuits with a 220V 20 Amp breaker. Never a problem. Their motors have a soft start like almost all good machines so very little surge.
Current was measured with a wrap-around meter on one line.
The amps do not add. At a certain instant, the current that is flowing toward the lathe on one line is flowing away from the lathe on the other, in an electrical "circle."
The lathe manual will tell you what the motor requirements are, use a breaker rated for that need. Electrical tables will tell you the minimum wire gauge for that breaker, and any needed compensation for length of run from the breaker.