I am going to put a remote switch on my 3520. I read Doc's article on "the yellow wire method" looks easy enough. The only down side is that the inverter is alwas on and therefore not protected from power surges. I can put in a heavyier switch that kills both legs of the 220V power comming in. Is there any chance that this will damage the inverter by turning it on and off many more times than now. Also what about turning on the power while the existing switch is in the on position. I like the idea of turning the entire unit off with the second power switch, just worried about unintended consequences.
You will not hurt the inverter by switching the main power source OFF between turning sessions.
If you turn the main power switch ON while the switch on the lathe is in the ON/Run position, the inverter will not start. You will then have to turn the lathe switch OFF and then back ON to get it to run. It's a safety thing.
There is a time delay of a few seconds from the time you apply the main power until the inverter is ready to run. (Maybe 5 seconds.) In a quiet shop, you can hear a relay click inside the inverter. If you turn the lathe ON before the time delay is up, it won't start. Turn it OFF, then ON again and she'll take off.
You can get a switch for the main power at Lowes, Home Depot, etc. It must be a double-pole, single throw switch so that both sides of the 240VAC line are switched. It will have four terminals. It mounts in an ordinary switch box and, externally, looks like an ordinary light switch.
Caution: there is a switch available that looks almost identical to the DPST switch that is called a four-way switch and is used to switch a light On or Off from two or more locations. It also has four terminals, but this switch will not work for power ON/OFF. With this switch, power will be applied to the lathe all the time; you can't turn it OFF.
Since what I am trying to do is to be able to turn the lathe on and off without getting in the line of fire (ie, use the remote switch for normal on and off) it seems like the yellow wire method may be the better approach. Amazon has some motor switches with a large stop bar for about $10 that will work just fine with the low voltage line. I think I will go that route.
Steve, just to be sure that I'm being clear on this, the main power switch which I described above is for disconnecting the lathe from its power source between turning sessions. Turning the main power off saves a bit of electricity and offers some protection for the inverter during thunderstorms and the like.
I did not intend, and I have not used, it as an ON/OFF switch for starting and stopping the lathe in normal turning. That would not work because you would have to operate the switch on the lathe anyway.
On the other hand, the remote ON/OFF is just that. It allows you to position the remote at the tailstock end of the lathe to avoid the line of fire, and so forth.
The on off switch just changes a low voltage terminal on the VFD. It does not turn off the main power to the lathe. The VFD stays on. I'm not sure it would be a good thing to switch the VFD on and off every time you want to stop the lathe.