I have the General 260, have had it plugged into the same outlet for over 5 years. It's alive but in a coma: the motor won't run but the computerized panel in the back is blinking O5F. The manual says that means there is too much voltage in the line, the remedy is "check the line voltage".
I unplugged the lathe, tripped the breaker it was on (it's the only thing on that breaker which is a 220 for a compressor). Put the breaker back on and plugged the lathe back in.......still blinking that same "fault".
How do I check the "line voltage" and if it says 220, is that the voltage? (forgive me if that's a dumb question I'm only a woman......oh, that'll get another thread going!!!)
How do I reset the factory or default settings in that computerized box?
Should I touch that computerized box?
I read everything in the manual and on the DVD (same stuff) and see no cure.
You likely had a thunderstorm pass through. I am east of you and have several last evening and one this morning.
It is possible that during a thunderstorm the line voltage was temporarily higher due to some lightning strike.
I recall a thread like this on another lathe, may have been Powermatic. In this other thread the solution was to unplug for an extended period, such as 20 - 30 minutes in order to reset the board. Likely needed to drain some capacitor down.
Worth a try since you cannot call General until tomorrow.
Dave gave the same recommendation that I was going to give - unplug the machine from any service voltage for at least 2-4 hours to allow a complete power down, including any "memory" capacitors, etc. Unless there is a "Full Reset" button on the electronic controller which performs a "cold re-boot", you should power the unit down completely, and then do a start-up after plugging the unit back in following an extended power-down period.
A call to General's customer/technical service in Canada should be made anyway, ASAP, so you get the best instructions on how to deal with similar circumstances from the folks who built the machine. For the rest of us, we are only making guesses, albeit educated guesses, on how to resolve the situation.
Several years ago a nearby lightning strike apparently damaged the transformer that supplied power to my shop. After blowing several alarm panels and noting that my cordless tool chargers were humming, I finally got smart and stuck a volt meter in an outlet. The 110 v outlets read north of 150 v and the 220 outlets were in the 300 v range. The problem was solved when the power company replaced the transformer. Cheap voltmeters can be found at any of the big box stores.
AS above but push the stop or off button on the lathe while the breaker is turned off. Leave it off until you turn breaker back on. Then restart as normal.
To be on the safe side, call your local power company and have them check the voltage from the transformer going to your house. Could save some appliances and other things. They should have a line truck on duty 24/7.
Many VFDs and other computerized panels guard against unattended restarts after a power failure. They must be turned off before before a restart. You don't want your table saw coming on and cutting off your arm when you aren't looking! Same with lathe. Probably triggered with a momentary power outage in a thunderstorm.
I have this same lathe and had a very similar issue with it a few years back.
it was after a thunder storm and I was also unable to get the lathe running. I shut the lathe down a number of times to "hopefully reset the VFD " but it still would not start up. I no longer remember the code that was flashing. when I placed a call to general they told me that most likely the VFD was toast, so over the next few days I went shopping for a new one all this time the lathe was unplugged, after maybe two or three days I thought that I would have another look at the drive and maybe see if it needed to be reprogramed, much to my surprize when I plugged it back in it started up just fine and has been good to this day.
Yes, we did have some nasty (albeit very beautiful) lightening a few days ago and some did hit pretty close.
I will unplug it now and just leave it until tomorrow morning then, as suggested, will call General and learn yet another technical thing about my lathe.
I love this lathe, we've been through a lot of years and a lot of wood together.
It's the same lathe that proved stronger than a pipe wrench! : D
Many years ago before I knew Ruth and before she lived where she lives now I would read posts from her about the General. I thought for too long that the "General" was a person. LOL
That was on, I think, the old yahoo rec.woodturner days, and I was about as new as a woodturner could be.
Didn't know the difference between end grain and side grain, and a bunch of other stuff that I now take for granted. At that time I had no idea that General was the name of a lathe manufacturer. But I was turning on a Craftsman back then, so what can you expect :-)