I need some electrical help. I have floating dock that supports my irrigation pump. I have had no problems in 15 years, but last week a neighbor across the cove reported a "tingle" when he went to get back up onto his dock from swimming. Because my pump was the only one working at the time it was obviously the one with the defect. The lights on the dock were protected with a GFCI and were not effected. I don't quite know how to test where the current is getting from the AC line onto the dock frame. Any good suggestions ?

Re: O.T.

#2

Re: O.T.

Bill Turpin WNC mountains

Is any of this stuff grounded? Have you lost a ground? A digital volt meter with leads from the outer case of the pump to the ground of of the lights should show any leakage. If your leads are not long enough, run a wire from the light fixture body to where you can reach it. Any voltage flow of more than a half volt is a problem. You may need to replace the pumps ground. Be careful. Tingles can kill you, especially around water!

Re: O.T.

#3

Re: O.T.

Bill Turpin WNC mountains

Does your neighbor have any electricals on his dock? A short can be felt even when nothing is turned on. A hot wire with poor insulation on his dock could be the problem.

Re: O.T.

#4

Re: O.T.

bill Crommett

Bill: Thanks for the reply, but the neighbor felt the tingle and because my pump was just started, he felt that it must be the problem so he swam over closer to my dock and the tingles got worse. I give him credit for backing off, because I am well aware of current leakage in marinas, and the fatalities that have occurred in fresh water marinas. My question is:1) should I run a test lead from the pump motor to a hot wire or 2) should I run a test lead from the pump case to the dock frame or 3) Find out if the algae on the poly pipe pump intake is carrying any strays. Everything is in EMT or poly conduit. The pump runs on 240 V. somewhere there is a leak getting from one of the hot wires to the dock frame. Do electric motors develop internal shorts ?

Re: O.T.

#5

Re: O.T.

Bill Turpin WNC mountains

Run a test wire from a KNOWN ground that is separate from the ground of the motor. Test with a meter from that test wire to the frame (outside) of the motor. Any voltage flow is a problem. Usually shorts in motors quickly cause motor failure. However small shorts can operate for years. Check to see if the motor is grounded. Check from a hot to the frame of the motor. If frame is grounded, there should be 120 vac to ground. If you are not comfortable with this, CALL A QUALIFIOED ELECTRICIAN! It will be cheaper than a funeral.

Re: O.T.

#6

Re: O.T.

bill Crommett

Bill: I will try your suggestions in the morning. My pump will not run until the error is found, and we have had sufficient rain to keep the garden alive for now.

The problem with finding a QUALIFIED electrician is that most of the ones around here are "wiring specialists" that don't know more about electricity than I do.

Re: O.T.

#7

Dick Hines

Re: O.T.

Dick Hines

A down and dirty way to see if your pump is the problem is turn it off and see if the problem goes away. If the problem goes away then you know your pump is the problem.

Re: O.T.

#8

Re: O.T.

bill Crommett

I cant turn on the pump with people in the water across the cove, but I have found that there is a good leakage from the pump case to the frame of the dock which should have no electrical connection.