#1

Motor wired at 220V running at 110V

Starry S Chan

My neighbor gave me an rarely used spa motor. This 3450 RPM motor is rated 1.5HP and it is wired for 220V. I already checked that it runs fine on 220V. It also seems run fine on 115V. I only run it on 110V for 10 seconds or so.

I did not notice any speed change between the two voltages. Does a motor wired for 220V runs at half of speed when it runs on 110V? I know this is the case with my hairdryer but I am not sure how this works with induction motor.

Starry

Re: Motor wired at 220V running at 110V

#2

Re: Motor wired at 220V running at 110V

John Kaner

Runs the same on 220v or 110v. On 220v, uses half the amps. Therefore cheaper to run as well as cooler.

Re: Motor wired at 220V running at 110V

#3

Richard Allen

Re: Motor wired at 220V running at 110V

Richard Allen

Running the motor without a load on 110 should not cause any problems. But the wire is small for running on 110 with much of a load. It is the load which "uses" the HP. At 220 volts the 1 1/2 hp motor should use something more than 5 amps when the load uses the full HP of the motor. At 110 volts the current doubles, the wire in the motor heats up, the insulation melts (that "electrical" smell), the motor shorts out and draws a LOT more current (smoke and sparks).

Induction motors speed comes from the line frequency (60 HZ in North America).

Re: Motor wired at 220V running at 110V

#4

Re: Motor wired at 220V running at 110V

Dale Miner

An ac motor wired for 220 will run nearly at rated speed on 110 if there is no load applied. If any load is applied, it will rapidly slow down and stall.

However, even at no load, it will not be able to generate the internal counter electromotive force (emf) to prevent an amperage draw that will cause the windings to become hot or worse. If any load is applied, it will rapidly overheat and burn the windiings.

10 seconds of no load should not have harmed it.

Re: Motor wired at 220V running at 110V

#5

Re: Motor wired at 220V running at 110V

Doug Turner

Some motors are wired to run on either 110v or 220V for example the Delta contractor saw motor. You could probably compare that motor to yours as far as wire size, capacitor etc.

Re: Motor wired at 220V running at 110V

#6

Re: Motor wired at 220V running at 110V

Starry S Chan

This motor can be wired to run on either 110V and 220V. The current draw at 110V or 220V is 18.2A or 9.1A respectively. This means that the motor wiring is capable of running at high current. I am just not sure what will happen if the motor is wired for 220V but the input current is 110V. I do notice that the motor starts with much higher torque at 220V.

I plan to use this motor to build a buffing station. This is not much torque requirement with buffing.

Starry

Re: Motor wired at 220V running at 110V

#7

Re: Motor wired at 220V running at 110V

Scott Crumpton

When the motor is wired for 220, the windings are in series. When wired for 110 they are in parallel effectively doubling the wire's current carrying capability. Run it on the wrong voltage for the way it's wired and one way or another it's bye bye motor.

Re: Motor wired at 220V running at 110V

#8

Re: Motor wired at 220V running at 110V

Starry S Chan

Thank you.

Your message is loud and clear. I will not run the motor wired for 220V at 110V.

Re: Motor wired at 220V running at 110V

#9

Re: Motor wired at 220V running at 110V

Barry Irby

John, You said:

"Runs the same on 220v or 110v. On 220v, uses half the amps. Therefore cheaper to run as well as cooler. "

That's not correct. The formula is Amps X Volts = Watts You are billed for watts or kilowatts. The motor draws 18.2 amps at 110 and 9.1 amps at 220 volts so the number of watts used is nearly identical thus the cost to operate would be the same. One advantage to 220 is that you can use a much smaller wire but must have the extra conductor for the other "leg".

If the motor is built to allow it to run on either 220 or 110 wire it correctly for whichever voltage you are suing and it will be OK. there should be a diagram in the box on the motor that shows the wiring.

Re: Motor wired at 220V running at 110V

#10

Re: Motor wired at 220V running at 110V

Bill Howatt

You don't need an extra conductor, you only need 2 wires and the usual safety ground. The conductor that was the neutral conductor in the 120V connection serves as the other hot conductor in the 240V connection. If you are using a cable with black and white conductors the white conductor should be marked with tape or marker pen at the ends to indicate it is not a neutral.

Bill

Re: Motor wired at 220V running at 110V

#11

Re: Motor wired at 220V running at 110V

John Kaner

Barry,

Thanks. I stand corrected. Once again I misunderstood what someone had told me and accepted as fact.

Re: Motor wired at 220V running at 110V

#12

Re: Motor wired at 220V running at 110V

Barry Irby

Bill, you are correct, or at least you have been correct up until now and I am not sure about now. Many things that were traditionally wired with two hots and a ground are now requiring a Neutral as well. Ranges and dryers come to mind. Since many of them have both 220 and 120 circuits in them they are requiring a neutral. In the past, they adopted the ground to make the tiny 120 volt devices work. (clocks and timers, etc.)

Motors and machines that do not have any 120 demand do not require a neutral, but with more and more machines using electronics and lasers, can it be long before even a TS requires a neutral?

Re: Motor wired at 220V running at 110V

#13

Re:PLEASE READ

Don Evans

The key here is that this is a motor for a SPA!!!

Most (all that I know of) spa motors are TWO speed.

They are made to be wired with a neutral and 220 volts plus a ground wire in USA.

They run both 1725 rpm and 3450 rpm depending on what voltage they are getting through the switching circuit.

There should be a wiring diagram inside the motor plate that gives you the wiring schematic, this will show you where the black goes where the red goes etc. But if you want to wire this thing so you can switch it back and forth between 1725 and 3450 that gets more complicated, to much for this forum.

You can wire it just to 110 v BUT you have to make sure you are using the correct wire terminal. ONLY one of the "hot" terminals is made to work with 110 v applied all the time and one of the "hot" terminals is made to switch on and off.

Don

Re: Motor wired at 220V running at 110V

#14

It's a common misunderstanding

Bill Howatt

People get told about the so-called I squared R losses from Ohm's law and the fact that halving the current reduces the heat loss by a factor of 4 and this makes it easy to draw the erroneous conclusion. The only thing is this assumes the other circuit parameters haven't changed.

Bill