Really hoping I don't have to call the HVAC guys and that you lot can give me some guidance...
My central-air unit is leaking water in the house. Why? How do I stop it, short of turning off the unit? Is it because I've got the thermostat set kinda low? I did have this problem once before and a new furnace air filter sorted it all out. I replaced THAT a couple of weeks ago so I doubt that's the answer.
There is no water in your AC. The water you are seeing is most likely water condensed from the humid air. Normally this water is caught and drained away harmlessly in a 'conconsate pipe.' It is possible this pipe is clogged. Look for a pipe or plastic tube around the unit inside the house that runs into a drain. Blowing out this line should solve the problem. If it is a window unit, the problem is the same but I'm not sure of the fix. Probably the same since water will condense out of the air when it is chilled. Good luck!
Hi Steve -- I'm hardly an expert but wonder if the condensate pump has failed or become blocked. A/C units remove moisture from the air by condensing it on the a/c's cooling plates, just as water condenses on a cold can of beer, and as it accumulates and drains off the plates it has to go somewhere, usually falling into a bilge-pump like device which comes on as needed to pimp it outdoors or down a drain. There is usually a check-valve in the line going out; this too can fail and let some drain back in every time the pump goes off.
The modest a/c unit I put in the wall between my shop and garage was putting out over a gallon a day in recent conditions, so it's far from just a few drops that you can be dealing with. My discharge for that is gravity-powered old funnel and a hunk of old garden hose, but for the first few weeks after I installed it the water was collecting into an empty coffee can I had to empty a couple of times a day.
Steve, If it is a central A/C there should be a line from the unit probably run into the nearest drain. There should also be a drip pan under the unit with a line going outside. This pan is just a safety device. It sounds like both are clogged. The A/C acts like a large dehumidifier and that water has to go some where.
We have ours serviced annually and one of the things they do is send a blast of compressed air through the drain lines. The tech that was just out told me it wasn't uncommon for them to have to make a couple tries prior to getting them clean. We have a switch in the overflow pan that if activated cuts off the unit.
If you can locate the drain lines you might be able to blow them out or run a wire through it at least part way.
Slime/mold grows in the dark, drain pan. It is fed by the normal daily dust in the air. I have seen it get over an inch thick in less than one season! HVAC techs can put several "algaecide briquettes" in the pans which slowly dissolve and kill the stuff. Algaecide treatment for a swimming pool will do the same. Bleach, if it can be safely put in, will kill it. The slime will get to be a thick cottage cheese consistancy which will stop up the drain p[ipes.
Do not set the tstat below 68�F. The entering freon temp is below freezing. It makes ice on the coil. A normally working system cycles off every ~20 minutes allowing the ice to defrost. Set point too low allows ice to accumulate until it hangs over outside the drain pan. It then drips on the floor.
Condensate pumps have a float switch which can fail. They also have a safety switch, if wired in, to shut down the AC if too full. As someone else said, there should also be another safety switch for a too full drain pan. Much better to be hot than flooded!
Be sure you wash your hands if exposed to the slime! It is thought that it contributes to Legionaires disease.
You got good advice. If this is a central unit, it may produce ten to twenty gallons of condensate a day. You MUST correct this. If you ignore it, you will be stunned by how much water it dumps where it shouldn't.
If you can find the outside end of the line you can stick the air nozzle from your air compressor into the pipe, use a rag to seal it and give the pipe a blast. Be aware that the water and whatever slime is in the line will be blown back into the unit and or house. It might be better to try to blow it out form the unit end if you can figure out how. I have use a short piece of flex tubing for this. If it is the slime that has stopped up the unit, sometimes just pouring Clorox into the internal pan in the unit and letting it work its way through will kill the algae and let the water flow. (Remove a side panel to find the interior pan.) The algae tablets are a good idea But don't use too many. One or two at the most.
Once your system has the algae in it, it will have it forever. You should have a "chlorination port" added to the drain line and put some Clorox in it once a month in AC season or use the tablets if you can get them. (Try an HVAC supply house)
And Bill's warning about the algae was good. If you get the stuff on yourself, get it off. Wear eye protection to keep the slime out of them. Not all, but some of it truly is nasty.
All of this assumes a gravity system. As other s have mentioned there could be a condensate pump. Its about the size of a shoe box and has a small pump. Looks like something that might go with an aquarium, but it is a quality and generally reliable device. If it is there and failed, you may have to replace it.
Steve, we had a problem similar to this a few years ago. The evaporating tray that leads to the drain is in our attic, and one night I discovered cold water dripping down through the ceiling. To make a long story a little shorter, I figured a mouse had gotten into the pan to get a drink, died, and went down the drain, clogging it up. A little bit of air from the compressor fired him right back out, and proved me right all at the same time. It was a relatively quick fix, but ewww, what a nasty mess. He had been in there for a while.
All this advise is great if the condensate drain/line is stopped up.
Could also be a condensate tray that is made of steel, and has corroded to the point of leaking water. You could clean the corrosion a bit, and plug the water leak (temporarily) to gain a little time, but eventually you would need a new evaporator coil/tray assembly installed.
Tomorrow I try to find that tray. The water is actually dripping from above the furnace unit itself (shoulder height on me), where the lines from the a/c unit outside meet the inside unit. It is dripping into a huge Rubbermaid tote for the evening. Tomorrow ought to be joyful. I hate crap like this.
Harry is Dead on. I had the problem constantly at my old house. After cleaning it out multiple times I removed it and added a new one that had a greater slope. It seemed to work although I moved about a year later so I don't have guaranteed proof.
A bit more information to help you understand, hopefully it will be clear.
A furnace is installed, propane, oil burner or whatever type, it is in a metal cabinet that can be mounted either horizontal or vertical. (sounds like yours is vertical) THEN the coil associated with the AC is mounted inside this cabinet, it is an upside down "V" coil.
Just under the coil is the drip pan talked about and it has a drain line, normally white pvc attached to it to take condensation that forms on the coil out of the unit to a drain or outdoors. Most work on just gravity to take the water out but some must be pumped as previously explained. There should be a switch with wiring attached to the pan in question that will shut the ac off if the pan gets too full of water it works with a float inside the pan to operate the switch, all very similiar to your toilet float system to shut water on and off.
If the unit is located in an area where water will cause damage to the home a good installation company will put another pan under the whole unit and a drain on it also incase the other pan and drain fail for some reason. Point is, don't confuse this pan if you have one with the first line of defense which is the pan immediately below the "V" shaped coil located INSIDE the furnace cabinet.
A word on clorox, be aware that if you go that method the fumes from the clorox will end up inside the home. The air moving through the unit blows through the furnace over this slimy water and into the home and so will the fumes from the clorox.
Personally I would vacuum it with a wet vac and deal with cleaning out the vac outside with a water hose.
Good luck it's a nasty job but someone has to do it!
Steve, Gil had a good thought, the internal pan may have failed. Also, I did not know Javex was a bleach brand in Canada. Actually, It did not occur to me that you were in Canada. Ain't the Internet great?
Sounds like you have a conventional gas furnace with AC. The AC coil is in the "box" on top of the furnace. Its a standard addition or attachment that allows the addition of AC to a heating system. There should be about 4 to 8 screws on the box that allow you to remove the panel. You may not get much of a view of the interior, but perhaps you can get enough to see if the internal drain pan is full. That would be good news. At least it would indicate the pan has not failed.
How is the water getting into the Rubbermaid? Usually when they leak, the water just drools down through the unit and into the furnace.
Don and I were typing at the same time. He has made some good points. To add a little: The "coil" that has been mentioned is not some sort of circular thing. It looks more like the radiator in an automobile. A bunch of little fine, closely spaced fins with some internal piping. The refrigerant passes through the piping and the fins act as surface area and facilitate heat transfer.
Most like you have an "A" coil which is the same thing as a "V" coil, but upside down. If you could see the end of it you would see there are two smaller "radiators" set in a V shape to maximize surface area. Some of these are designed to be set in a number of positions and will have a pan on more than one side. The pan is the tray that catches the water.
I would have to check, but I have not seen many systems with an internal shut off switch. If you have one, what they do is shut off the compressor. A strange sort of setup, but apparently its what they do. When the pan fills up, the little low voltage switch signals the compressor to stop and thus the cooling stops and therefore no more condensation is produces and the system would not over flow. Since yours is leaking, you either don't have and internal shut off, or it failed, or the pan is leaking and not filling up. The reason I said this is a strange setup is that these switches shut off the compressor, but the rest of the system continues to run. So from your point of view, its running ans running and your house is not getting cool. They leave you to figure out that the compressor is shut off. Seems like a little red waring light would be better, in addition to shutting off the compressor.
Air is blown up from the bottom and through the coil. The coil is chilled and it sweats and the condensation drools into the pan and should be carried away by the pipe. A problem with this design is that when you remove a side panel, you are looking at the exit side of the coil. The air enters from the bottom and you won't be able to get a look at that side of the coil unless you have an angle coil. (A single one set at an angle) If your system is slimed it may also have a dirty coil, but the dirt will be on the inlet side. It's probably a job for a technician to pull the coil and inspect the inlet side.
Once you get the system running again, you might want to check its operating temps by taking the "split" temperatures. Put a thermometer on the return and let it run for a few minutes. Read the return temp. Then move the thermometer to a supply outlet and take that temp. What you are looking for is a difference of between 14 and 20 degrees Fahrenheit. This is somewhat crude, but if you get less it generally means low refrigerant. If you get more it often means reduce air flow. (dirty filter, dirty coil, too many vents closed, poor duct design or damaged ducts.) The reason I mention this is systems get dirty over time and the slime in the pan (if you have it) and dirt on the inlet face of the coil could be related.
The water could also be dripping from the line set. The larger tube carries ~45�F/7�C refrigerant back to the compressor. It will sweat (condense water out of the air). This tube must be insulated. A nick or cut in the black foam needs to be fixed with duct tape. Replace missing foam.
The bleach I mentioned earlier is a last resort because of safety reasons. Algae briquettes are much safer and last much longer if available.
The V coil can also be a "A" coil. If there is FROST on the big line back to the compressor: tstat too low, freon charge is low, poor airflow, stopped up filter, internal fins on coil stopped up because filters were not properly changed. The $1 cheap filters from Lowes, HD, Walmart, etc. should not be used. You should not be able to read a book thru a good filter. If you can see through it, dust can get through it. Quality filters will save you money in operational expenses. They should be changed MONTHLY or more often if needed. Does the dust from your shop get into the A/C?
Barry and I were also typing at the same time. I type slowly, so he beat me below. Pan over-flow switches are found in cadillac systems. They are put in by the installers. They should always be put in systems mounted above ceilings, often found in office buildings. Wet ceiling tiles fall with suddenness and HUGE messes. They can hurt people and sensitive electronics.
Here is an OT to this OT: When cutting grass, try to mow close around outside unit with the unit off. Grass clippings will stop up the fins on this unit. Twice a season, use a high flow water squirtter to flush the crud out of the fins. You and your power bill will be happier.
Don't use too high a water pressure! Yes, yes, I did. I just used regular hose pressure, but with a nozzle and it bent the fins (some of them). That's when I learned about fin combs.
Funny story....at our old house, we determined that our bathroom was haunted. Every once in a while, we would hear funny noises and sometimes sense a faint smell of sewer like odors. Long sotry short, our ac drained into the plumbing system and over the winter, the trap water dries up and when the fan comes on, it pressurizes the system and the bathtub must have had the shortest column of water, so that's where it came out. I simply removed the rubber coupling and poured in some water to fill the trap. I told the next owner about it so she would know what to do and not assume the bathroom was haunted.
Tony, please note that I said high flow, NOT high pressure.A nozzle on a garden hose is enough. Fins exposed to oil fumes...exhaust from kitchen fryers will require some soap(condenser coil cleaner) sprayed on also. A commercial soap with a little caustic added to cut the grease. Continue washing until water runs clear.
Gil said: "Could also be a condensate tray that is made of steel, and has corroded to the point of leaking water."
My drip pan went bad (lots of pin holes) and the manufacturer did not make replacements but I was told to go to a metal fabricator to have one made. There was no way they could make an exact duplicate. They were going to get some galvanized tin and make a shallow pan and solder it at the corners. I knew that crap was not going to work well or last long so I took the old one out, cleaned off all the rust on both sides, applied some navel jelly to kill the rust and then got me some fiberglass cloth and resin to put on it and it was better than new.
Bill: There are really three grades of air filters. Pleated polyester, good fiberglass, and the cheapos that possums can crawl through. The pleated can be sorta restrictive. Go with middle grade. However, one of the easiest ways of cutting installation costs in a HVAC system is to cut return air filter grilles and duct work. This leads to higher operating costs and more noise. Most A/C units handle 400 cfm per ton. A filter grille will properly handle 2 cfm/sq. inch of net opening. Louvers subtract from net opening. Do you have enough filter surface area? Smaller surface area of filters, leads to sooner loading of a quality filter. The purpose of the filter is to keep the dust from stopping up the in-accessable fins on the A-coil, not to keep the house clean. I spent years trying to cut open coils to wire brush the inside fins where improper filters were used or not changed. An extra filter per month is much cheaper than a 2 or 3-hour service call. A properly sized duct system is silent and does not whoosh!
A few years ago! Fortunately, I noticed it quick enough that I didn't do any permanent damage. The comb is a handy tool to own. Technically, there should be no contact with my fins ont hehouse or shop ac, but sometimes, something happens and there is. I have used the spray you get from HD and Lowes. Seems to work ok. Can't really tell, but it isn't that expensive. I clean the coils on the house and the shop (window unit) now and then. When we first moved in, the coils got full of dirt from construction and landscaping. That caused issues, so I've been mindfull of keeping them clean. Anyway, just wanted to share my stupidity for someone else to learn from.