Most generic VFDs have some 250 programming parameters. We usually use about 25 of them changed from the default. Over-load protection usually ships turned off.It needs to be enabled with the proper trip point. Braking time needs to be closer to ten seconds than zero. If it stops too quickly it can un-screw a chuck and dump a heavy load in the floor. Overload is usually set at 115% of FLA, (full load amps). Does the drive calculate the fifteen % or do you? Understand the settings or get someone that does. You do not want to hear that spark noise again.Frequently, parameters are set for the worst mistakes possible, if you do not change them for the proper settings.A 480V setting will protect the drive if you forget to. Please change it to the proper voltage.
Is your braking resistor OK? Did it fry also? With the resistor, the drive uses the motors windings to create a reverse magnetic field which slows the motor down. The braking time is function of this. You want it as fast as possible (for safety stopping and efficient turning) and as long as possible to keep from loosing your chuck.