Just to put some thoughts in. I am an electrician by trade but in the UK so not up with your wiring regulations.
For a motor/lathe that size over here, it would have to have protection in the start circuit for the motor. i.e. overload and no-volt protection (sometimes a thermal trip is added) In that case when you fuse the supply you are rating the fuse to protect the cable in the event of a fault on the cable. So as long as your fuse protects the cable that should be fine. If you are just running the lathe off this circuit you could look for some specific motor fuses (The lathe may already have them in you'd have to look at the manual) which means you can fuse it lower, without them blowing on the surge currents of starting.
Another factor to consider on the size of cable to use is the length of the cable from the source. As long as the lathe has suitable protection for the motor, you can't go wrong with bigger cables. You will get less voltage drop when starting especially which is good. There's nothing to stop you using the bigger cable with a smaller fuse, will just mean it is well protected and you get the advantage of a lower impedance supply.
Hope this helps even if it doesn't answer your question :o)
David