OT- Electrical
Mark Mandell - Gone Round In New Jersey
The case of the Disappearing White Wire
So we got a house for my daughter and I've been slowly correcting the screw-ups by the prior owner, not the least of which have been the guy's electrical work.
Last on the list is the garage where he had half a dozen ungrounded outlets in conduit and a generator back-feed using #14 wire!!! Yes, I ripped them all out.
Appears that the guy had a "pro" run a feed and install a 30amp sub panel in the garage that everything was connected to, but here's the rub: The panel is fed from the main with #10 3w/ground with the ground wire insulated (green), however the main panel uses a single clamp bar for both common and ground. When the feed gets to the sub, the white wire is not present, seems to have been snipped rather than being connected in the sub box.
Question No. 1: Is this Kosher? [Guaranteed neither inspected nor blessed]
Question No. 2: With 2 circuits to install [yes, both GFCI] can I properly bring in both ground and common to the sub box's single bar?
In my experience, using grounding wire as both ground and common is not a great idea, but my alternative seems to be to rip out the whole thing and run a new feed to a new sub box with separate connection bars for ground and common even though it makes no difference when the feed connection is made in the main panel.
Comments anyone?
TIA

stranded wire in the right colors.