Shop build advice -- outlet locations

#1

A.J. Hamler

Shop build advice -- outlet locations

A.J. Hamler

My basement shop build is proceeding apace. The framing is done and looks awesome; I think it'll work perfectly. Glad I agonized and planned and re-planned and re-re-planned it all to come up with the most workable arrangement.

Now, it's on to electricity. The electrician comes Wednesday to install the sub panel in the basement, followed by the outlets. I'm curious as to what you think about some of the outlets.

I've already plotted and marked out all the outlet locations on the studs and am confident they're all located perfectly to serve all my machines and portable electric tools -- plus ancillary stuff like where I want my radio, task lighting, battery charging and etc. and etc. I've already set the total number and type of outlets, too, so no questions on any of that.

For all my tools and general woodworking purposes, I've already set the height of the outlets intended for that. That is, I know exactly which outlets will be at the standard low height of 12"-18" off the floor, and which outlets I want at half-wall height for machines and over countertops. Ditto for my office and the storage room. Those are all good to go and no questions on any of that either.

However, I'll also have maybe six or seven outlets that are "unassigned" to anything I anticipate needing to use woodworking-wise. What's your opinion on the height I should make those outlets -- standard low, or high? Again, these are all extra outlets for which I have no planned specific use.

Keep in mind that one of these days we'll sell this house, and unless whoever buys it also plans to use it as a workshop the space will probably end up being either a family room or rec room. I want the place to be as "sellable" as possible

With all this in mind, what are your thoughts on those six or seven extra outlets.

Thanks!

A.J.

Re: Shop build advice -- outlet locations

#2

easy

Bill Tindall, E.Tn.

make them low. Trivial to raise them if later desirable to do so. Not so handy lowering them without a wire stretcher.

I have outlets within reach dropped from ceiling over my bench. I like cord for router, for example, coming from above for it is less in the way.

Re: Shop build advice -- outlet locations

#3

Re: easy

Joseph Mulherin

You might consider having a bar of outlets mounted on your workbench.....obtained from Harbor Freight...

3 foots or 4 foots.

Re: Shop build advice -- outlet locations

#4

Re: Shop build advice -- outlet locations

jesse cloud

Bill's advice is good.

Beyond that I thought and thought and planned carefully all my outlets and they worked fine with my equipment for a couple of months, then a big project required moving things around, then another moved them into a new configuration and I'm looking at some of the big hunks of iron that take up so much space with a scowl and just might downsize some. So my advice would be don't sweat it too much...

A couple of receptacles on the ceiling gives a lot of flexibility!!

And custom extension cords are not hard to make.

Don't forget to post a pic of the new digs!!

Re: Shop build advice -- outlet locations

#5

You don't mention what all you intend to do.

Gary Smyth

OK it's in the basement and at least some is for woodworking What else is going on down there-- washer dryer, furnace, freezer, fire suppression, sump pump, air purification, lighting? What about access to the outside? I ask because you might want to put in at least a couple of 110's and a 220 outlet for a big saw, drum sander, welding, compressor, generator, plasma cutting, etc. Some of these should go to a outdoor outlet, but close to the work space. Think for the future you. Since you already have a subpanel and some free space do it now and save $500 for a return call.

Think about 3D printing, computer, CNC.

DO NOT worry about setting up now for selling the house in the future. Do what you need for you. When you buy a house, there are expenses. If the power is available at the box they will put whatever they need where they need it. -- it is not your concern.

As to outlets, the height is fine. I would however expect a duplex outlet equivalent to one every four feet around the perimeter of the room. Never less than two outlets per wall. I'm pretty sure from your opening you have that taken care of.

When it's done and before you close up. send a picture(s).

Re: Shop build advice -- outlet locations

#6

JL

Re: Shop build advice -- outlet locations

JL

One thing I did with my shop was place two outlets "high" - near the ceiling. This is for air cleaners or LED shop light fixtures.

Re: Shop build advice -- outlet locations

#7

Re: Shop build advice -- outlet locations

Joseph Mulherin

That's exactly what i did in 1985 when i built my shop.

Re: Shop build advice -- outlet locations

#8

Re: You don't mention what all you intend to do.

Barry Irby

All good advice so far.

Gary makes a good point. Set it up for what you want. You can't outguess the market. You can not possibly know what some future buyer will want or think of your workshop setup. That said, make sure yo don't ignore the Code or the "regular" stuff. Put in any and all outlets, lights, and switches that would be there if it weren't a workshop. And, you can't have too many. Anyplace you think might be popular for plugging in stuff, put a double box and two duplex receptacles. Costs almost nothing now and you will appreciate it later.

Re: Shop build advice -- outlet locations

#9

Re: Shop build advice -- outlet locations

Larry Clinton At Frankfort, (Central) Indiana

Sir, when I built my shop, my son and I did all the wiring ourselves. (I am a qualified electrician). Having an old home 1880's vintage, I fought a lack of outlets for years. It is several times as expensive to add an outlet after the area is finished. I installed ceiling outlets, several 220V outlets, some were dedicated to the air compressor, dust collector, welder and others spaced for mobile equipment like my planer etc. Then I installed 120V outlets on every other wall stud about 60" off the floor, this allows them to be in the right position for "above the workbench location and also allows 4X8 sheets of plywood to be stored under them. Then I added a few near the garage door, and entry door.

The ceiling outlets are switched with 4 switches ~ three control fluorescent lighting rows and one for 6 Halogen light fixtures. When I was through I had filled every breaker in the large 100 amp service box. My biggest recommendation is to add any and every outlet you may think you may need plus a few more. Cost of installing a few outlets now is less than adding one later!

All of my 120V outlets are wired with a GFI at the lead so every outlet is protected.

After all of this I found a couple of places I wish I had added another outlet!

Re: Shop build advice -- outlet locations

#10

Re: Shop build advice -- outlet locations

John K Jordan

>>>All of my 120V outlets are wired with a GFI at the lead so every outlet is protected.

Some devices don't play well with GFCI, in particular VFDs such as the Delta used in the Jet 1642 lathe cause them to trip every time. I would test first, then if necessary put the VFD machine on a separate non-GFCI curcuit.

I put 110v receptacles every 4' in my new shop, some doubled at planned work benches, some extras close to where it made more sense in my plan. Most outlets are above work surface height except for some close to the floor that feed specific machines. I think it is better to have more receptacles than you plan at the moment to use. I think code has a maximum on one circuit, if you have to follow the code - this would make sense if you planned to plug something into every outlet.

I put all receptacles in the walls covered with 1/2" panels installed with screws in the event I want to change something. I removed one panel several times when upgrading from a 110v lathe to 220v lathe and when wiring another circuit.

JKJ

Re: Shop build advice -- outlet locations

#11

Kneale Brownson

Hard to put in too many

Kneale Brownson

I put in double boxes, had 110 outlets on one side of the box, 220 outlets on the other. Separate circuit for each wall of the shop.

When we built my wife's knitting/quilting shop, we put the outlets all half way up the walls except where there were windows/doors. The older you get, the more you'll appreciate not having to bend to the floor to plug/unplug something.

Who cares what the next owner might want? It's for your use.

Re: Shop build advice -- outlet locations

#12

Re: Shop build advice -- outlet locations

Jay Lombardo

Retired electrician here.

1) You can't have too many

2) Locate them above the work surfaces

3) Place a couple up high just below the ceiling

My .02 good Luck

Re: Shop build advice -- outlet locations

#13

A.J. Hamler

Re: Shop build advice -- outlet locations

A.J. Hamler

Thanks, guys; excellent stuff.

I never thought about changing the location down the road, but putting the unassigned outlets low makes perfect sense --- since my shop is in the basement the electric source is high, so if I put those outlets low then I (or the next owner) can easily make them higher. Thanks for that.

I also never gave a thought to my air cleaner which will be on the ceiling, so an outlet up there is a good idea. Never thought about that. Again, thanks.

Someone recommended double outlets -- they're ALL going to be doubles.

And, yes, I've already planned for an outlet in the center of the shop for a drop cord.

Thanks all for the great advice.

A.J.

Re: Shop build advice -- outlet locations

#14

A.J. Hamler

Also...

A.J. Hamler

Rest assured that I've designed everything in this shop to suit me and what I plan to do, and haven't worried about future owners. However, for those half-dozen unassigned outlets I wanted to err on the side of selling the house down the road.

With that in mind, standard low locations for those is perfect for both me and them.

A.J.

Re: Shop build advice -- outlet locations

#15

Re: Also...

Ron Pemberton

When I built my shop I could have put in more wall outlets. I did put a couple in the ceiling for drop cords. One thing I did was to place double outlets in four places to correspond to the position of stationary tools in the floor. I ran conduit for the power before the concrete was poured.

Re: Shop build advice -- outlet locations

#16

Re: You don't mention what all you intend to do.

Pete in Holland MI

All my outlets are 50" from the floor to the bottom of the box. A piece of plywood will lean against the wall and not block the outlet. Most all your machines will be easier to plug into without leaning over the machine/cabinets/junk that accumulates along the walls, which can also damage plugs/outlets if things shift. 12-18" off the floor is OK in a living room where you are trying to hide them behind furniture.

Also, outlets ought to be at least every 4' around the periphery of the room. Build for flexibility, not the one & only layout......which will change some time in the future.

Consider too that if you're running a 20 amp service, you need the more expensive 20 amp outlets. Most of the 89 cent outlets are only rated to 15 amps.

Re: Shop build advice -- outlet locations

#17

Re: Shop build advice -- outlet locations

Johanna Johanson

I was surprised to see so many people suggesting that outlets in the shop be placed low on the walls. Why? I have 2-3 110 outlets on every wall at a height of about 40 inches. There are two 220 outlets on the walls. There are 3 110 ceiling outlets and 1 220 ceiling outlet. I have 5 110 circuits and 2 220 circuits. Every outlet is marked as to which circuit it is on. It seems to me that it would be impossible to overdo the number of outlets.

The reason I put my outlets high on the walls was to prevent their being covered by stuff stored on the floor. I have never regretted that decision.

Shop size: 1 room is 20 x 24 and the other room is 16 x 16. I wish it were larger! Like the number of outlets, I don't think you can have too large a shop!

Re: Shop build advice -- outlet locations

#18

Re:  outlet locations Height!

Larry Clinton At Frankfort, (Central) Indiana

After thinking about the height, I may have been wrong, I did put all of them above 48", but may have been about 50- 55" off the floor. I did not install ANY lower than that, as I knew I would be adding benches and possible storing items against the wall, (besides it is very hard for me to reach low to plug something in). The outlets height worked out well as I have work tables along one wall with my CMS, bench top Mortiser, grinders and other items. The outlets let me plug in items easily. I also hung cabinet along most of my walls on French cleats, probably 70' + of those used to store portable electric and hand tools supplies and junk! All of my large machines except my lathe and drill press are on mobile bases. I use homemade heavy duty extension cords (8 and 10 gauge) and 4" flex dust collector hose to hook them up. Even with my 30' x 30', I find I need to move my cabinet saw, planer and joiner occasionally for different projects. My Dust collector is wall mounted and the air compressor is stationary.

Re: Shop build advice -- outlet locations

#19

High!

ronster

My 5 year old shop has outlets (and a lot of them) high enough to not be obscured by 4x8 sheets goods leaning up against the wall. Never regretted that! It's been a good height for my wallside bench too. And I hate bending over too. Think that advice came from woodcentral. Someone said to leapfrog the circuits for adjacent outlets too. I didn't do that, but once I wish I did.

Re: Shop build advice -- outlet locations

#20

Got kids or grand kids (even in the future?)

Pete in Holland MI

Route all of your outlets (110 & 220v) thru a single switch of adequate capacity, mounted up high, next to the door. Flip this off, and all of your machines cannot be turned on by little curious fingers. Plugging the radio into this same circuit is my indicator that the power is on. Lights are on a different circuit, as is a single outlet, where my cordless chargers all gather.

Re: Shop build advice -- outlet locations

#21

Re: Got kids or grand kids (even in the future?)

Larry Clinton At Frankfort, (Central) Indiana

That would be an impossibility for me as I have many separate circuits for my 120V outlet strings. I did not "leapfrog" my outlet wiring as only one or possibly 2 persons work in the shop at the same time. and have never kicked a 120V breaker out in the 13 ~ 14 years the shop has been in use. I installed an outlet on every other wall stud which are on 16" centers, plus extras where I thought I might need them and also installed some in the upstairs storage area, total of 60 ~ 70 20A 120V outlets!

Re: Shop build advice -- outlet locations

#22

Re: Got kids or grand kids (even in the future?)

John K Jordan

Disabling receptacles with a switch at the door might work for a tiny shop with limited electrical tools.

I also have a lot of receptacles on multiple breakers including some 50 amp 220v lines for the welders and big motors, probably also 60-70 total. (Code limits the number of duplex receptacles on one branch circuit to 10 or so but common practice is 7 - that would take a lot of switches high on the wall!) In addition, I have some things plugged it I want to keep powered when I leave the shop: security system, wifi, personal cell tower, chargers, air quality monitor.

It would be a nightmare to wire my shop with circuit cutoff switches, a big additional expense, and take a lot of wall space inside and out to put central distribution near the door. If that was important it might be easier to split the service into several sub panels and use a big cutoff switch to switch off an entire sub panel.

Instead, I lock the shop when I leave. I use electronic keypad deadbolt locks so locking/unlocking is painless and I don't need to make sure I have the key with me.

JKJ

Re: Shop build advice -- outlet locations

#23

Re: Got kids or grand kids (even in the future?)

roger lance

The OP said he was going to have a sub panel installed for his shop and then have the various circuits run presumptively from that sub panel.

As the sub panel has a master switch (breaker), all he has to do is turn that switch off and lock his panel door.....everything in his shop is off and secured from curious children.

Re: Shop build advice -- outlet locations

#24

Re: Got kids or grand kids (even in the future?)

Brian Holcombe

I currently unplug everything, but have been considering cutoff switches for bigger machinery. Any suggestions that can handle 220v 20-30 amps?

Re: Shop build advice -- outlet locations

#25

A.J. Hamler

won't work

A.J. Hamler

I am indeed getting a new separate panel for the basement, however not only will electricity for the shop come from there, but so will electricity for my office, storage room and some lights on the non-shop side of the basement. Flipping a master switch would kill all those areas, not just the shop, so that won't work.

However, you suggestion has me thinking that when grandson Jed comes to visit it would be a simple matter to flip off just the shop circuits and leave the office and other areas powered.

Good suggestion.

A.J.