Wire size needed/

Posts

Wire size needed/

#1

Wire size needed/

Ray Newman

Colleagues: getting a new table saw and need to determine wire size needed to hook up.

Outlet is 20 or 30 amps, 220v (need to check it).

Outlet to saw will be about 30 feet -- up and over DC system. Concrete floor so cannot go under slab.

Have 45 feet of 12/3, but I do not think that is enough.

Thanks.

Re: Wire size needed/

#2

Re: Wire size needed/

Ray Newman

Just checked the breaker and it is 40 amps!

Re: Wire size needed/

#3

Re: Wire size

Mark Mandell - Gone Round In New Jersey

I think (but haven't looked lately) that 12/3 copper has a limit of 25 amps. A 3hp table saw will be pulling 25 amps in run mode unless the blade is stalled. I doubt it will pull that even on start-up as there's no resistance on the motor's rotation like will happen with a big compressor.

Ergo, your 12/3 should do fine. Just remember to run it in conduit from where it "leaves the structure wall"

Re: Wire size needed/

#4

PS

Mark Mandell - Gone Round In New Jersey

Change out that 40 amp breaker or rewire with 10/3 copper! Can't run 40 amps in 12/3 even if you're only pulling 15 amps on the load.

Re: Wire size needed/

#5

You're good.

Hoa in Alameda

Disclaimer: EE, but not licensed electrician.

I think my 3HP Unisaw is rated at 240V, 16A.

If your saw is similar, 12/3 wire is sufficient.

I don't believe you need to change out the 40A breaker, or use 10/3 wire. I have a bunch of 120V 20A outlets in the shop. Do I need to change out the breakers or use 12/3 to run my 2A 5" orbital sander?

Re: Wire size needed/

#6

My Sparky

Mark Mandell - Gone Round In New Jersey

"trained" me that your wire size is determined by the breaker and the "potential" load on the circuit. The breaker is used to limit the power on the circuit to the ability of the wire to carry it. Since a 40amp breaker will have the capacity to overload a 12/3 wire, either you change the wire or change the breaker, regardless of how much load you actually plug into the receptacles etc.

Re: Wire size needed/

#7

Hoa, you might want to study that a bit more.

Keith Newton

I believe a 40 amp breaker protects a # 8 wire. A 30 amp is for #10 wire, a 20 amp takes care of 12 gauge, and 15 amp breakers are for 14 gauge wire. The above numbers are for copper, and are different for aluminum.

While you can run a small tool on any of these sizes, if you have too large a breaker for the wire size, it may not trip when you have a direct short, or maybe a loose wire nut arcing, or connection to a receptacle, which can get hot enough to start a fire, which would otherwise trip the breaker.

The breaker doesn't care how few of the amps your sander needs that it will carry, it is there to protect the hard-wires and outlets downstream of it.

Just Google to find more than you ever wanted to know.

Re: Wire size needed/

#8

But... but....

Hoa in Alameda

You guys are talking about the wire from the breaker to the outlet. I think the OP, when writing "Have 45 feet of 12/3" is referring to the wire (that he may use) from the plug to the motor.

Assuming the motor is rated at 16 A, a 12/3 wire from the plug to the motor is sufficient. The breaker can be 40A, but that wire does not need to carry 40A. This is similar to the 16/2 wire to my orbital sander. It's plugged in a 20A outlet, but does not need to carry the whole 20A.

Re: Wire size needed/

#9

Re: But... but....

Ray Newman

Hoa is right -- I am inquiring about what gauge wire from the wall outlet to saw connection.

Sorry for the confusion, I could have expressed myself better.

The new saw is 13A/220v/3HP

Re: Wire size needed/

#10

Exactly....

John in NM

It is a common misconception that the breaker is intended to protect the load - in this case a table saw and accompanying wire. Circuit breakers are intended to protect the circuit itself, right up to the outlet (in this case).

The reason for this misconception is very straightforward - it's how we all end up using circuit breakers in our homes and small shops. Technically, those stationary tools like table saws should have a separate disconnect device and over current protection attached to the machine and appropriately sized to protect the machine. I've never seen a small shop bother to do this though.

Size the breaker for the installed wiring and outlets, size the machine cord for the anticipated load due to the machine.

Re: Wire size needed/

#11

Re: Wire size needed/

Ray Newman

Gents: am going to ask around about an electrician.

Thanks for the information.

Re: Wire size needed/

#12

Plz post what you find out.

Tom Dunlap

When you get a definitive answer would you let us all know?

Thanks,

Tom

Re: Wire size needed/

#13

Yes, I misunderstood, my bad.


Re: Wire size needed/

#14

This Might Help  *LINK*


Wire Size Calculator

Re: Wire size needed/

#15

Re: Wire size needed/

BrianMonumentCO

After you contact your electrician you might want to check with your local building department.

THe circuit you are plugging your table saw into may not be wired correctly for you usage.

There is the issue of the plug you are using.

My Delta Unisaw has a 250/20 amp circuit with 12/3 wiring.

I have about 8 feet of 12/3 wiring from the plug to my unisaw.

The outlet I have looks like a 100 but has the left leg horizontal and the right leg has a T with a vertical and a horizontal part. That is with the ground at the top.

That receptacle is called a NEMA 6-20R

My plug on the line to the saw has a horizontal leg and a vertical leg using the above receptacle.

NEMA 6-20P This is described as 220V 20 amps.

Re: Wire size needed/

#16

In That Case

Mark Mandell - Gone Round In New Jersey

12/2 w/g is fine. Your saw only has connections for two hots and a ground. Third conductor is not needed. You'll need a 20 amp receptacle and plug to match.

Re: Wire size needed/

#17

My experience

Bill Tindall, E.Tn.

I know what the inspectors look for. The wire must match the breaker, period. It is a simple matter to look up what the wire will carry. 12 ga = 20 amp is my recollection. Somebody that wired some equipment for me got to do the breakers over because they violated this rule in a 40/50 amp situation.

Re: Wire size needed/

#18

Re: My experience

Barry Irby

I agree with Bill.

This is more complicated that it appears at first glance, but basically the breaker protects the wire attached to it. A 12/3 wire is rated for about 20 amps and should be attached to a 20 amp breaker.

There are many factors that are related and should be taken into account. The Motor has ratings on it for RLA (running load amps) which is what it draws running at full speed and not under significant load. Also has LRA (Locked Rotor Amps), this is often about five times the running load. When you flip the switch there is a large current draw to spin the motor up to speed. This is nearly instantaneous is the shaft is free to spin. Breaker will ignore this huge draw for a brief time. If your dog the saw and load the blade heavily and slow it down, the current draw increases and if its high enough long enough the breaker will trip to protect the wire. Another factor is the length of the wire. 45 feet is not a terribly long run, but may come into play if you are close to the limits of the wire.

I would suggest you use a 20 amp breaker for the 12/3 wire.

Re: Wire size needed/

#19

Re: Wire size needed/

Bill Howatt

The plug and receptacle voltage and current ratings must match the maximum voltage and current on the circuit. You can't have a 40A breaker and a 20A receptacle.

The situation gets even more complicated although possibly adding some wiring relief if the motor-load is on a hard-wired dedicated circuit (no receptacles). In this case the breaker can be larger to prevent startup trips but there are special rules for the wire and maximum breaker.

For the typical shop with plugs and receptacles it is best to stay with the usual 15A for #14, 20A for #12, 30A for #10 and 40A for #8. Note that if you have real long runs from the panel these values can be derated.

Bill

Re: Wire size needed/

#20

Re: Wire size needed/

BrianMonumentCO

In Ray's case he should replace the 40amp breaker with a 20 amp breaker and install the same receptacles that I listed in my last post. L6-20R. With a 20 Amp breaker would do fine.

The wire in the wall could remain overspecified.

If I were he, I would work to shorten all wire distances in general, if possible.

I wonder what receptacle he has now?

But most important as said by others is that the rating of the machine, the plug and receptacle and the circuit breaker all are aligned correctly, a UNISAW should have a 20 amp 250 V service.

That circuit he has is most likely a dedicated circuit to run shop 250 V items.

Why not change the breaker?

Re: Wire size needed/

#21

I didn't say that.

Hoa in Alameda

>> as said by others is that the rating of the machine, the plug and receptacle and the circuit breaker all are aligned correctly, a UNISAW should have a 20 amp 250 V service.


Others? I sure didn't say that.

Back to the question in one of my previous posts, I have several 120V 20A outlets in my shop. Does that mean if I want to use my 120V 2A orbital sander, I'll need to change the breaker and the receptacle to match the sander?

Another case, I have one 240V 20A outlet in my shop, can I plug in my 240V, 9A bandsaw? How am I supposed to align anything if I have different tools with different power needs sharing one outlet? Building a dedicated outlet for each tool?

This is of course with the assumption that the existing circuit (breaker + wiring + receptacle) is already up to code. It is not part of the OP's question.

Re: Wire size needed/

#22

Re: I didn't say that.

BrianMonumentCO

Never said YOU did.

My comment was addressed to the thread in general NOT to YOU.

Other posters have suggested rewiring.

I agree.

My main point is that this OPs circuit would appear to be a DEDICATED circuit.

Most if not all circuits are either hardwired for a specific thing (furnace, hot water heater) or have a receptacle for general use (dryer or in our case shop tools).

I don't know of too many items with a plug that have a 40 amp 250v service needs (I suppose a welder might).

But what receptacle is on it? If it is to be hardwired for the UNISAW then the circuit really should be

downgraded to a 250V 20amp as that is what the 3HP 1PHase UNISAW needs.

That means the use of 12/2 wiring and a 20 AMP breaker.

If the receptacle is a 250V 40 amp receptacle the plug will not be spec for what the UNISAW draws and that would be a serious mistake.

An electrician and the building inspector should now weigh in.

Re: Wire size needed/

#23

Re: I didn't say that.

Ray Newman

gents:

Dedicated circuit.

Wall outlet is NEMA L6-30 amp.

Old saw has a NEMA L67-30 amp plug and I think #10 wire.

Re: Wire size needed/

#24

Re: I didn't say that.

BrianMonumentCO

Ray,

If you changed the breaker to a 250V 20Amp breaker.

Leave the wire as is.

Change the receptacle to NEMA 6-20R

Use a NEMA 6-20P on the cord to the Unisaw.

Your circuit would be correct for your usage.

The breaker is right for the load and receptacle/plug combination.

The heavier wire does not need to be replaced as it is MORE than enough.

The breaker and the load are more closely matched.

Good luck.

Re: Wire size needed/

#25

Hoa.....

Barry Irby

The breaker is supposed to protect the WIRE that it feeds. The Breaker, the wire, and the receptacle and plugs are all supposed to be matched as far as amperage goes. This keeps you from plugging poorly matched things into the circuit. IE, you can't plug your welder into your Unisaw circuit.

There is an exception and that is you can use 15 and 20 amp receptacles interchangeably on 15 amp circuits.

The circuit does not protect small devices. It is acceptable to plug a 2 amp device into a 15 or 20 amp circuit and there might be enough amps to destroy the device. Hopefully the device would fail harmlessly.