Re: DC tripping protected outlet

#26

Re: Update

Keith Newton

I haven't followed all the responses, and don't know if anyone ask if this device carries the ground circuit through it.

Since there is possible static charge in vacuum systems, that may have gone into the ground line before, but if the new switch is only hot and neutral without a ground, maybe the static is being picked up and confusing it. Just a wild guess.

Re: DC tripping protected outlet

#27

While You're At It

Mark Mandell - Gone Round In New Jersey

Either change out that 30amp breaker for a 20 or

change out the receptacles for 30 amp rated units. 30amp outlets are only singletons and you will also have to change the plug(s) to match.

You really are playing with fire in this configuration. While your wiring (10ga) may handle 30 amps, your duplex outlets will NOT, and can melt, "light up", or both. Since your DC is outside your shop area you may not even know of a problem until it's too late to contain the fire.

Re: DC tripping protected outlet

#28

Yes and no....

John in NM

Nothing wrong with a 15 amp outlet on a 30 amp breaker if one only plugs in stuff that draws 12 amps - as AJ is proposing to do. Doesn't meet code, no, but it will work fine and is safe enough.

Personally, I doubt that a 15 amp breaker will melt if 20-30 is demanded of it, but I have nothing much with which to back that up and I know it :D

Now if we want to discuss the implications of leaving it this way for some future owner, then you sure got a point :D