Re: electrical panel question
Rick Christopherson
Because you are using the breaker to backfeed power into the panel, it is required to be secured to the bus. So the red locking tab is appropriate and required.
The second part of this is not having any breakers sharing the same stabs on the panel. This is because doing so can exceed the amperage rating of those stabs. The incoming breaker appears to be 100 amps. So any breaker placed opposite to this has the potential to exceed whatever the rating is per-stab. Just FYI, the per-stab rating is generally lower than the total rating of the panel. That's because the stabs (horizontal parts of the bus bar) are physically smaller than the main bus conductors running vertically down the length of the panel.
However, if you really need to free up more breaker locations, it MAY be possible to correct this. I say that it "may" be possible because it will depend on 2 conditions being met first.
#1. The feeders from your main load center to the sub panel must be protected. In all likelihood, this is already accomplished by a circuit breaker installed in your main load center. So as long as you already have a circuit breaker in the main load center that is properly sized for the wires, then you don't need to worry about this part. The existence of the backfed breaker can be removed under the following condition:
#2. Because this is an outbuilding, you must have a service disconnect whereas all power to the building can be shut off with no more than 6 hand movements. This is why the electrician used the backfed breaker instead of connecting to the main lugs at the top of the bus bars.
So if you have 6 or less circuit breakers in the subpanel, then you can simply move the incoming feed to the main lugs. However, if you have more than 6 breakers, then you would need to install a service disconnect switch of some sort prior to your sub panel.