electrical panel question

Posts

electrical panel question

#1

electrical panel question

Jerry Gibbs



I recently had an electrician run a sub-panel to an outbuilding. The red plastic "guard" in the picture is fastened at the back of the main breaker on the sub-panel. What is its purpose? Do I have to leave it? Now the plastic whatever is blocking two breaker slots. Thanks. Jerry

Re: electrical panel question

#2

Re: electrical panel question

Bill Houghton, Sebastopol, CA

Can you ask the electrician? Or the panel manufacturer?

That breaker design just clips in place - over a tab at the outside, and held by spring pressure on the busses. If the red plastic thingie is pushing down against the main breaker (hard to tell from the picture), it could be to ensure that the main stays in place over time. But I'm speculating; I'm not an electrician, and not keeping up with the ever-changing rules in this area.

Re: electrical panel question

#3

Bob

Re: electrical panel question

Bob

It looks like there is one on the other side as well. What size wire and how long is the run? It may exceed the sub panel max load? I have never seen one before and I worker on a lot of industrial systems, maybe I just forgot its been a while.

Re: electrical panel question

#4

Re: electrical panel question

Larry in nw ohio

I haven`t seen anything like that either. The only thing I can come up with is, could that section be damaged so it should not be used, so they put that in so no one could use it, for what ever reason. Larry

Re: electrical panel question

#5

Re: electrical panel question

Ed Wozniak-Buffalo, NY

Does the guard prevent the circuit breaker from being removed? When a regular circuit breaker is used as the main panel breaker in a sub-panel it has to be treated differently than the other breakers. When a breaker serving a subcircuit is removed from the panel it no longer has power connected to it. But when a breaker that is used as the main circuit breaker for the panel is removed it will still have power connected to it unless the breaker in the main breaker panel powering the sub-panel is switched off. The guard might be there to prevent someone from accidentally removing the main circuit breaker thinking that it is just a regular breaker powering a branch circuit.

Re: electrical panel question

#6

Re: electrical panel question

Bill Howatt

I don't know either but if that is that is the main breaker beside it perhaps that area is just for main breakers and not branch circuits. My electric furnace has a 125A breaker that stretches across both sides of the panel (4 slots) so it could be reserved for a large breaker like that.

Bill

Re: electrical panel question

#7

That sounds right...

John in NM

Seemed like it had to be related to the somewhat odd main breaker set up. I've never seen one done like this, but then I've only had my nose in a handful of panels.

Re: electrical panel question

#8

Re: electrical panel question

Rick Christopherson

Because you are using the breaker to backfeed power into the panel, it is required to be secured to the bus. So the red locking tab is appropriate and required.

The second part of this is not having any breakers sharing the same stabs on the panel. This is because doing so can exceed the amperage rating of those stabs. The incoming breaker appears to be 100 amps. So any breaker placed opposite to this has the potential to exceed whatever the rating is per-stab. Just FYI, the per-stab rating is generally lower than the total rating of the panel. That's because the stabs (horizontal parts of the bus bar) are physically smaller than the main bus conductors running vertically down the length of the panel.

However, if you really need to free up more breaker locations, it MAY be possible to correct this. I say that it "may" be possible because it will depend on 2 conditions being met first.

#1. The feeders from your main load center to the sub panel must be protected. In all likelihood, this is already accomplished by a circuit breaker installed in your main load center. So as long as you already have a circuit breaker in the main load center that is properly sized for the wires, then you don't need to worry about this part. The existence of the backfed breaker can be removed under the following condition:

#2. Because this is an outbuilding, you must have a service disconnect whereas all power to the building can be shut off with no more than 6 hand movements. This is why the electrician used the backfed breaker instead of connecting to the main lugs at the top of the bus bars.

So if you have 6 or less circuit breakers in the subpanel, then you can simply move the incoming feed to the main lugs. However, if you have more than 6 breakers, then you would need to install a service disconnect switch of some sort prior to your sub panel.

Re: electrical panel question

#9

thanks

Jerry Gibbs

don't need the breaker slots, but this surprised me.

Re: electrical panel question

#10

Ellis Walentine

Thanks, and a disclaimer

Ellis Walentine

Thanks, Rick. Your posts are always appreciated.

As a non-electrician, I'm grateful for knowledgeable explanations of electrical matters like this. I don't ever presume to answer these questions even if I think I know the answer, because I've learned over the years that I'm just not well enough informed to give authoritative answers.

Also, as usual with this sort of question, WoodCentral can't endorse or assume any liability for any advice shared here. The purpose of this forum is to allow people to tell what they know about a given subject, with no guarantees that their knowledge is correct or safe. Each questioner is advised to use the information shared here to guide them, and that they assume complete responsibility for the decisions they make. In electrical matters in particular, I suggest that folks consult qualified professionals and local enforcement officers prior to undertaking electrical improvements.

Ellis Walentine, Host

Re: electrical panel question

#11

Re: Thanks, and a disclaimer

Rick Christopherson

Yes, Ellis, that is why I choose my words carefully when I do decide to participate here, especially on electrical matters.

Re: electrical panel question

#12

Jason Roehl in Lafayette, IN

Excellent reminder.

Jason Roehl in Lafayette, IN

I think what you said about getting information from the interwebs lends itself to a corollary to a well-known saying:

"If you trust, verify."

Jason

Re: electrical panel question

#13

Follow-up on Disconnects

Rick Christopherson

Because one of the previous posters in this thread sent me an email question about disconnects, I thought it might be a good idea to post this follow-up. In it I will quote and explain the applicable sections of the NEC.

225.31 Disconnecting Means.

Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.


This is pretty straight forward. The building must have some form of disconnect, which is further defined in subsequent sections.

225.32 Location.

The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors. For the purposes of this section, the requirements in 230.6 shall be utilized.


Even though no specific distance is given, the disconnect needs to be close to where the wires enter the building. (Buried wires do not enter the building until they come to the surface.)

225.33 Maximum Number of Disconnects.

(A) General.

The disconnecting means for each supply permitted by 225.30 shall consist of not more than six switches or six circuit breakers mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard. There shall be no more than six disconnects per supply grouped in any one location.


This is the portion that permits a small subpanel to not require a main breaker as long as there are fewer than six breakers or switches to cut power to the structure.