3P starter wiring for dust collector

#1

3P starter wiring for dust collector

Henry Higginbotham

Motor starters/contactors are not exactly my area of expertise. I bought this one through eBay thinking it would be easy to get the wiring information online from Square D. Not so, apparently.

The motor is 3hp, 3-phase, 230V. I'm planning (hoping?) to control the 120V coil with a wireless remote, as for outdoor Christmas lights (other suggestions welcome), plugged into a separate circuit.

But I don't really understand how these things work. The coil measures 31.3 ohms, which would work out to around 460 watts. There's no mechanical latch that I can see, so is the coil under power the entire time that the dust collector is running? That seems like a lot of power to dissipate from a coil that's inside a contactor, that's inside a steel enclosure.

Then there's the matter of the auxiliary switch (labeled "?3" in the picture). I've gotten a vague notion from reading forum postings that it might have something to do with holding the contacts closed, but no confirmation of that, and no indication of how it's to be wired. (This is a physically separate NO switch that closes when the main contacts close)

There are two more connections at ?1 and ?2 that I'm unsure of, as well.

Anyone here an expert on this sort of thing? If I had something resembling income right now, I'd just hire an electrician, but . . . .


Re: 3P starter wiring for dust collector

#2

Re: 3P starter wiring for dust collector *LINK*

John McGaw

I found documentation at the Schneider site which might be of help. Try going there and doing a search on the part number if the link I've given doesn't apply exactly. There are plenty of others and you didn't give the part number so I'm just guessing about which one you have. BTW: that device is amazingly expensive -- I never would have guessed.

[edit]

Forgot to mention it the first time but your concerns about the power dissipation are not warranted. You cannot predict the power based on voltage and DC resistance in this sort of circuit. The AC current flow will depend on the impedance of the coil which is a combination of resistance and inductance and which will be much higher than what you measured. If the coil is rated for 120VAC 60Hz then you should be just fine assuming that the coil isn't damaged.


Schneider

Re: 3P starter wiring for dust collector

#3

Re: 3P starter wiring for dust collector

Jay Lombardo

the terminal marked ?2 is not the #2 term. It is for the neutral of the 120V control circuit. It then goes through the overloads and up to the coil through the red wire on the starter. The terminals marked 2 & 3 are the holding circuit. Yes the coil remains energized all the time the motor is on. Hot from control circuit typically goes to NC stop button through button to NO start button & term 2. Other side of start button to term 3 and a jumper from 3 to the remaining side of the coil. Holding circuit keeps coil pulled in after you let go of the start button, until you break the circuit by pushing the stop button. Remote control would require a relay (probably latching) controlled by remote that would act as a switch hot from control circuit would then just go to relay & then back to coil, no holding circuit.

Re: 3P starter wiring for dust collector

#4

Re: 3P starter wiring for dust collector

Larry in nw ohio

Henry If you paid any more than $20 for that just to control Christmas lights, if I read your post correctly, then you paid to much,because you can buy remotes to control up to 8-10 amps from Ebay. If you go to "Wireless remote control wall outlet", you can buy bunches of them the last time I looked. Larry

Re: 3P starter wiring for dust collector

#5

Re: 3P starter wiring for dust collector *LINK*

walta

First is the electric service to your shop single phase or 3 phase?

Less than 1 % of home shops will have 3 phase service. If your shop is in a commercial building you likely do have 3 phase power.

If you do have 3 phase power is it 208, 240 or 440 ?

Next the motor starter you have has overload heaters that must be sized match your motor.

The photo a generic wiring diagram for a motor starter with 240 volt push to start and stop buttons.

Walta


img

OWWM Wiki

Re: 3P starter wiring for dust collector

#6

Jay . . .

Henry Higginbotham

Thanks. I know there must be some good information in there somewhere if I could just follow it all.

One thing I hadn't noticed in my previous probing with the multimeter was that the continuity between what I have marked ?1 and ?2 depends on the heaters. I can see the purpose of that now (I think), but I've got a ways to go on understanding the usual ON/OFF setup and how I might incorporate a remote control instead.

I have a Powermatic 45 lathe that I was planning to part out on eBay (it's missing the tailstock quill, which is too expensive to replace), so I'll study how the starter on it is wired up. My other tools have LVCs and it makes my head spin just to look at those.

To everyone else, this is probably a very low-interest thread. Would it be okay if I PM'd you sometime if I don't figure it all out?

Re: 3P starter wiring for dust collector

#7

Re: 3P starter wiring for dust collector

Henry Higginbotham

Although it's a residential area, the shop has open-delta 3-phase on its own service. It's 240 volts. The neighborhood dates from the '30s and '40s when some residential air-conditioning required three phase, so the transformers were already there and it cost me nothing. The power company has since installed new ones, as well.

I purchased the heaters separately based on the chart glued to the inside of the enclosure (SF 1.0, FLA 8.0 = B11.5 heaters, if I read it correctly).

Since this is for a central dust collection system, I'm looking for some sort of remote that I can just carry from one machine to another. A Christmas-lights remote will switch a 120V receptacle in another room, so there's some way to use it for my purpose. I just don't quite have that part yet.

Re: 3P starter wiring for dust collector

#8

Re: 3P starter wiring for dust collector

walta

So you are the lucky 1%

This should work. Plug the AC into the wall for testing use the lockout switch once you are sure it works just plug it into your Christmas lights.

You may want the control transformer this keep everything on the same circuit.

Please note the ground on the control transformer.


Walta

Re: 3P starter wiring for dust collector

#9

Re: Jay . . .

Jay Lombardo

Henry, i sent you an e-mail with a very simple solution to what you are trying to do. Make sure it doesn't end up in your spam filter.

Re: 3P starter wiring for dust collector

#10

Re: 3P starter wiring for dust collector

Henry Higginbotham

Lucky, yes. Even though presently nothing is using it except a 2-ton chain hoist.

I appreciate the drawing, especially the inclusion of my (poorly chosen) ID labels for the mystery terminals.

Time to sit down and study all this until I'm satisfied that I understand it, then put it all together and hope the smoke doesn't get out.

Thanks again.