Electrical problem

#1

Electrical problem

Dave in Bryn Mawr

My shop is in a garage where I have a propane heater. This morning, temperature 12 degrees, It will take a long time to get the temp up. The problem is when I turned on the table saw it blew the fuse. Replaced fuse and it blew also. Fuse is 15 amp delay. What's happening? Could it be that the motor is so cold it draws a higher surge when starting? Any other possibilities? Thanks!

Re: Electrical problem

#2

Re: Electrical problem

John McGaw

The cold would be my guess and probably several factors are ganging up on you. Possibilities: 1) Lubricated bearings have more drag when cold calling for more power consumption to overcome and the surge of power is likely to last longer until the blade spins up. 2) The belt itself is likely taking more of a set in the cold and will present a 'lumpy' load requiring more power to get off dead center. 3)The copper wiring has lower resistance in the cold so the current can be higher. Any one of these might be enough to cause problems even if everything else is perfect.

Just my guess of course, me not being there with instruments to measure things. And if it is that cold I don't want to be there anyway...

Re: Electrical problem

#3

15A pretty small for table saw

Dick Coers

What saw, or better yet, electrical rating? I don't think I have a 15A in my whole box, well maybe for bedroom lights.

Re: Electrical problem

#4

Re: Electrical problem

Pete in Holland, MI

Cold makes everything work harder.

What else is on the circut? 15 amp is pretty light for purely a tablesaw, let alone if lights, freezer, heater on the same circuit.

Do you use an extension cord? Smaller than 12 gauge (14+) will also not help.

Your propane heater may heat the garage, but the iron in the garage will take hours to warm up and start easier.

Re: Electrical problem

#5

Re: Electrical problem

del schisler

that cold would make the beiring very stiff, and the amp draw will be more, check and see what the motor amp's is, if the motor has been working on the saw tell the real cold , that that would be your answer , if you have breakers in the box is that the only thing on that breaker ?? if 15 amp you could change to 20 amp ??

Re: Electrical problem

#6

Re: Electrical problem

Dave in Bryn Mawr

The effect of cold on the wire seems most likely. The saw is 30 feet from the fuse box. Most of this passes through an unheated room. Cable is 12 gauge. Would it safe to try a 20 amp delay fuse?

Could I confirm this by measuring the voltage at the motor? If volts go down, amps go up, right? (My high school science memory).

Re: Electrical problem

#7

Re: Electrical problem

Larry in nw ohio

You could try and take the belt off the saw and try the motor by itself and see if it`ll run that way. If it does you may run it awhile to warm the bearings up a little. Then put the belt on and try it. Larry in NW ohio

Re: Electrical problem

#8

Re: Electrical problem

Howard Norman

If the wiring is 12 g than a 20 amp fuse could be used.

Re: Electrical problem

#9

Re: Electrical problem

John McGaw

If everything on the circuit from the fuse to the load is rated for 20A then a 20A fuse should be safe. This means house wiring, outlet, plug, cord etc. must be good for 20A and that everything is in good working order (no loose or corroded connections etc.). The fuse is there to protect the circuit (and thus your building) and it really doesn't care what is plugged into it.

I had to retrofit a 20A Hi-Mag (slow trip) breaker on the 120V circuit which supplies my dust collector and drill press (never used simultaneously) when I rewired and installed a remote control on the DC. The motor is only a 2HP and a standard breaker would pop about 1 time in 3 before installing the surge-tolerant unit.

Re: Electrical problem

#10

Re: Electrical problem

TomD

If it turns out that the belt is part of the problem, you can replace it with a link belt. They are better running anyway. I promised I was going to replace everything in the shop with link belts, as the local supply always had one size for sale every month. Of course as soon as I came up with the idea, that was the last of the sales.

Re: Electrical problem

#11

Re: Electrical problem

Dave in Bryn Mawr

Thanks to all! I will pursue all these possibilities, but my first try will be next Wednesday when the temp is supposed to be 60.

Re: Electrical problem

#12

Re: Electrical problem

Gary

Dave, I believe you already got your answer, but this is for clarification. When the saw is initially turned on the motor will draw more current for a very brief moment, until it gets up to speed. This is true for all electric motors. Normally this shouldn't blow the fuse, however the coldness is most likely causing more stiffness in the moving parts of your motor. Belts are stiffer, lubrication more viscous, tolerances between motor shaft and bearings tighter. This all means the motor works harder and will initially draw even more current just to get started. I suspect the normal initial current surge is close to the 15 amps, but in the cold it's drawing just slightly more than 15 amps and blows the fuse.

As mentioned, changing to a 20 amp fuse should do the trick, but make sure your wiring/outlet can handle this (whatever the electrical code is for 20 amp service). Hope this helps.

Re: Electrical problem

#13

Re: Electrical problem

Howard Acheson

What is the amperage rating of the motor? Look at the plate on the motor.

Is it on a dedicated circuit? If not, what else is on the circuit and running when you attempt to start the saw?

Re: Electrical problem

#14

Re: Electrical problem

walta

Please be careful if there was 15 amp fuse installed it is unlikely all the wire is 12 gage or a 20 amp fuse would have been used from the beginning.

Only change the value of that fuse after you have inspected every piece of wire in that circuit and are sure every bit is 12 gage and in good condition.

Let's not warm your place up with a fire.

Walta