OT - Generator transfer switch

#1

OT - Generator transfer switch

Ray Carson - Lawrenceville, NJ

I hope maybe someone here can help me out. I'll try and be brief.

I often lose power at my house and I decided after Hurricane Irene to buy a generator in lieu of battery backups for my two sump pumps. It came in very handy as we lost power during Hurricane Sandy for about 10 days. I powered up both sumps, two refrigerators and had power to spare for a couple of neighbors.

I didn't like running the extension cords all over and under closed doors so I decided to install a transfer switch. This would also enable me to run my gas furnace and a few other small items like the internet as well. Below are the specifics:

I have a Husky HU5000 generator. 5000 running watts / 6250 peak watts. I installed a Reliance ProTran, 6 switch or toggle transfer switch, model number 30216A. The kit came with the switch, power inlet box a 6 foot 30 amp generator power cord and a 20 amp male end for anyone with a 240/20 amp socket on their generator. I had to cut the male end off and install the supplied 20amp male for my needs. I have a 65 foot run of 10/3 wire running from the power inlet box to the transfer switch.

I followed the directions to the “T” and at one point had the system working before I closed up the one junction box I installed, the main breaker panel, the power inlet box and the transfer switch box itself. I had a few problems and now the system doesn’t work in the “generator mode.”

First problem: I apparently had some arching at the connector where the 10/3 enters the transfer switch. After checking the wire carefully nothing was pierced or comprised.

Second problem: With the generator running and the generator power cord plugged in I can get a 240 reading at the female end before I plug it into the power inlet box. No power down the line on the 10/3 wire. I even made sure I twisted but didn’t over twist when “locking” the plugs.

Third problem: All circuits work normally under the power from PSE& G when the transfer switches are set to the “Line Mode.”

Everything on the “inlet” box as well as the generator power cord is wired correctly. “G” for ground, “W” for the white or neutral, “X” red lead and “Y” black lead. No cut wires, no bare ends, all tight twisted wire nut connections. All breakers snapped in tight. All circuit breakers on the transfer switch and generator are not tripped.

I’m completely baffled !

Re: OT - Generator transfer switch

#2

Re: OT - Generator transfer switch

John McGaw

"Second problem: With the generator running and the generator power cord plugged in I can get a 240 reading at the female end before I plug it into the power inlet box. No power down the line on the 10/3 wire. I even made sure I twisted but didn’t over twist when “locking” the plugs. "

When you say that you got a reading, what method did you use to make the measurement? You need to be careful if you are using a high-impedance meter such as a digital volt meter (or an antique VTVM for that matter). The problem is that induced voltage can be seen with the meter but when an actual load is applied the induced voltage drops to zero. A much more reliable method for checking such a circuit is a simple old-school incandescent light. In this case you would want to measure from red-white and then black-white for voltage using a 120V lamp unless you can come up with a 240V bulb which could safely used across the hots. Alternatively you can wire a 120V light across each side and then measure voltages with any sort of digital meter you might have since the lamp load will kill off any stray induced voltage.

Re: OT - Generator transfer switch

#3

Re: OT - Generator transfer switch

Barry Irby

I am not an Expert on this, but I have been doing battle lately with a house with aluminum wiring. I have found a number of outlets that metered as being properly connected but that would not provide power to a tool if you tried to plug them in. In every case I found loose or very poorly connected wires, either in the suspect outlet or in the one just prior to it in the circuit. I would suggest you have a weak connection or two. Very carefully go back through your connections and be sure each is tight, properly twisted and make sure you have the proper sized wire nuts on each. Can't tell you how many times I have had the DUH! moment after I settled down and got over the frustration.

Re: OT - Generator transfer switch

#4

Re: OT - Generator transfer switch

Galen Vetterick

Not sure I follow in detail. If you cut one end of the power cord from the generator to the power inlet box are you sure you kept the proper four wire relation to the new plug? You say you have 240 but that would be from line to line and not line to the neutral. Make sure you have the the right pins as hots. and you get 120 from each hot to neutral pin.

You ran 10/3 from the power inlet box to the transfer box. Was this not 10/3 with a ground(4wires)! If you had arcing at the transfer switch the first time it sounds like you had connected a hot line to what should be a neutral at one end or the other. On the long line you now may have melted a wire in the run as well so cannot get a voltage measurement as you now say.

I would go back and check that you have not crossed up the lines. I'd solder the wires and not just rely on wire nuts for heavy current.

You also need to make sure the house loads you connected will keep the lines balanced as best you can.

Just shooting in the dark here even though I have power. :D

Re: OT - Generator transfer switch

#5

Re: OT - Generator transfer switch

Larry in nw ohio

Ray If your a novice at electrical hookups, especially with 220-240 volts, I think you should think about getting an electition to do this for you. Electicity is a tricky thing to work with, even if you really know what you are doing with it. Good luck and be very careful. Larry

Re: OT - Generator transfer switch

#6

OT - Generator transfer switch-problem solved !

Ray Carson - Lawrenceville, NJ

I appreciate the advice from the group. I felt very comfortable doing this installation and I have had some experience doing this before. I realize I probably didn't give enough information for you all but I didn't want to take up too much of the WC board space.

In short, it was a short !! It’s as simple as that. I had done everything correctly except I nicked the red wire in the 10/3 ever so slightly at the point where it entered the transfer switch in the basement. I traced continuity through all the wires and rechecked every connection a third time. Upon closer examination I saw the nick. I replaced a small section to get rid of the nick and everything is running smoothly. To give myself a second degree of security, I called a licensed electrician friend of mine and he looked over all of my work free of charge and said I did a really nice job. He told me to just be more careful next time cutting back the exterior jacket of the Romex.

I guess my eyesight isn’t what it used to be. Geez, I’m only 46 yrs. :D

Thanks again to everyone for reading and posting a reply.

Sincerely,

Ray

Re: OT - Generator transfer switch

#7

Geez, I’m only 46 yrs.

Galen Vetterick

Well no wonder, your just a kid and kids do make mistakes. Us old guys never do! :D

Glad you solved your problem and still around to tell us. ;)

Re: OT - Generator transfer switch

#8

Not alone

Bill Houghton, Sebastopol, CA

I was very confused by the tendency of a circuit to flip the upstream GFCI outlet, until I realized I'd pinched the NM ("romex") at one side of the clamp on one box, and cut right through the hot wire's insulation.

I now check very, very carefully as I install NM to make sure it's nestled in the center of the clamp. This frees me up to make other dumb mistakes.

Re: OT - Generator transfer switch

#9

Re: Not alone

Larry in nw ohio

Ray I very glad to hear that you still here and everything went OK, and that you have it fixed. It usually turns out to be something simple and easy. I`m also glad you have a friend to check it over. It`s always best to have someone to recheck your work. Larry

Re: OT - Generator transfer switch

#10

Which goes first?

John in NM

Eyes or memory? :D

For me its memory (age 42), eyes are getting there but I don't need bifocals yet.

Re: OT - Generator transfer switch

#11

Re: Which goes first?

Jerry Nicholson

I have always heard that the memory is the second thing to go but I don't remember what the first thing is.

46? I have had my table saw longer than that!

Jerry

Re: OT - Generator transfer switch

#12

Re: Not alone - response to Larry

Ray Carson - Lawrenceville, NJ

First time for everything. :) Seriously !

I've cut back Romex hundreds of times and never had an issue. What I did was circle the outer jacket with my utility knife perpendicular to the inside wires. What I should have done was just cut a small slit in the end of outside jacket or parallel with the wires and just pulled back the outer cover to the point needed.

In my years of doing home repairs, my job, pretty much everything, I've become a very OCD person and like things done neatly. Hindsight, I should have paid more attention to the details instead of the aesthetics. (sp)

AGREE !!! Fotunately, nothing got fried !! ;) A MAJOR lesson learned.

Ray

Re: OT - Generator transfer switch

#13

Tough crowd !! :-)

Ray Carson - Lawrenceville, NJ

Yes, I'm only 46 yrs. old and I have a lot to learn. Isn't that why we have Wood Central? Not for electrical advice but to learn from our elders. hehe

Touche' :D

Re: OT - Generator transfer switch

#14

My boss used to tell me...

John in NM

That I was getting CRS - and I'd always ask him what that meant again :D :D :D

(First couple times that was an honest answer, seeing as I'm just a simple hick and pretty acronym challenged. Later it was just a good running joke :D )

The nice thing about losing memory first is that by the time one might be tempted to waste money on viagra, they can't remember what they're missing.

Re: OT - Generator transfer switch

#15

Re: Not alone - response to Larry

Larry in nw ohio

Ray The thing I do when wiring with Romex is to score the outer jacket like you do but I just take the blade and lay it on the jacket and press down somewhat and take the handle and move it up and down to the point of cutting through, then do the same on the back. Then I slit it down the front with the wiresto the point of cutting through and take the outter jacket and pull it off. It usually works for me, but it takes practice. But of course there are a bunch of ways to do it. Larry