Since the severe storm went through a couple of weeks ago and we were without power for 5 days, I`ve been thinking about getting a whole house generator. Does anyone have one, what kind do you have , have any trouble with it any other things I should know before getting one. Thanks to all Larry
Start with your fuel supply. Whole-house generators usually require propane or nat gas, although some run on diesel. Propane delivers the most power as using natural gas will derate the output by about 15%. The advantage of nat gas from the main is, of course, that you don't have to worry about running out of fuel.
Whole house residential stand-by's will be in the 17-22KW class. I am in the process of putting in a 20KW Generac with an auto transfer switch and "load-shedding" which allows you to run central air conditioning. Generator cost is in the $4-4,500 range, and installation can run from $2,400 to $5,000 depending on the work needed.
The larger units are all stationary and require installation permits, inspections, and licensed installers.
After hurricane Isabel in 2003 we lost power for 5 days. The most recent Mid-Atlantic storm took us down for only one day, even though we are in a tree heavy rural area.
For us, the cost of a whole house generator was not warranted. I purchased an 8KW portable unit that I keep in my garage until we lose electric. I then wheel it out, about 15' to the side of the house and plug in into a purpose installed receptical with a 10' power cord. The receptical is connected to a load side transfer switch. The generator is capable of delivering 220V/115V at 30 Amps. This is enough for 10 circuits in our house including the well pump, sump pump, a bunch of lights, microwave oven, oil burner, TV, freezer, refrigerator and a few recepticals.
One important thing to do if you go this route is to pay for the installation of a load side transfer switch. This is required by local code, and it ensures that the generator is isolated from the electrical grid so you do not energize the circuits from the utility with the generator. I believe the switch cost me about $500 and another $500 to have it installed.
I keep 2 - 3 gals of gasoline on hand at all times so I can be up and running quickly. Fuel stations are within a 15 minute drive. The fuel consumption is 1 Gallon = 1 and 1/2 hours of run time, approximately. I generally run it about 6 hours on and 6 hours off during a multi-day outage, which are infrequent. This is sufficient to keep the food cold enough in the freezer and the refrigerator so that it does not spoil.
As a Home Inspector I have seen an evolution in generators. It used to be that we saw small to medium sized portable units in peoples garages and sheds and when the power failed, the owner would drag them out and set them up. This required keeping fuel (gasoline) on hand and then running out for more.
A truly terrifying aspect of this setup was how they got connected to the house. Some used cords that plugged into the dryer plug. Some people had cords hanging out of the bottom of the panel. Some people wired slightly more permanent plugs. The message here is, DON'T use any of these. Be sure to get a proper transfer switch. This will either manually or automatically separate your house service from the power company and connect it to the generator. This is very important. Without the transfer switch if you get mixed up you could start the generator first sending power backwards down the power lines and injure the very people trying to repair the system.
So, Mark is right. Be sure you have a proper fuel supply, It may be nearly impossible to even gt to a service station and even if you can they may not have power to pump the gas or may not have gasoline to pump.
Get a quality unit.
Consider the size. Do you need to run the whole house, or can you separate it into perhaps a smaller zone and run a limited number of things. Be careful what you choose to run and not run. I recently saw a house with two panels, one for the generator and one that would not be used during a power failure. The problem was they were going to run the well so they could have water and flush the toilets, but had not realized there was a pump in the septic system. Not going to flush much without that pump.
When we lived in Upstate NY we also had an 8KWH generator and the appropriate electrical hook up. It was more than sufficient to power the critical appliances. If I were to have the need again, I would do it the same way. The down sides are that the generator should be run monthly, IIRC and you do need to keep fresh gasoline available. However, I would see these inconveniences as preferable to a $20K tab for a whole house solution. FWIW
I have a manual transfer switch for 5 circuits. The box has 6 switches, but I connected two for the 220V water pump, so now 5 circuits.
These power the water pump (so I can flush) and 4 other circuits which power the fridge, the other fridge, the freezer and my fish tanks (tropical so need heat and water circulation). Last circuit is for the coal stove so we will not freeze in winter (major consideration).
I do not recommend using the house panel for the isolation. This means you cannot tell when the power is restored to your house. You can see your neighbours, but this may not mean your house is restored.
I have a friend who recently had a 200Amp service whole house back-up installed. This needed a propane tank installation. Give this some thought if you decide on this method of back-up.
If money were not an issue, I would prefer a whole house backup using diesel. This is the most expensive, and since money is an issue for me, I am presently using my 7KW portable unit.
I am considering a bigger portable unit, which will give me a few more circuits. My "learning" is that I would really like to be able to power the internet and computers and TV in addition to the present circuits. We live and learn.
It would, if you could be depended on to remember to do it. A transfer switch, on the other hand, connects your circuits to the grid or to your generator, but never your generator to the grid. The power company rather likes it that way.
I do training sessions for arborists who work around power lines...that would be all of us! One section is about post-storm work. Finding where power is on and what might be energized.
Generators will send power back up the transformer and become high power not just 110v. Arborists and others have gotten electrocuted!!!
Short of a disconnect switch pulling the main breakers, not just flipping them, is a better option.
We were without power as well but being on a secondary road we had power back on the 5th day. I was lucky that the local hardware got in 25 gas powered generators (they were real good about the price $725.00 and said they only marked them up about $5.00 and did it more as a community service) I picked up the first one so I was with power in the second full day but we lost everything in the refrigerator/freezer but saved and cooked most of the stuff in the stand alone freeze (never opened) in our walk out basement which stayed at about 73 degrees. We slept there on a air mattress for two of the 5 days. I will have to put in an electrical box to feed extensions from to the fridge, freezer, 2 wood stoves and a few lights. I also have 1 220 hook up but found that I can run for 11 hours on 7 gallons of gas if I keep the load as low as possible even though the gen has 2 banks of 4 120VAC and 1 220VAC outlet.
I finally had a Generac 7500 kw hooked up with natural gas. Without electricity, my sump pumps would not work, which meant a potentially wet basement...including my finished basement and workshop. After 15 years, I could go away for a weekend without worrying about my basement or calling friends to go check it for me. I originally had a gasoline powered generator to run the sump pumps and freezer, but I had to be home to hook it up...useless for the most part.
Be sure you have it hooked up properly! Anyone not using a properly installed transfer switch is a fool. Make sure it is inspected and serviced regularly, including replacing the starting battery at least every 3 years (I did mine every two...small cost compared to my basement set-up.)
Get one big enough to run what you need...furnace, pumps, microwave, garage opener, etc. AC, if you really want to go big. My idea was to provide basic necessities, not run the whole house as if it was a resort. At the same time, a 10 kw generator would have given me a little more leeway for not much more money.
FWIW, the permanent generator was a big selling point when I sold my house.
Don't mess with the portables if you rely on pumps to keep your basement dry. Unless you are constantly home to hook them up, they are useless.
The one problem I had was in nuts, bolts and screws vibrating loose. Check them all, particularly the throttle linkage and the starter motor. I learned the hard way. A little locktite is good insurance.
I use a portable generator, I put in outlets for the freezer, refrig. and 2 outlets for lighting they do not tie into the house wiring in any way so I don't have to worry about a transfer switch.
We have a 16KW Generac system with auto transfer switch running on a 1000 gal. propane tank as needed. It has been extremely reliable when called upon. It tests itself once a week. Completely installed it was well under $5000-not including the tank and its installation. We don't run any 220v circuits on it like a dryer, AC, electric stove, pottery kiln or the subpanel for my shop. It does power the rest of the house for lights, well pump, frig, furnace, water heater, microwave, etc. It was a little strange the first time I went home to the only house on the street with lights on during a power outage. Hit the botton and the garage door went up and all was right with the world. Nice feeling. The neighbors know we are available when the power goes out.
Yes, relying on people to remember to turn off the main breaker or any breaker is a risk.
It is permissible to run your generator with an extension cord and plug devices into the cord and there is no way you will back-feed with this arrangement. The problem is for some things like a furnace it likely is illegal to have it powered by a plug and socket.
I often wonder with all the "dead" houses and devices such as fridges, freezers, water heaters, air-conditioners, etc ready to turn on just what sort of an electrical spike would occur back-feeding the grid before my 6KW generator tripped out. Maybe Mythbusters could do a test?
that 220 with 25 amps you'd put back out to the street becomes 20,000 volts the other side of the "can". Easily enough to kill the lineman six poles down the line or one of your neighbors who thinks the wire down on his driveway is dead.
And while we are not all stupid when coming to electrical safety, we are getting older. In the stress of the moment it is possible for the best of us to overlook what should be the easiest of precautions. And what happens if the primary(you) is away or indisposed when the emergency occurs. Just asking.
I have a 12KW Generac that powers pretty much everything in the house, except the Air Conditioning. It's wired through a transfer switch, and kicks in after a short (15 seconds?) delay after the power goes out.
Coincidently, we had a storm yesterday that took the power off for about six hours. We were the only house in the neighborhood with power, thanks to the Generac.
Mine is natural gas fueled. Hookup required a permit, a licensed plumber for the gas hookup, and a licensed electrician for the electrical work.
There are also restrictions regarding locations of the unit with respect to eave overhangs, proximity to windows, etc., so check with your local code folks for what you'll need.
you're in a development with houses on 3/4 acre lots where the load would get sucked by the neighbor's A/C, the genset would just trip, unless, of course, the diodes simply got ghosted first. But if the lineman or the guy with the wire in his driveway was the next "load" down the line, somebody's dead.
A general question gets a general answer. Give a detailed scenario if you want an answer to a more limited question.
I commented above about the need for an Interlock or transfer switch. I commented on observing the sort of evolution from almost nobody had a generator to them being common. I want everyone to stop and think for a second. Visualize what the likely scene is when you need the generator. For me, the most common event would be during some nasty weather, often at night. The power goes out. With a portable unit I would have to hope that I drained out the old stale gasoline, had the foresight to store some with Stabil in it and rotated it enough to keep it fresh. then drag it outdoors into the open air. (I frequently hear about people killed by the fumes form the generator in the basement or garage. Don't do that.) Then hook it up through whatever connection I had provided. Then start it so I could get enough lights on to see what I was doing. OOPS!, I meant to turn off the main in the panel first.
I have had people tell me stories about firing off their generator and watching the neighbors house light up but rather dimly. A friend in the country told me he left his running for hours without tripping the main. The power company heard it running and shut it down while they fixed his line. I'm sure there are hundreds or thousands of similar stories, some of them where people got hurt. The point is the tranfer switch may cost about as much as a small generator but could be the most important part.
A couple of other points....I mentioned the evolution from nobody having one to many. The next step in that was I now see trucks running around with "generator service" as one of their offerings. That should tell you something. It might be five or more years between events. I wonder how many of those units will run at all after sitting for a long time? An when yours won't run, neither will a thousand others and there won't be enough service trucks to go around.
And, Gasoline might be the most dangerous thing most of us deal with on any sort of routine basis. So if you are looking at a gasoline powered unit you are condemning yourself to deal with gasoline forever, keeping it fresh, adding Stabil, storing it where you can get to it but not endanger your house, etc.
So perhaps one of the propane or natural gas units that is properly installed and runs once a week to test itself might be the most convenient and most likely to serve you well.
Don't think anyone's taking this lightly, including Bill. But the topic is dangerous in that an incomplete question could lead to an erroneous answer which, in turn, leads to a dangerous course of conduct by someone else. All because "I read it on the Internet that you could do that."
On this subject, "backfeeding the grid", we need to be uniform and intolerant of even the slightest exception to what must be an absolute rule that "You disconnect the main power feed before running a generator hooked into your structure wiring." Whether you do it automatically with a ATS or you do it manually by going to your service panel and tripping the mains (as I did) as part of your generator procedure, it must be done. You can bet that any other response will result in some jackass playing Mythbuster by trying it "just to see" what would happen.
I know several guys who have worked as linemen for many years. They've told me that there was a time when, if 'central' killed the feed, they could count on the down line being and staying dead until they got things repaired; not any more. With the spread of home generators and solar power, they have to treat every wire as live and dangerous.