Re: OT electrical questions
Jason Roehl in Lafayette, IN
As Charlie said, it's possible they moved some circuits around.
However, even if there are two 120V circuits on one two-pole breaker, it's not a problem. An amperage greater than the labeled rating on either leg will trip that breaker, with the bonding strap also killing the other leg. So if it's a 20A, 2-pole breaker used for two 120V circuits, then a 21A load on one of those circuits will kill both, even if there's no load on the second.
It's one way to reduce the total wiring on some circuits. For instance, your workbench could have receptacles every 12", with consecutive receptacles on different circuits. (Say there's 6 of them--all the odd numbered would be on one leg, and all the evens on the other). If they're all wired to the same 2-pole breaker, you could run 4 wires to all 6 receptacles--two hots, a neutral and a ground. The hots would power every other receptacle, but the ground and neutral would be shared. To do the same with two separate 120V, single-pole breakers, you would have to run 6 wires--a hot, neutral and ground to each receptacle. That would mean, for example, two runs of 12/2 w/ground vs. one run of 12/3 w/ground, which would be cheaper.
Jason