Electrical Qouestion

Posts

Electrical Qouestion

#1

Electrical Qouestion

Larry in nw ohio

I got a really odd question. Could a person run two wires on one leg instead of one wire so he could get the right amount of amps to a panel. In other words if he wan`ts to get say 30 amps could he run two #12 wires instead of the one #10. Larry

Re: Electrical Qouestion

#2

Re: Electrical Question

Barry Irby

Yes and no. There are conditions that allow you to do it, but its not as easy as it sounds. The wires have to be exactly the same length and connected exactly as well on both ends. Much harder to do than it sounds like and is really frowned upon if not completely disallowed. At best, its nt a good idea.

Re: Electrical Qouestion

#3

Re: Electrical Qouestion

Chuck in Mtl.

probably against most electric codes as well although there is no technical reason why it will not work.

Re: Electrical Qouestion

#4

Re: Electrical Qouestion

Joe W

The conductors have to be a minimum of 1/0 for it to be compliant with the NEC