OK, so the table saw and the lathe are 220V. There is a 220V dryer outlet in the garage/shop. I have a 10 gauge wire extension cord. I installed a vertical 2x4 for a power pole between the lathe and the saw. I mounted the individual outlets in boxes on the 2x4.
The dryer outlet is served by four wires - black, white, red, and bare ground. I do not have nor do I want to purchase a 4 conductor plug for that outlet. I do have a 3 wire dryer plug and outlet. So I connected the black and red as hots and the white to the third "L" lug. I stuffed the bare ground deep into the box. Good so far?
Now the 10 gauge extension cord has three wires - black, wire, ground, all insulated. What to connect with what in the three wire dryer plug? Gotta solve that before I can connect the saw and lathe outlets. Probably more questions then. Thanks.
Carol Your old drill bit friend here. I`ll try to tell you what I would do with the wiring. You have 3 wires in your extention cord, am I right so far. I would take the male and female end apart to make sure how it is wired, a person can never tell for sure unless you look. OK now the fun starts, find out for sure which ones are the two hot wires and mark that on a piece of paper because I would forget. Now the other one should be ground or neutral, how you want to connect your saw is to make sure you connect the two hot together and the other to neutral. That should do it, now someone can chime in and correct me. Oh Carol this would be a good time to wish you a good Thanksgiving. I told you I forget a lot, I also wanted to tell you that Consumer reports magazine has a pretty big write up on TV`s this months, they have a lot that you can find out what would be best for your situation. Good Luck Larry
Black to Black, White to Red, Ground to ground. You should "re purpose" or mark the white wire. If you have some red tape or a red magic marker, color it red as a warning it is now hot and not a neutral. Or if you don't have red, just color it black.
Black of the extension wire to black in the dryer outlet. White of the extension wire remarked red to the red in the dryer outlet (red beng the 'other' hot). Now is the bare ground in the dryer outlet used as ground and the white wire in the dryer outlet stored out of use? The dryer plug has 'white' marked on the "L" prong. This is what has me confused.
The two hots are black and red from the breaker box. Haven't yet doubled checked where that white wire is tied down in the breaker box. But ground is ground and it is a bare wire and connected to earth.
The safety ground must be continous all the way through to whatever device is plugged into the circuit. This is the bare wire. I'm confused by a 3-pin dryer plug with a L pin. Mine are all 4 pins but are smaller than a stove plug/outlet. Normally, the L pin is a neutral and the ground pin is round whereas the hots are flat.
I also don't understand "stuffing the bare wire deep inside the box". It should be connected to the box and then run to the ground screw, often colored green, on the outlet.
The white wire if it was used as a neutral and not a hot should run back to your electric panel and be terminated on the neutral buss bar with all the other whites. If it is the main panel there will be a brass screw somewhere that ties the neutral to the panel case and therefore ground but you don't need to worry about this. Even though it is electrically grounded by the screw, it must never be used as a safety ground unless it is marked green and connected directly to the panel ground, not the neutral buss bar.
In the configuration you describe the white (marked red or black as Barry described since it is not a neutral) will go to one hot and the black to the other. The green wire from the cord will go to the ground. The neutral wire in the box will be insulated with a cap and tucked out of the way.
If what you are doing doesn't make sense or you don't understand it get some assistance. This is very dangerous if done incorrectly.
Your extension needs two colored hots and earth ground which is green, grn/yellow, or bare. You will not need a neutral in a three wire,220 volt system. The neutral in the four wire system is to provide 120 volts to timer motors and/or lights. Please be careful! Do you have an electrician friend?
At the power pole, three taps come off the output side of the transformer: one at each end of the output coil and one in the middle. Measuring between the taps at each end (the "hot legs") gives you 220 volts; measuring from either end to the tap in the middle gives you 110 volts. This tap in the middle is the neutral, which is attached to the ground circuit at your main panel (but ever after separated).
In all electrical circuits, the electricity flows, so to speak, in a circle: in 110 volt circuits, this circle is made by the hot leg and the neutral; in 220 volt, by the two hot legs.
The white wire in the dryer outlet is the neutral. This is a universal standard in the U.S. If your tools are converted to 220 volts, you don't need a neutral, because they're set up for the electricity to flow in one hot leg and out the other. You DO, as others have said, need an equipment ground. The equipment ground is what saves you when electricity escapes and gets into the frame of the machine.
If your dryer outlet box is metallic, the equipment ground needs to be fastened to the box before it's fastened to the outlet fixture.
You might want to find an electrician who'll do the work for an affordable rate and will let you look over his/her shoulder. Electricity can kill you faster than a non-SawStop table saw
But, at the same time, electrical work is not rocket science. It is one of those areas in which you really need to understand what's going on conceptually, and in which you really need to know what the "rules" are and follow them obsessively, in order to do it safely. If you want to do it yourself, get a good basic book from your library on residential electrical work and get better grounded (ok, I couldn't help it) on the basic concepts and rules. You won't be wasting your time.
There's been a lot of good advice here; each post has had something valuable in it. I'd stop and do your homework, then come back and revisit this thread with your questions.
OK, I got it. Earth ground all the way through to the tool and ground to metal boxes as they may exist. I will cap off the white neutral.
I am not unfamiliar with electrical circuits, but I do need my book for 220v circuits. It just happens to be in Arizona at the moment. I was thrown by the 4 wire outlet.
I appreciate your comments about getting an electrician, but I have been here before, just not as prepared as before. Yet you wonderful people came through and straightened me out. Thank you! And have a great Thanksgiving!
You got it. Black to black and remark the white as a red/black/hot and it goes to red. The saw will run with only these two connected. Connect the third wire to the ground to be sure the metal parts of the tools are grounded for safety and you are golden.
The four wire dryer circuits are relatively new, (ten years or so ?) and are set up because many devices like dryers use mostly 220 for the heating elements and a tiny amount of 120 for timers and warning lights etc. Traditionally they used the ground wire as "neutral" to allow them to pull a little 120 off either the black or red side. Was not a technically good idea even then but it was such a small amount of current they ignored it instead going tot he expense of a fourth wire.
In the panel, most panels are three wire panels. Two hots and all the grounds and neutrals terminate on a common buss bar that is connected to both the ground wire and the neutral. Locally, four wire panels are somewhat rare, but the difference is the grounds and the neutrals are separated in the panel and the strap that "Bonds" them together is removed so that they are isolated or not tied to each other. The ground buss is connected to the panel box itself so that the panel itself is grounded. In this case, the ground should all be on one buss and the neutrals on the other. (In the last few years they have started to demand that each ground and neutral wire be under a single screw on the busses. In older panels they doubled them up regularly. The main thing is each wire be solidly connected.) If they are separated, the neutral with have the large incoming neutral wire connected to it and the large copper ground wire will be connected to the ground. In three wire panels both will be connected to the same buss.
All of this is just background, in your case two hots and a ground and Bob's your uncle.
It is perfectly legal to re-purpose wires by painting or with colored tape. ALL electrical entrances I have installed (MANY) have the white/neutral feed line from the weatherhead to the meter base and from the meter base into the main painted over the black wire. In fact I am not sure they even sell the entrance size wiring in any color other than black in this area. Other times typical recolored lines are used is in the wiring of three - four way lighting switches. Carol has been correctly advised to use the black and white wires as the "hot" wires - remarking the white with either red paint or tape. By the way Carol, it doesn't matter at all if you hook the red "extension" wire to the black or red "feed" wire. In other words when making the extension cord as long as both the black and (re-marked) red wires are attached to the 2 "hot" terminals (gold colored) and the bare wire is hooked to the "ground" (white L shaped) terminal it will be safe and work fine. You can crisscross them in the extension and it will have absolutely no effect. Barry is correct in his statements - In Indiana some of the Utilities still require the neutral be "bonded" or connected to the entrance box along with the ground - in other areas the Utilities will not approve of the bonding and will refuse to hookup until its removed. That is why the entrances are supplied with a loose bonding screw when purchased new.
Chuck, Larry is correct. As far as I know, the entire country operates under the National Electric Code which is enormous and extremely complex and there are certainly local variations, either formally adopted in local codes, or that just persist out of local practice. If Carol were running in conduit, she could run a Black, a Red, and a Green for ground and would be in perfect shape. I have never seen Sheathed wiring common called Romex (a brand Name like Kleenex) that comes with that combination of wires. Fr generations 220 circuits in residential use have been run with a Black a White and A ground (often bare copper) and in residential wiring there is an exception that permits the white wire to be repurposed or converted if you will to a hot wire and only recently have they started to insist that it be marked as a hot. Locally they use black Magic Marker or Black electricians tape (both commonly available) to indicate they are hot wires. In the past, you just had to figure it out for yourself. I actually don't know if they are enforcing the coloring of the ends of the wire where Carol is, but it could not hurt to do it even if it only for her own use. And Larry is right about the black versus red thing. Doesn't matter at all in practice. It is simply a designation as far as using it in the field. If you connect to a black and a red, you get 240, if you connect to the black twice or the red twice, you only get 120. So, to make it easy to attach to one of each, one is black and the other red. If you flip them from one end of the cord to the other, the tablesaw does not run backwards and the dust collector blow instead of sucking, they just run. The incoming conductors are black, and the other often has a red stripe on it called a trace and the white is designated with a piece of white tape wrapped around it or you have to surmise it is "white" because it is connected to the neutral.
I would not give Carol or anyone else a bum steer about electrical stuff. If I am reasonably confident I have the info you need, I will share, but If I don't know, I stay out of it.
Hope everyone's Thanksgiving was as good as mine...or better.
You had it correct the first time, but the forum convinced you to change it. Contrary to popular belief, a NEMA 10-30 receptacle is an ungrounded 120/240 volt plug. The dryer is NOT using the ground as a neutral. It is using the neutral as the ground. (look at the image below and you will see the "L" is labeled with a "W", which is the standard designation for the neutral.)
Even though it makes no difference electrically as you are using it, you need to put the white wire back on the L-shaped lug. You do this because if that outlet is ever used as it is intended, that neutral is a Current-Carrying-Conductor, and you cannot have a current carrying conductor be bare copper.
As used in your extension cord application, the neutral will still serve the purpose of a chassis ground because it is not carrying any current with your cord. It's not proper, but it is better than miswiring the receptacle in the wall.
Also, you do not need to relabel the conductors in the cord. That only applies to in-wall wiring.