Shop is ready to wire

Dustmaker Mike

OK the siding job to the house will be done this weekend, so it is time to get the material to wire the shop.

Before anybody tells me to get a licened electrican I AM going to.

I just have a few questions before I give them a call. First off I have to put a sub panel in the shop area. I want a 100 amp service. What size wire do I need to run? Will 8 Gauge do the trick or will I need to go to 6 gauge? The run is about 50 feet from the main panel and will be all in the basement.

Second question is I have a 100 amp service already at the main panel and want to upgrade it to a 200 amp service. I am thinking all I have to have done is a panel swap and a meter block. Am I missing something?

I am going to buy all the material and need to start getting the cost of things before I head to the electrican. I want to sound a little smart.

Thanks

Re: Shop is ready to wire

#2

Re: Shop is ready to wire

David Hay Denver

Out of curiosity, why are you going to buy the materials? The electrician can probably get most of the parts at a discount with his contractor account at the various supply places.

David

Re: Shop is ready to wire

#3

Re: Shop is ready to wire

Sean Troy

On the swap, it all depends how old the 200 amp panel is. A new Square D Commercial panel is what I went with and don't look back at all. All you need is 12ga. for 20 amp 10 for 30amp. You could go all 10 but that's not needed.

Re: Shop is ready to wire

#4

Re: Shop is ready to wire

Steve Schoene

Aren't you also going to have to increase the size of the service entrance cable when you up grade to 200 amp service for the main panel?

Re: Shop is ready to wire

#5

Re: Shop is ready to wire

Marv

The electricians I know, always mark up whatever they buy and sometimes higher than I can buy the stuff. Plumbers do the same thing.

When I wired my house, I hired an electrician to come and spend one hour with me to answer my questions. I paid him his advertised hourly rate. Turned out to be quite a bargain. I had a list of question written down before he got here. As he answered each question I scribbled down the answer. He even answered questions I didn't know to ask. It actually took less than an hour, but I felt generous and paid him for a full hour. I was surprised to find someone who would again to do that.

Marv

Re: Shop is ready to wire

#6

Re: Shop is ready to wire

Joseph Mulherin, Sr

Mike, Steve is correct about the wiring service to the 200 panel. When I changed out several years ago they came and replaced the service to a higher grade wiring. Turned off the elec. at 7:30am, tore out the 100 amp panel, installed a 12x12" junction box above because the house wiring was undersized for the new codes; ran new wiring to the 200 amp panel, installed conduit from 200 panel to garage/shop and ran 10ga. wiring to 100 amp panel. Was wiring up the 200 amp panel and I noticed someone watching me out of the corner of my eye....it was the city building inspector. He said I seemed to know what I was doing and signed off on the permit....and I had another 2hrs of work left to do. Had the elec turned on at 3:30pm before wife got off work and came home.

I did all this work because I was in construction and knew how to do all of the methods required for proper installations. But, if you have any questions...have the electrician answer them asap or have him do the work, and like the other poster said he could probably get the materials at a discount rate.

Re: Shop is ready to wire

#7

Why I am buying the material

Dustmaker Mike

I can get the material at the rate the electrician would pay to the distributor, so I do not want to pay a markup. I am going to run the shop myself with the advice of an electrician friend.

I am just making sure I understand what I am getting into. I have run wiring in three different houses which was all inspected and passed with flying colors. The main box is the part I do not want to touch.

The house is ~15 years old so the service is most likely not an issue. Again I will have it checked before I proceed.

Thanks

Re: Shop is ready to wire

#8

Re: Shop is ready to wire

Bill Turpin in WNC mountains

Both #6 and #8 are too small for 100 amps. Please consult a code book!

Re: Shop is ready to wire

#9

JL

Re: Shop is ready to wire

JL

When I wired my shop, I did all the wiring myself - except for wiring the sub panel into the main.

The electrician used 2 gauge. I didn't have the tools to handle that easily! Fortunately the run was rather short. I ran the conduit up to the sill plate (above the suspended ceiling).

Re: Shop is ready to wire

#10

Re: Why I am buying the material

Marv

Mike,

Don't know how they do it where you are, but here in California when going from 100amps to 200 amps at the main box, the incoming 200 amp line was huge. Took a 2" dia. ABS underground conduit from the street to my house that was about 300 ft. Three huge conductors twisted around each other barely fit inside that ABS pipe. They used five gallons of grease to grease it and had to pull it through with a 3/4" rope, being pulled with a truck. It might have been the long distance of 300' that dictated the size of the cable, I'm not sure. Or it's a function of how much amperage you'll be needing. PG&E did it all at no charge because I gave them a long list of machines I intended to put in my shop. I didn't do it until ten years later though. They didn't ask and I didn't tell them when. The "don't ask-don't tell" rule worked for me even back in 19&76. What puzzles me is, the power line up on the pole that they hook up to is much smaller than the cable coming up to my house. Maybe someone here can explain that?

Marv

Re: Shop is ready to wire

#11

Re: Why I am buying the material

Ryan Hartje

The wires on the pole are likely mid-voltage or high voltage before the transformer. Higher voltage, need less power(amps). (over simplified but basically correct)

Re: Shop is ready to wire

#12

Re: Shop is ready to wire

Ryan Hartje

#6 maxes out @53' for 100 amp, #4 can go 91 and would be the better bet. Looks like you will need an 1 1/4" conduit minimum.

200 amp needs 1/0 cable minimum with a 1 1/2"- 2" conduit.

Check the numbers out for yourself before installing.

Re: Shop is ready to wire

#13

Re: Shop is ready to wire

Larry in NW OHIO

Mike If your wanting to have a full 100 amps at the shop panel you should go with #2 THHN copper I don`t care for aluminum or something equivalent to be on the safe side. But that is just what I would do. Have a safe day. Larry

Re: Shop is ready to wire

#14

I can 'splain

Barry Irby

Wire size is all about dissipating heat. Electricity generates heat as it flows through the metal. More current=more heat. Copper is a better conductor than aluminum. Copper = less heat or more current. Thinner insulation allows for dissipating heat better. Conduits confine the heat and cause the wires to operate hotter. Hotter = more resistance= less current. Wires operating in free air can dissipate the heat better. If you could chill the wire down near absolute zero the resistance drops to nearly nothing and you could transmit an enormous amount of current on a fairly small wire.

Re: Shop is ready to wire

#15

Re: Shop is ready to wire

David Yoho

Second question is I have a 100 amp service already at the main panel and want to upgrade it to a 200 amp service. I am thinking all I have to have done is a panel swap and a meter block. Am I missing something?

There's more to it than that, Mike. Years ago I did the same thing at our first house. Your electrician will know the requirements for your area but we had to have the power company run a new service cable (tri-plex) from the pole to the house. From there we had to install what they called "four-ott" (0000) service entrance cable to the meter. This upgrade also required a larger solid copper ground wire that terminated outside to an eight-foot ground stake driven all the way into the earth.

Re: Shop is ready to wire

#16

Re: Shop is ready to wire

Marv

Would it be practical to just install a second 100amp service with a separate meter? You'd get two bills each month, but hey.......

Marv

Re: Shop is ready to wire

#17

Re: Shop is ready to wire

FredD

Not only talk to the Electrician first , have him look at the job and don't insult him by intimating you can buy it cheaper then he will charge you.

He has the the License and the knowledge and the expertise , how can you improve on that?

FredD

Re: Shop is ready to wire

#18

I am all for buying cheap

Dustmaker Mike

if it is from the electrican or the warehouse I just need to know what I am buying and a rough cost before I call him in.

Re: Shop is ready to wire

#19

Re: Wire Sizes

JoeW in Detroit, MI

As is the answer to many questions, the answer is - it depends. Are you going to install aluminum or copper wire? For 100 Amp Service 4AWG copper, 2AWG aluminum. For a 200 Amp service, 2/0 copper and 4/0 aluminum. Don't forget 6AWG bare stranded for service ground. Is the shop separate or connected to your house. If connected, ground wire from main house panel is generally acceptable. If shop is separate building, you wil need to establish a separate ground with ground rods,or other means. Neutral in the sub-panel is not bonded to the service enclosure.

Re: Shop is ready to wire

#20

I wouldn't buy anything...

John in NM

Part of the point of hiring the electrician is that he'll save you the trouble of endless trips to home depot buying stuff, then going back for stuff you forgot, then having the guy charge you stand by time while he waits for something else you forgot.

You won't save much buying it yourself, in this contracting market you might not see any savings at all - and you risk PO'ing your contractor. As an aside, I recently had to hire a concrete pumper - the truck was $95/hour, with a $250 trip charge. The trailer pump was only $10 cheaper with the same trip charge and would have required more expensive concrete with smaller aggregate. Six or so years ago that pump truck would have cost $200 an hour or more - and the Albuquerque market isn't even that bad compared to a lot of them.

I would recommend finding out all the info you want to know and asking the inspector if you can sit in on his review when he goes over it. I've seen a lot of contractors not even have anyone there during the inspections, then rant and rave about what a jerk the inspector is. Being there to listen to what he says and discuss any problems just plain gets you an easier pass when he comes back.

Re: Shop is ready to wire

#21

Re: Shop is ready to wire

Ilja Burkoff

First thing you need to do is talk to your local power company. They will give you a spot report. You can do this yourself or get a contractor that will help you with it. The spot report will give you the info on where your new 200 amp pannel will be. You can not assume that it is going in the same spot or that you might have to change to an underground.

With the upgrade to the 200amp pannel you will have to upgrade the survice conductors. If you are above ground, the only thing you should be out of pocket is the mast and the wire in it. If you are underground, your power company will tell you the rules. Also keep in mind, local city/utility add to national coads.

As a contractor, I will leave you with this. If a customer it trying to cut my profit, I will pad some other line item in the bid, or just go on to the next job. I have a number that I like to make every day and don't take jobs that I will come up short. Some will tell you that the industry is slow and you should get it done cheeper because of it. In my experance, the only ones that are slow are the contractors that just are not top notch.

Good luck