Up front, I do not know Canadian code, but I do know U.S. code. I suspect that in this regard they are similar or the same.
The 80% derating applies to continuous loads, and most woodworking tools are not continuous, so this derating is not required. Moreover, most woodworking tools do not operate at 100% load even when they are operating, so this further eliminates the need for the 80% derating.
There is nothing wrong with putting this on a 30 amp circuit, except that #10 wire is a bear to work with at the outlet. If you don't want to mess around with the larger wire, a 20 amp circuit will suffice.
However, if you are going to stick to code, then you cannot put a 20 amp receptacle on a 30 amp circuit, nor can you put a 30 amp receptacle on a 20 amp circuit. The only time you are permitted to mix these is that you can put more than one 15 amp receptacle on a 20 amp circuit, but it has to be more than one.
Also, the length of the circuit is not an issue in your case. The length of the circuit is not sufficient to result in an appreciable voltage drop, nor is voltage drop a code requirement. Additionally, the voltage drop is not dependent on the breaker size, but on the actual amperage draw of the tool.