Cat5 wire and electricity...problems?

Posts

Cat5 wire and electricity...problems?

#1

Cat5 wire and electricity...problems?

Terry Alexander

>I know that for the best TV reception you are supposed to keep your video cable away from electrical lines. In building our new house, I went to great pains to keep those separate.

Currently, we have a wireless router in the shop and we have proved it will not connect to the house (guess too many walls and/or too far). Once the house is wired for internet, we must run a land line (Cat5) from the house to the shop. So, when we switch from our current internet provider (via satellite) to the phone company's DSL, we will have to run a wire (Cat5)from the house back to the shop. (Hope this isn't confusing).

We already have run a 2" conduit from the house to the shop to make the electrical connection from the box on the house to the shop.

Having said/typed all of that....

Is it ok to run a Cat5 cable in the same 2" pipe with the electrical feed to the shop? If so, do we need some kind of "special" Cat5?

TIA for your valued advice.

Terry Alexander in West Texas

Re: Cat5 wire and electricity...problems?

#2

Re: Cat5 wire and electricity...problems?

Warren Johnson

>I would recommend not using the same conduit. There is a great possibility of interference, which would affect the performance of the network. That said, I have installed Cat. 5e cable close to electrical wires and not had a problem. You would be taking a chance and if you experience problems, you could use Plan B. They make a direct burial Cat 5 cable. It should run you about .20-.25 cents a foot.

Re: Cat5 wire and electricity...problems?

#3

Re: Cat5 wire and electricity...problems? *LINK*

Robby Wright in San Marcos, CA

>Terry - It is against the law to run a signal level cable in the same conduit with power cables. There are direct burial versions of CAT 5e rated cables, but the easiest way to do it is to dig a small trench and put in a 1" PVC conduit.

Once the glue dries, take a ball of string and tie a 6 inch square of plastic bag material to the end of it. Making sure the string is free to feed into the conduit, then apply your shop vacuum to the other end. It will suck the plastic and the string through so fast it will scare you. Be sure to stop once the string is though the pipe. It will continue to feed through the conduit until you are out of string and all of it is in the vacuum. DAMHIKT. You can also blow the plastic through with an air nozzle. Use the string to pull a network cable through. You will still have room for a few more cables should you need them in the future, like a TV cable, intercom cable, phone line, etc.

Have you thought about a higher power wireless router and high gain antennas? My router with high gain antennas will reach quite a ways.

Robby Wright


High Gain Outdoor Antenna

Re: Cat5 wire and electricity...problems?

#4

Great tip! :-)

Ellis Walentine, Host

>

Re: Cat5 wire and electricity...problems?

#5

Why it's so

Bill Houghton, Sebastopol, CA

>Imagine that, for whatever reason, the insulation on one of your electrical service lines breaks down - and so does the insulation on the data cable - say water gets through both, or mice get in and nibble the insulation (I wish we'd kept the mummified mouse that ate through the insulation on the wires in our original wiring; I imagine its last thought was, "My, this is surprising!"). You've then fried the circuits on your router, at minimum; could cause a fire.

The same, by the way, applies to low-voltage or any other wiring other than electrical service. Keep them separate. If you decide you'd like to hear when someone rings the doorbell in your shop building, either run a separate low-voltage conduit for the extra doorbell in your shop or do some kind of wireless repeater for it; don't run it through your electrical service conduit.

Re: Cat5 wire and electricity...problems?

#6

Re: Why it's so

Rob Hix - King George, VA

>I agree, keep them separate.

Personally, I think wireless is great, but if possible I use a wired connection. I do a lot of video over Ethernet and it just does not hold up well on the wireless connection. I prefer wired connections whenever possible.

Rob

Re: Cat5 wire and electricity...problems?

#7

Re: Why it's so

Fred Davis

>That reminds me of one of the funnier incidents I experienced building subdivisions in CA.

For the one for McKay homes in Pleasanton ,after the models were up and running, we had about ten production house in various stages with two or three owners already residing.

One day this perplexed woman came to the construction shack and said she had a mystery .

It seemed to her that every time she turned her oven on to bake , the doorbell rang.

I told her I would have the Electrician check it out and told him we had a woman with a over active imagination needing his assistance.

Well it turned out she was right , the Electrician's apprentice had run the door bell transformer supply wire in the same holes in the studding with the 240 V. range supply cable which violated the rule of no low voltage wire adjacent to high voltage because of the possibility of induction.

Everyone had a good laugh and learned a new one that day.

FredD

Re: Cat5 wire and electricity...problems?

#8

I just ran into this.........

Richard Jones

>yesterday in a house and couldn't find any NEC language to back me up. Can you cite a code section? Thanks.

Rich

Re: Cat5 wire and electricity...problems?

#9

Re: Cat5 wire and electricity...problems?

John K Jordan

>>Use the string to pull a network cable through.

If you pull a second string through with the cable and leave it in the conduit, it will be easier to pull an additional cable in the future. Good, strong, braided nylon string should still be in good condition years later.

JKJ

Re: Cat5 wire and electricity...problems?

#10

Another option

A Wright

>in addition to the high gain router/antenna posted in the earlier response, you can also use a wireless repeater to extend the range. If your existing router can get wireless to the "edge" of your house, then you can add a repeater in that part of the house to extend the wifi signal to the rest of the house.

These devices look just like a wireless router, and are less than $100.

Re: Cat5 wire and electricity...problems?

#11

Re: Why it's so

Fred Davis

>

Re: Cat5 wire and electricity...problems?

#12

Re: I just ran into this.........

Fred Davis

>Ric,

About all I can say at this point , is in the years I contracted , it was common knowledge and practice to avoid running low voltage wiring next to high voltage because of the possibliltiy of induction from one to the other,..

If your really interested , I would call your local building department , electrical inspection division, or Jay here on this forum may have the chapter and verse.

FredD

Re: Cat5 wire and electricity...problems?

#13

Fred.........

Richard Jones

>I AM the local building department.............:) As an old sewer and water plant builder, I wouldn't dream of running instrumentation wire anywhere near power wire.

I'd love to find some language in the NEC to disallow this, but can't, hence my question. Even then, I'm not sure I could legally enforce it in a 1&2 FD. In my state, code does not address anything less than 50 volts. Next code cycle, no problem, as it looks like <50va is addressed, but doesn't do the homeowner any good right now..........

Should it be done? No. Can it be done legally? Not sure.

Thanks.

Rich (still looking for that NEC section) in VA

Re: Cat5 wire and electricity...problems?

#14

Re: Fred.........

Fred Davis

>Richard,

at the risk of starting a non productive argument which I certainly don't want to do .

Reread my post , I never said this was a NEC mandated rule .

What I will say and have said , is this occurred in Pleasanton , California , which is the county seat of Alameda , California and in a area of the country that generally leads the nation in Construction practices by several years.

In addition the event happened , just like I said it did and the Electrical contractor was a little embarrassed at explaining to the home owner what really occurred.

As for codes , they exist in that state in several forms , one being the State building code which supersedes all others and the UBC and NEC and National Plumbers code which in all of their various forms and year subscribed to, regulates the local building practice's.

Then there are the methods of work , taught to the Electricians by their Union in a four year apprenticeship program which is far and away superior to say, a Block test formulated and graded in Florida for the rural states like this one I live in.

So Richard , what are you saying , it didn't happen , should or shouldn't be regulated, or just let it go and we could have little ringy dingys all over the place and housewives thinking their new home was haunted?

You did say you just ran into this problem recently , what did you do about it?

Ellis, this was approved by my committee of three house cats that watched me type this and deemed not sarcastic in any way , nor should it be. ;-))

FredD

Re: Cat5 wire and electricity...problems?

#15

Re: The telco guys...

Glenn Madsen near San Francisco

>would look to run their wires at steep angles to the power, whenver they could, to avoid cross talk. Much more important in the DSL era than prior to that time...

Pleasanton has a substantial fiber optic hub there, for almost all of the carriers... A fairly modern place, they are building for the next decades.

Re: Cat5 wire and electricity...problems?

#16

No argument here

Richard Jones-

>Fred,

You didn't say anything about the NEC, I did. I was looking for ammo, i.e., a code section that I could cite to a contractor. I thought you might help. No hidden agenda here, no baiting.

Our state also has journeyman program, with mandated continuing education. A good thing, for sure.

What did I do? I told the contractor that I couldn't find anything to prohibit him from doing what he was doing, but that it was sure stupid and would probably cost him a lot of time and bucks to come back and troubleshoot future problems. I'll go back next week on a different inspection to see if he fixed it. Should it be regulated? Until this week, I thought that something so common-sensical didn't NEED to be regulated.

If you say the event happened, then as far as I'm concerned, it did. I have no reason to doubt you.

I see lots of stupid stuff on a day to day basis, but I can't legally prohibit anything that is allowed in the code. Doesn't make it right, but it does make it the law, and the judge here doesn't like me making up laws.

If I offended you in any way, I apologize, that was not my intent.

Richard

Re: Cat5 wire and electricity...problems?

#17

Re: The telco guys...

Fred Davis

>Glenn , your slipping , I said Pleasanton was th county seat of Alameda county and I know better then that , I worked there for twenty years or so, I must of had the Alameda county FAIR on my mind , since that is where it is.

I hate it when that happens , and it happens more often then not lately . ;-((

FredD

Re: Cat5 wire and electricity...problems?

#18

Re: No argument here

Fred Davis

>Richard ,

no offense taken and the Contractor you are talking about has to be very dimwitted to keep doing something that you told him , could cost him down the line , the least he could do was appreciate the tip .

I have know many Inspectors who would increase their scrutiny after something like that was ignored.

It's true Judges don't like you making up code rules, though I have known more then a few Inspectors that did.

The judges prefer to keep law making in their bailiwick I suspect.

What is maddening to a code enforcement officer is ,even though the subject is not addressed in the code, common sense should rule in the absence of code book reference.

Now for a question for any who knows on the subject of Induction.

I made my wife a fairly decent China Cabinet and lighted the interior with low voltage Halogen lamps made for that purpose.

What is a mystery to us and we thought the Cats were doing it for awhile is, when lightning strikes within a few miles of us , it triggers the step down Transformer to light up the lamps.

While this may sound trivial on the surface , what it does is cause the lamps to be on for a lot longer then we normally would use them and they are hot little buggers.

So , is this Induction at work , radiation from lightening or what?

Any informed guesses appreciated.

FredD

Re: Cat5 wire and electricity...problems?

#19

Re: No argument here

Dan Donaldson

>Need a bit more info on what you mean by "triggers" the stepdown transformer. How do you normally turn on the lamps? if it is one of those touch sensitive type of switches where you touch some kind of a metal part to cause the light to turn on, then it makes sense. The way this work is that your body changes the capacitance of the circuit, and/or acts like an antenna and couples in a signal, most likely 60 hz from the house wiring. If you touch a high impedence scope probe with a finger, you can see some fairly large voltages show up. This same effect can be caused when lightning strikes. It is a large electromagnetic pulse and can be picked up by one of these types of circuits to trigger it. Not sure how to prevent it unless there are some kind of sensitivity adjustments or possibly a way to make the plate that you touch smaller or shield the main circuitry. Would take a bit of experimentation to figure out.

Re: Cat5 wire and electricity...problems?

#20

NEC

Tim Greif - West of Chicago

>Richard.

The code most certainly addresses the issue. It is NOT allowed to run low voltage stuff in the same raceway as power. I�m in Europe right now and not able to look it up. I�ll get back to you on this when I return next week. In the meantime, do a search on Class 2 and Class 3 circuits.

Re: Cat5 wire and electricity...problems?

#21

Re: NEC

Richard Jones-

>Tim,

I did find some info in chapter 8, Communications, but again, our state code dispenses with anything less than 50 volts, so not sure if this would apply. The language about no low voltage in with line voltage is in there, as you say, just not sure if I can call that one or not. Plus, the IRC is no help here, as nothing less than 120vA is mentioned. Maybe I can get some more input over at the ICC forums, amongst the codeheads......:)

Thanks for the help, I'm still looking.

R

Re: Cat5 wire and electricity...problems?

#22

State codes...

John in NM

>In New Mexico, I believe the state code only supercedes the code books when it is more restrictive, not less, may be different elsewhere of course. Closest section I could find in the moments I devoted to it - ;) - is Section E4204.1 in the 2003 IRC, which is of course out of date now. The cross referencing provided lists NEC 725.55 as the coresponding section of NEC. The trouble is E4204.1 is sufficiently vague in wording that I couldn't say whether it would apply or not. However, if I wanted to put both cat 5 and line in one conduit, finding this section would keep me from doing it.

As an earlier poster pointed out, its really easy to put in a second conduit.

Re: Cat5 wire and electricity...problems?

#23

Re: No argument here

Fred Davis

>Dan,

The lamps are "normally " turned on by touching a bottom hinge on a upper door at the left end of the cabinet which I ran one lead from the transformer to.

That is why we at first thought the cats somehow were touching the hinge, it turned out they were innocent.

This is a fairly common way of turning on lamps , energizing circuits and so on.

So I was surprised that lightning discharging the Transformer was not a more widely known phenomenon.

"large electromagnetic pulses" are everywhere, really big ones at a Nuclear bomb explosion or implosion, though we haven't had one of those close for a while. ;-))

FredD

Re: Cat5 wire and electricity...problems?

#24

Re: Cat5 wire and electricity...problems?

Scott Crumpton

>I have a similar setup with my shop about 100ft from the house, with and additional 50 foot of building to get to my computer. The cable modem, 4 port router and AP are at the house. Living in lightening prone Florida, a 150ft lightening catcher connected to my computer was not something I wanted. What I did was to run optical fiber from the house all the way through the shop to where the computer is located. At each end there is a media converter which connects to the router at the house and another 4 port switch at the shop. I also pulled a cat5 as a backup, but it sits unconnected.

A long time back prior to having a home network, I took a direct lightening hit on a tree 10ft from the shop. The induced currents blew out 3 GFCIs, 2 surge suppressors, and one switch was blown off the wall. All of the computer equipment was at that time plugged into a single surge suppressor power strip (a common ground point for everything). This power strip was plugged into yet another surge suppressor (one of the ones blown out by the strike). None of the computer equipment was damaged. The common ground point for all the equipment prevented any damaging potentials between components. This experience was the reason that I went to the effort of using fiber between the two buildings.

I suspect that there won't be any issues with fiber in the same pipe as the electrical service.

---Scott.

Re: Cat5 wire and electricity...problems?

#25

Re: No argument here

Dan Donaldson

>It can depend on a lot of different things. The exact layout (if the wire to the hinge from the transformer is long, that could have an effect as could the specific orientation of the wire horizontally or vertically), the sensitivity of the circuit in your application, the grounding structure of your house and the local area. I am not sure how widespread the issue is, but regardless, if it is affecting you, then it doesn't matter because for you it is 100% common ;-)