Jim Moore
>OK, here is a detailed explaination of how I see the Naational Electricl Code requires this circuit to be treated. Warning: this could be verying boring to many readers, and those in the know, are aware that the NEC overkills everthing. Non the less, here it goes.
NEC 430.6(A)(1) states that Table 430.248 must be used to determine ampacity of conductors rather than the actual ratings of a motor. Exception #3 of the same does state that we can use the full load curent marked on the nameplate if BOTH the horsepower and FLA are shown on the nameplate. Let's assume they are for this discussion.
NEC 430.22 states that a single motor conductor in a continuos duty application shall have ampacity of not less than 125% of motor's FLA as determined by 430.6(A)(1). Again, Exception #3, for our discussion, will let us use the FLA numbers on the nameplates as given by the orignal poster.
NEC 430.24 states that if more than one motor is served, the feeder ampacity must be figured by adding 125% of the largest motor FLA rating with the sum of all other motors FLA ratings as determined in NEC 430.6(A)(1).
NEC 430.22(E) discusses duty-cyle service and nameplate rating percentages and provides a table for clarification. In the table, it states that any motor application shall be considered as continuos duty unless the nature of the apparatus it drives is such that the motor will not operate continuously with load under any condition. This would be like an elevator or such.
While we would all agree the table saw would probably not operate under load continuously, the dust collector could.
So applying the above we have:
The 2 1/2 HP dust collector has a nameplate rating of 13 amps at 240V.
The band saw is rated at 10 amps at 240V.
The table saw is rated at 13 amps at 240V.
Let's look at what he has now: DC and BS on same circuit.
DC is largest motor, so take it's rating time 125% to get 16.25 amps.
BS is the samller, so take it at 100% for an additional 10 amps.
16.25 + 10 equals 26.25. This feeder should be rated greater than 26.25 amps. Probably 30 amps, not 20 amps as he curently has.
If you add the table saw, it increases the ampacity requirements by another 13 amps to get 39.25 amps. Now your pushing it, but you could use a 40 amp rated feeder to feed all three pieces of equipment.
You are not allowed to derate continuous duty motors in most cases. And we would agree that the table saw and the bandsaw would not probably ever be run at the same time, assuming a one-man shop. And realistically, we know the that in the real world, the 20 amp circuit will be fine for the DC and the BS, or even the DC and the table saw, since neither saw will run at FLA very long.
But the Code does not address real world situations. It looks only at the maximum that could happen. So if you were figuring this circuit by Code, you would need to put a feeder in that is rated over 26.25 amps for the DC and BS to run together. For the table saw and DC together, you need a feeder large enough to serve 29.25 amps.
I'm not going to tell you to change the DC and BS circuit because as long as you run them as we all typically do, you will have no problesm. The TS should be on another circuit though.
As far as derating of conductors, goes, let's leave that alone. That is getting way too complicated for this forum. Just be aware that you cannot just fill any conduit up with as many wires ae you can get into it. The Code will make you derate the ampacity rating of the conductors in a pipe once you reach a given set number of wires.
Finally, as far as connected and calculated loads are concerned, NEC Article 220 III requires feeder calculated loads shall not be be less than the sum of the loads on branch circuits supplied, after any applicable demand factors are applied. There are not demand factors for motors in the NEC that I know of. The smallest calcualted load of any motor will be 100% of its FLA.
Enough of this confusion. Put the TS on its own circuit, start the DC first before staring the BS. And you should be fine. Just not in compliance with the NEC.