110V from 220V?

Posts

110V from 220V?

#1

110V from 220V?

Joe in Tallahassee FLA

>Can I hook up a 110V receptacle from the 220V outlet that runs my table saw? I want to install a router under the saw extension table. The saw is in the middle of my shop and I have a 220V floor outlet at the table saw but did not think of running a 110V line when I poured the slab. Can I just somehow use one of the legs off of the 220?

Thanks,

Joe

Re: 110V from 220V?

#2

Looks like "no"

Denis Ch�nard, Orl�ans, Ont.

>If you've run a two conductor cable to the TS, then both are hot. While you will get 120 using one of the hot leads with the ground, I'm pretty sure this is not allowed by code, and might be dangerous to boot.

If you had the insight of running a three conductor cable, then you do have a neutral that can be used with one of the hot leads to give you 120V safely. Just make sure that the draw on the hot lead you choose does not exceed the breaker's capacity (actually 80% of it to be on the safe side).

Hope someone more knowledgeable than me will chime in...

DC

Re: 110V from 220V?

#3

Yeah, you need a neutral wire.

Eddie Pacheco; San Jose, Ca.

>Like Denis states, DO NOT use one of the hot wires and ground to get your 110v. That's a recipe for a big ouch.

Try to run a leg of equal gage white wire in the conduit you already have. This will be difficult especially if you used 1/2" dia. conduit, but it's not totally impossible. It might take a combo of wire snaking, strong string, a good smooth taping job of string to wire, liquid soap, and finally luck.

Re: 110V from 220V?

#4

Re: Yeah, you need a neutral wire.

Sam Layton

>You have to have two hots, a neutral, and a ground to do what you want. It may be very hard to run a neutral at this point. You could pull all of your wires out, and run 4 new wires if your conduit will allow.

Sam

Re: 110V from 220V?

#5

Re: 110V from 220V?

Joe in Tallahassee FLA

>I get it. Dang! Guess I'll be running an extension cord when routing, at least until I get around to pulling new wire.

Thanks much for the help.

Joe

Re: 110V from 220V?

#6

step down transformer...

Phil in NJ

>You could install a 220v to 110v step-down transformer... of an appropriate rating.

Might be cheaper to just run another circuit, but it is an option...

-Phil

Re: 110V from 220V?

#7

Re: 110V from 220V?

Larry in NW Ohio

>Joe If you ran single strand wire, it would be no problem to run the wire you need. Could you specify what you have in your concrete for conduit and wire. Larry in Ohio