Question about tool power needs

#1

Question about tool power needs

Stephen Kirk in Quakertown, PA

>I'm looking pretty seriously at adding the Rikon 10-325 14" bandsaw to the shop sometime soon. I'm not sure what they mean when they say it supports 115/220v power. Some reviews say it's pre-wired for 110, but then in the product specs I see that it's really 115. I only have a 110 line in the shop (and now more circuits to run 220, unfortunately - a 60 amp service is a tad limiting). Would I be able to run a 115v wired saw on a 110 line? Assume that it's likely a pretty light 110 line too (probably 30+ year old wiring in the house). My old 1 1/2 hp table saw doesn't seem to have any problems.

Yes, I do want to upgrade the house to a 200 amp service and run new lines to the garage/shop, but that's not in the budget right now.

Thanks in advance!

Re: Question about tool power needs

#2

Re: Question about tool power needs

Bill Howatt

>The line voltages provided by the utility have slowly increased over the decades but the old terminology persists.

Line voltage used to be nominal 110V then went to 115V, sometimes you even see 117V specified and in more modern times 120V. The actual voltage provided can easily swing between 115V and 125V during the day. The 220V specification is based on 110V. It is double the "lower voltage" number since the 120V is obtained from half the 240V. Like 120V, 240V should be the number used when talking about the higher voltage available.

Your saw will be fine on the 120V but if you have a very long run of wire from your panel to your shop you might find the voltage drop to be excessive when the saw is running under heavy load. By switching the saw motor to 240V (220,230V) you reduce the current by half and thus it will work better on a long line whose wire size is marginal. However, you need to provide a 240V circuit!

Other option is to run a 120V circuit from the panel using #12 wire if your existing wire is #14. This will minimize the voltage drop.

If your TS works fine, I don't believe you will have trouble with the bandsaw.

Bill

Re: Question about tool power needs

#3

Re: Question about tool power needs

Larry Clinton At Frankfort (Central)., Indiana

>Bill is completely correct. I am one of the old timers. I learned to house wire in the 1950's and make extra money adding outlets and installing porch lights in my small town as a teenager. I still often refer to the voltages as 110 / 220 volt or 115 / 230 instead of the current 120 / 240 correct nomenclature. However the "line voltage" is actually determined by the utility company by the tap they use on the transformer on the pole that feeds your entrance. This is currently accepted and adjusted to be a nominal 120 VAC from either "hot" leg to neutral and 240 VAC between the "hot" legs. You should have no problems running the band saw if your TS is running ok. There are a LOT of houses (some with shops) still running on a 60 amp entrance. Remember a 60 amp entrance provides 60 amp at 240 Volt - or 120 amp at 120 Volt. Most homes actually never load the 60 amp circuit. The reason the new standard has became 200 amp is due to many homes running air conditioning, electric ranges, electric water heaters and clothes dryers. Obviously if you have an electric heat pump or electric heat the 200 amp service is really needed.

Re: Question about tool power needs

#4

Re: Question about tool power needs

Larry in NW Ohio

>Stephen If I were you I would get a basic book on eletricity and read up on it. Since you have a shop, no matter how large or small it is, it would be very helpful to learn a little about electricity. If you need some wiring done you will at least know a little of what the eletrition is doing. Good Luck Larry in Ohio

Re: Question about tool power needs

#5

Re: Question about tool power needs

Stephen Kirk in Quakertown, PA

>Thanks, that's a lot of great information. Sounds like I should be OK with what I have. Now just to decide if the Rikon is the right saw for me.

I should see if it's feasible to put a 240 circuit out to the garage. I have the issue of only having one line in the garage and that's a 120 line. So, I can really only run one thing, plus my lights, at a time. A second line, heck 2 more lines, would be nice but my circuit panel is full up.

Re: Question about tool power needs

#6

Re: Question about tool power needs

Stephen Kirk in Quakertown, PA

>Well my only big devices are the electric stove and electric dryer. The house is heated by wood and oil and my hot water is oil fired (no hot water heater). I just have a problem in that my electrical panel is full up, and some circuits a little overloaded. We tracked most outlets and lights to come up with a map and things are a little odd in the house (not uncommon, from what I hear).

I should have an electrician give me some recommendations on getting more/better power around the house and especially out to the garage. I wonder if there is a way to re-arrange circuits without upgrading the whole service or panel.

The explanations were helpful, though. Thanks. I don't feel so clue-less anymore.

Re: Question about tool power needs

#7

Re: Question about tool power needs

Stephen Kirk in Quakertown, PA

>That's sounding like a good idea. I have some home books which include wiring that I should re-read. I'm glad the people here can make things a little easier to understand, though.

Re: Question about tool power needs

#8

Re: Question about tool power needs

Barry Irby

>Your panel may have "take off lugs" that allow an electrician to set a subpanel. If not, he may be able to use the dryer circuit to power a subpanel and the branch that to the dryer and the shop. I prefer to be sure the subpanel is fused through the mains to be sure you don't over load the service entrance cable. For years I ran my shop off the dryer circuit. On laundry day I would occasionally trip the breaker because the dryer and the TS were both on at the same time. I got tired of it and tired of being the goat who turned off the dryer and did not turn it back on and added a shop circuit. (Who knew the dryer did not come back on when you reset the breaker. Picky, picky, picky.)

Re: Question about tool power needs

#9

Re: Question about tool power needs

Carol - now in NC Nebraska

>Trot off to the library and get the Black and Decker book on wiring. Lotta color pictures and laid out in a useful format. If you do that, bet ya buy one! I got my electrical experience from my uncle when I was a kid, wiring switches and outlets (like Larry!).

There is one other booklet I found years ago at a borg on wiring circuits. Don't know if it is still available, but when I want to wire three way switches, that's the first thing I dig out.

Re: Question about tool power needs

#10

Re: Question about tool power needs

Larry Clinton At Frankfort (Central)., Indiana

>Steve, you can add a "load center" to the existing entrance panel - This is not a real expensive or difficult option if you have the ability to do it yourself. This consists of installing a new 240 Volt double breaker in your existing box of say 50 amp capacity. (I know it's currently full), so this requires removing the two current circuits that are hooked to the breakers you remove. These will have to be rerouted to the new box. The new load center can have several breakers -2 of which will feed the old circuits. The load center will have to be fed with the proper size wire and ground wire. This can be installed near the existing entrance, or in a remote location. additional breakers and circuits, both 120 and 240 Volt can then be fed from the load center (after installing appropriate breakers). I personally don't use them as I can install a new 200 amp entrance for less than $250 in material, but may be a relatively inexpensive way to get by. The load center can be re-hooked to the new 200 Amp service if/ when you upgrade. (I have done residential, commercial and industrial wiring for several years before retiring.) As a caution, I would check with your local building inspector prior to proceeding as some areas have different code requirements. A load center is pictured in the link to Amazon - http://www.amazon.com/dp/B000H5Y86A?smid=A1SV1BYDTUK2Z5&tag=nextag-tools-tier4-20&linkCode=asn

Re: Question about tool power needs

#11

Re: Question about tool power needs

FredD

>That response to your electrical problem, namely hook it up to the drier circuit, is illegal and will give your home owners insurance a loophole to duck paying a claim if you have a house fire and the adjuster sees that hookup.

That reponse to your question is the number one reason why woodworkers work with wood and electricians get paid a lot more.

Get a licensed electrican to give you your options, then you will know for sure and can sleep better for knowing it.

FredD