220V 3-way switches?

Posts

220V 3-way switches?

#1

220V 3-way switches?

Jerry Klug

>Setting up my chip collector I can walk across the shop and start it up or get a remote that I will probably misplace. I was wondering if there is a 3-way switch like I wired into my house lighting, only for 220 volt, so I could start the collector at two sites? If so, what do I ask for at the volt store?

Re: 220V 3-way switches?

#2

Re: 220V 3-way switches?

DocJim...Fayetteville, NY

>You can use a regular 3 way for 120...you only have to switch one of the hot leads. There is always one hot active. Be sure to use a 220 breaker.

Re: 220V 3-way switches?

#3

Re: 220V 3-way switches?

Jerry Klug

>Do I still retain the start/stop switch on the collector for power off when I am through in the shop?

Re: 220V 3-way switches?

#4

Re: 220V 3-way switches?

DocJim...Fayetteville, NY

>There is no need to. Just make sure to unplug it before working on it, if you have to, just like with any tool, because the one hot is still active even with the wall switch off.

Re: 220V 3-way switches?

#5

Ask for 277-volt...

awh

>277v, 3-way switches are used all the time in commercial office buildings.



Tony Haukap

Home Page - http://www.cyberspace.org/~awh/

--

Re: 220V 3-way switches?

#6

Re: 220V 3-way switches?

Jay St. Peter - SoMD

>I made my compressor work that way. I put switches in the garage and shop since they are both plumbed. I wired a 110V circuit in typical 3 way to a receptacle. I then used a power relay (switched by the 110V power) to switch the 220 lines to the compressor. It works out nice since I put the power relay in a box with a 110V plug, 220V plug, and 220V receptacle. So no strange wiring inside the walls.

Jay

Re: 220V 3-way switches?

#7

Another way

Gene Gauss

>I have five DC locations (blast gates) in my shop. I wired 220 volt2 to each of the machine outlets at those locations with AWG#12-3+G. I connected the five 220V outlets in parallel between the black and red wires, which were fed from one double pole 220volt (20 amp) breaker in the service panel. I wired from the black wire in each outlet box to a 120 Volt switch located in the same box and ran the white wire from the other side of the switches in parallel to the coil of a 120 volt relay which applies power to the DC. Turning on any switch, which are all located near the blast gates, turns on the DC. I mounted the relay in a separate enclosure. Gene Gauss

Re: 220V 3-way switches?

#8

How quickly they forget

Rick Christopherson

>Well, it was just two weeks ago on this very forum that I really took it in the shorts for informing people that it was not required to replace the integral, single-pole control switch on a tool when they converted the tool to 240 volts. Some people even responded to this information as though I was being irresponsible for even suggesting such a thing. So where are all these posters today?

A 3-way switch is not integral to the piece of equipment it is controlling, and it only breaks one conductor. This means that one of the ungrounded conductors is not being opened when the switch is opened, yet nobody is questioning this today. Why not?

Just in case it is not obvious, this is tongue-in-cheek, and I do have a smile on my face.

Seriously though, tonight I did just make a cursory review through Article 404 and I cannot find any requirement for a 3-way switch to break both ungrounded conductors, even when it is not integral to the equipment. That being said, you can use a standard 3-way switch to control your 240 volt load, with one caveat.

Because this switch is controlling a motor, it is not likely that the switch contacts will be rated for motor duty. As a result, the contacts could fuse and the motor could remain powered after the switch is turned off. Being a dust collector, this is not a huge safety risk, just know that the switch may have a limited life.

Personally, I would prefer to use a motor contactor and low-voltage controls at each of the control locations. This is pretty simple. You need 3 conductors going to each control point, and they can be as small as telephone wire. All of the On buttons are connected in parallel with the contactor relay, and all of the Off buttons are connected in series with the relay coil. Any On button can start the system, and any Off button can stop the system.

Re: 220V 3-way switches?

#9

Re: How quickly they forget

Larry in NW Ohio

>Someone said to use a relay, and I think Rick is saying this also, to early for the ole brain cells to start up yet. I think to start a motor as big as 20amps and over I would use a relay of some sortor a motor starter, which could be called a relay. Then you can use light duty toggle switchs such as regular light switchs. But be careful. Larry in Ohio

Re: 220V 3-way switches?

#10

Re: How quickly they forget

Jay St. Peter - Southern, MD

>Thinking about it, your suggestion is what I would do for a DC if I wanted it hard wired. I used a cheap 110V remote control to switch a power relay on my DC. My remote receiver is actually wired into the lighting circuit so the mysterious false triggers on cheap remotes don't happen when I'm not in the shop.

The air compressor switch is used far less often, so it is wired in near the doors to the garage and shop.

Jay

Re: 220V 3-way switches?

#11

Re: 220V 3-way switch

Mark Mandell - Gone Round In Jersey

>Morning Jerry.

I'll reinforce what Rick and others have said about a motor relay, as that is exactly how my system was originally set up.

My DC is in my garage while my shop is in the basement. One of my Sparky friends came over and put in a 220 motor contactor that is controlled from 3 locations, two at different locations in the basement shop, and one in the garage. The contactor is controlled by a 110 relay which is controlled by the hard-wired switches, and the DC motor is plugged into the single receptical on the contactor box. We set it up that way so that if I were making chips in the garage, I could open a port in the garage and fire up the collector to keep from covering SWMBO's ride in dust.

The system has worked flawlessly. I did away with the garage port in the duct when I upgraded my system, but kept the 3rd switch (4-way for 3 locations) to be able to check the bag seal after I empty it. My friend chose the electrical fittings and said he preferred a 110v control circuit even though there were low voltage switch units available.

mm

Re: 220V 3-way switches?

#12

Re: 220V 3-way switch

Larry in NW Ohio

>I used a motor starter that was taken out of industrial equipment made for 440volt but the coil is for 110 volt. I got it from a surplus dealer a few miles away and only cost me $20 with enclosure. This is the better way to go for your bigger equipment. I forget but I think it`s rated for over 50 amps, so that should take care of a 3HP DC. Larry in Ohio

Re: 220V 3-way switches?

#13

Re: 220V 3-way switch

Jerry Klug

>Thanks to all for the input. I have done a fair amount of wiring in home remodels but 220V can creep me out. I guess that extra hot lead is what does it. I was able to go to the BIG CITY today (in Central OR, that is Bend, Pop 70,000) and was able to get a unused but returned and cosmetically marred relay for less than half price. Now all I have to do is wire the three way switches on 110v to the coil side of the relay and I can start and stop my D/C at the lathe and the sanding station.

Thanks again as your input gave me a good starting point to know what to ask for.