Home Articles Forums Gallery Marketplace Videos

WoodCentral Forums

Knowledge You Can Build On — Est. 1998

Support WoodCentral when buying things you need

OT - Electrical question.?

Posts

Re: OT - Electrical question.?

#26

Doesn't apply to fuses

Mark Goodall - ATL - tooljunkie

>Our houses in Quebec didn't have the split circuits in the kitchen, but my house in Ontario did. But it had glass fuses, so if I remember correctly, there was no way to have a dual-glass-fuse like you can have a dual circuit breaker.

In fact the first house I ever lived in that had circuit breakers was here in Atlanta. All the others in Canada had glass fuses.

Happy Woodworking!

Re: OT - Electrical question.?

#27

You've illustrated the common error....

John in New Mexico

>as far as I understand it, a dual pole bridged handle breaker is only required if the neutral is shared. The dual pole breaker is more to ensure that the two hots are at 180 degrees to eachother and thus will not overload the neutral. The confusion is due to the common practice of doing this sort of thing with 3+ground wire. Your old house with the fuses probably used two neutrals to go with the two hots (or the electrician knew enough to put them on opposite eachother).

John

Re: OT - Electrical question.?

#28

Yes.

Rod Peterson -- Ormond Beach

>Even on the peninsula which houses the range and has countertop space to the right of the range. Although I don't have a rectptacle on the right side I could have—never thought of it), I do on the backsplash on the left. Since the quartz is contiguous at the back of the range all the way from the counter on the left to the short counter on the right, I'm sure that just counts as one. And the receptacle is close enough to the range to be within counting distance of the short section, too.

Rod

P.S. the kitchen can be seen at my website in the This Old New House section.

Re: OT - Electrical question.?

#29

What is a circuit?

DB

>I agree that you can have as many circuits going through the box (up to the limit of the size of the box) as you want But if you can utilize the power from different circuit breakers in the same box then you need a common trip circuit breaker. A light operated by 3 and 4 way switches is only part of a circuit. You can have more than several lights operated by several different 3 and 4 way switches on the same circuits.

Here is my difination of a circuit (called a branch circuit by the NEC. The circuit starts at the circuit breaker and goes through the various outlets, switches, and lighting fixtures.

What is your difination of a circuit?

Re: OT - Electrical question.?

#30

Electrical question.? Wow !! I didn't mean to....

Ray Carson in Lawrenceville, NJ

>start a thread this big. Sorry.

I appreciate all the responses and decided that breaking up the existing circuit is the best solution. It's actually not going to be that difficult.

Ray