HeatherA in Alaska

>Hello,

I purchased a 3hp unisaw a while back. I didn't know anything about them at the time and actually had gone to see about a bandsaw but the seller made me a good deal on both saws. I noticed that it had a locking plug and asked if it was 110 or 220. He said 110, that the former owner of the saw put on a locking plug so tht it would not get pulled out of the wall. So I got it home and cut off the plug and put on a regular one. Of course nothing happened. The motor clearly says 220 (actually 230). I don't have 220 power to the garage. Questions

1) I have heard that you can change the motor wiring so that you can run it on 110. Is that only on motors that say 110/220? The saw is a 34-802 with the 3hp baldor motor.

2)The other option would be to run a cord from the dryer. It would be about a 40 foot run. It that do-able? I figured I would need a 10g cord. If so, would I have to put a different plug on the extension cord to fit the dryer outlet or are there plug adapters?

Thanks,

Heather

Re: power to unisaw

#2

Re: power to unisaw

Howard Norman-Prescott, AZ

>Heather, you are correct you can only rewire motors that are 110/220 not 220 only motors.

As far as running a 40 foot extension cord, yes you can do that. That is a long cord but a #10 cord would probable work OK. You would want to install a plug that matched your dryer outlet on the one end. I am a firm believer in twist lock plugs so I would use them on the saw end. I don't have the reference chart at hand at the moment to tell you which one to use. This isn't the best solution but it will work. Any chance of getting a hard wired run from the dryer to the location of the Unisaw?

Howard

Re: power to unisaw

#3

Re: power to unisaw

Larry in NW Ohio

>Heather Instead of coming off the dryer plug, would it be possible to tap in at the service panel itself. I think the best solution is to get 220 to the saw. Check out the various runs you could make and of course take the shortest easiest route. Larry in Ohio

Re: power to unisaw

#4

Re: power to unisaw

Larry Clinton At Frankfort (Central)., Indiana

>Yes Heather you can run an extension from your dryer plug with no problems at all. I have a fairly large shop but I am disorganized and can't figure out where I want my equipment. I have 3 or 4 220 volt extension cords and all my equipment on mobile bases including my 3 hp Unisaw, 3 hp planer, 4.8 hp band saw & 5 hp planer. I used #10 gage for the jointer, band saw (it is rated just under 30 amp) and Unisaw and 8 gage for my 5 HP planer. All are about 35' long. The 3 HP 220 Volt Unisaw motor is rated at about 20 amp - 10 gage is ok for 30 amp so you will have negligible voltage drop. I have 10 or 12 220 outlets in my shop but still have the Unisaw plugged into extension cords most of the time as I keep it near the center of the shop.

Re: power to unisaw

#5

Re: power to unisaw

Jerry Burns

>Heather I just did a voltage drop calculation for a 50 foot cord at work the drop was 2 volts for 50 foot for a 3phs load for the single phs load that you will have the drop will be more but not more then 5-6% with is well with in the limts for the saw uh yes use #10 copper wire

Re: power to unisaw

#6

Re: power to unisaw

HeatherA in Alaska

>Thanks for the help. I don't think that I could add another circut to our panel, It seems like we don't have enough power as it is (my assumption could very flawed.) Whenever I power up my lathe it dims the lights in the house. The circut box is about 3 feet from the dryer. I will try the cord. We only have 100amp service to the house. I am worried about what is going to happen when I try to turn and use my new dust collector. I may have to add additional service to the house .

Heatner

Re: power to unisaw

#7

Re: check with the electric utility

Larry Clinton At Frankfort (Central)., Indiana

>I would doubt you really have a problem with your 100 amp service. It is quite likely you have an undersized transformer feeding your house. Most homes with today�s appliances run less than 60 amp maximum unless you have electric heating or run an electric range, electric clothes dryer and electric water heater . Remember your 100 amp service actually will provide 200 amp at 120 volt or 100 amp at 240 Volt, (or a combination of the two). Often the service provider will put a 100 amp transformer on a pole and feed more than 1 house. Works ok until the loads increase. I had the same problem when I moved into the home I now own about 40 years ago. I was an Engineer and brought an accurate RMS voltage meter home from work and measured my voltage - it was under 105 Volt at certain times of the day. I did have a little argument with the power company until I told them the meter was certified - traceable to the NBS (now NIST). It took a week or so, and a threat of a lawsuit if my TV and appliances were damaged, and they replaced the transformer. Lo and behold, I had no more lights dimming, or low voltage. I wired my shop a couple year ago with a 100 amp entrance fed from my 200 amp house service. I (with my son in the shop) have ran 17 - 4 foot 2 bulb fluorescent light fixtures, 6 � 100 watt bulbs, my 2 ton central air conditioner, the 5 hp planer, 3 hp dust collector, large air compressor, small refrigerator, and 3 hp Unisaw at the same time without any light dimming or problems.