OT: flat bonding wire in armored cable?

Posts

OT: flat bonding wire in armored cable?

#1

OT: flat bonding wire in armored cable?

wilbur

>I finished up the wiring for my fluorescent lights in my workshop area last night. I am tying the new lights into existing armored cable wiring that is original to my 65 year old house. I'm using junction boxes to make the connections.

I was a little surprised to find that the old wiring had a flat wire which I think is aluminum wrapping around the two copper wires in the cable. I thought initially that I was dealing with 2 conductor armored cable wiring and that the armor was the ground. I'm pretty sure that this flat wire is supposed to be a ground, or an aid to grounding. Right now I wrapped electrical tape to shield the sharp edges and was able to tie it to the "real" ground wires using a grounding plug, but I don't really know what to do with it.

What should I be doing with this flat wire?

Re: OT: flat bonding wire in armored cable?

#2

I think you're right...

John in New Mexico

>Probably for grounding, but if no one who actually knows rather than supposes (like me) speaks up, you could try asking at FHB's website, someone there is bound to have seen it.

John

Re: OT: flat bonding wire in armored cable?

#3

Re: OT: flat bonding wire in armored cable?

DB

>Yes that is your ground wire. The coiled metal does not always make good enough contact for a good reliable ground, That is the reason you can not get BX cable anymore.

Re: OT: flat bonding wire in armored cable?

#4

Re: OT: flat bonding wire in armored cable?

Dave Chatham

>That aluminum wire is not an equipment grounding conductor, but rather a bonding wire. After you put the red anti-short bushing inside the spiral wrapped armor, you wrap the bonding wire around the OUTSIDE of the armor prior to installing the connector. Make sure there is enough past the connector for the inspector to see.

Dave

Re: OT: flat bonding wire in armored cable?

#5

Thanks!

wilbur

>That's what I wound up doing. I took some time to make sure that the clamp clamped down onto the bonding wire.