Quick Electrical Question

Posts

Quick Electrical Question

#1

Quick Electrical Question

Nat Robison

>I'm wiring two rooms in a newly-finished basement, basically family/all-purpose rooms.

In one room, I'm putting in 3 recessed lights and 4 outlets. In the other, I'm putting in 2 recessed lights and 6 outlets. As with a lot of rooms, I suspect that 80% of the receptacles won't ever be used but I know you have to plan as though they will be.

Anyway, would 15 amp circuits (one to each room) be sufficient for this load?

Re: Quick Electrical Question

#2

Re: Quick Electrical Question

Dan Donaldson

>For that use, 15 amp is probably OK, but I would run #12 wire so that I could hook it up as a 20 amp circuit. The only cost is the extra for the wire, and it is a lot easier to do it now than later.

Re: Quick Electrical Question

#3

Re: Quick Electrical Question

Jim Swank

>Run 20 amp circuits. It really costs little more. Check your local code first if you're thinking of 15 amp circuits. Even if you're not going to get it inspected, you may be able to avoid future problems.

Re: Quick Electrical Question

#4

Around here...

John in New Mexico

>The limit is 10 outlets per 15A general use circuit -not all jurisdictions put a limit on it. Based on this, you'd even be ok with the whole thing on one circuit, so one for each room should be much more than adequate.

Personally, I'd use 14 awg wire, but if you want to follow Dan's advice its your call. If you do use 12 awg, I'd recommend using 20A breakers and 20A rated receptacles.

John

(not an electrician)

Re: Quick Electrical Question

#5

Also

Mark Goodall - ATL - tooljunkie

>"...As with a lot of rooms, I suspect that 80% of the receptacles won't ever be used but I know you have to plan as though they will be...."

When it comes to electricity, you might find that the CODE states something like, there must be 1 outlet for every X feet of linear wall. At least it does for around here.

Happy Woodworking!

Re: Quick Electrical Question

#6

Re: Quick Electrical Question

Phil in NJ

>You should consider a separate circuit for ceiling lights and the outlets. It might not be code, but think about it... if you blow a breaker, do you want the lights to go out too?

Re: Quick Electrical Question

#7

Lightning answer. Check your local code.

Forrest Addy

>

Re: Quick Electrical Question

#8

Re: Quick Electrical Question

wilbur

>Here's a quick way to estimate what a given circuit will handle:

120V x 15 amps = 1800 watts

75% of that to provide a safety margin = 1350 watts

So if your total anticipated wattage between lights, appliances, radios, TVs, etc., is 1350 watts or less, then a 15 amp circuit should be able to handle it.

Of course, codes completely overrule this back of the napkin type calculation, and I'm not an electrician.

Re: Quick Electrical Question

#9

Re: Quick Electrical Question

Pat Evans

>20A breakers and #12 wire are a good idea. You might sometime have a large electrical load, such as an electric heater, and the added circuit capacity would be better. Also, wiring lights in one room with receptacles in the other would preclude total loss of power in a room in the event of a breaker tripping.

Re: Quick Electrical Question

#10

Re: Quick Electrical Question

Barry Irby

>Back In The Day, we figured 1.5 amps for each receptacle or 3 amps for a duplex outlet. This allowed five on a 15 amp circuit and they would allow you to squeeze 7 on a 20 amp circuit. Lately I noticed the local Codes officials are ignoring that and allowing a practically unlimited number of outlets on a string. Leaves me a little confused. Also, it used to be considered good practice NOT to have all the outlets in a room on the same circuit and to have lighting on a separate circuit as well. The idea was that if you had to work on a circuit, at least some of the outlets in the room would still be on. And if You had to work on the lights, you could plug a trouble light into the outlets. So it might be smart to mix and match.

Actually, Forrest is correct, Check with your local code enforcement office, even if you do it under an assumed name.

Re: Quick Electrical Question

#11

Re: Quick Electrical Question

Rick Christopherson

>This isn't a workshop, it's a family room. You have less than 500 watts of lighting load, so a single 15 amp circuit for the lighting will handle both rooms without any problem. With just 10 outlets in a living space, a single 20 amp circuit will also be just fine to cover both rooms.

As for outlet spacing, an appliance with a 6-foot cord must be able to reach an outlet without crossing a doorway, so the minimum spacing is 12 feet, but even short wall sections need an outlet of their own. Personally, I prefer to load the corners because this is where appliances are most common. You are not required to use 20 amp outlets as one poster suggested. 15-amp outlets are permissible on 20-amp circuits.

Re: Quick Electrical Question

#12

yup, I always seem to forget that one...

John in New Mexico

>15A receptacles are permited on a 20A circuit when more than one outlet is on the circuit. I stand corrected.

Re: Quick Electrical Question

#13

Re: Quick Electrical Question

Fred Davis fredd

>to flatly say that a 15 amp outlet is allowed on a twenty amp circuit does not address the code that requires a dedicated twenty amp circuit such as a garbage disposal, dishwasher , list is as long as you want to reflect on.

In addition if they havn't downgraded the NEC requirements , you can't combine light runs and outlets on the same circuit except in the case of a switched outlet you normally would plug a lamp into.

In addition, if you run a 20 amp dedicated circuit that has a switched load on it, such as a disposal, then the switch has to be rated 20 amp as well.

Lastly , if you will think about it, using 15 amp outlets on a twenty amp circuit as a cost saving measure is foolish when you consider that the 20 amp breaker protection for the 12 awg wire could let thru enough current in a overload situation to melt down the 15 amp outlet without kicking out the breaker.

In all cases of electrical supplies, buy American, the stuff made in Mexico will fail sooner then later and may burn your house down.

FredD

Retired General Contractor