Re: Electrical problem in the house
Bill Howatt
>Are you sure the live ones are on the same circuit and it isn't a case of the whole circuit being dead?
Do you have a Ground Fault Interrupter (GFI) receptacle which feeds the downstream outlets and it has tripped. This happened to me once due to moisture from a roof leak at this time of year due to an ice dam. I forgot there was a GFI and there was enough moisture in a ceiling outlet that it tripped.
Have you or anybody else done any work on the circuit that might have resulted in a wire breaking when a receptacle or switch was pushed back into the box. I had a copper wire break inside the insulation near a switch screw terminal after some renovations. Worked for a few days then quit.
Chance of rodents eating through the wire in attic or elsewhere?
If you are doing a visual inspection instead of using a voltmeter you may miss something.
If the live ones are on the same circuit then you can assume they are closest to the main panel but unfortunately you really have to sort out how the circuit is connected to really understand it.
You could measure the dead circuit relative to the safety ground and see if the hot wire is live. This would tell you if you lost the hot or the neutral. A resistance test should show the neutral connection shorted (0 ohms) to the safety ground. Make sure you only do a resistance check with the neutral. Measuring a live hot terminal can damage your meter. This still leaves you with the problem of finding where the discontinuity is though.
Good luck,
Bill