Electrical problem in the house

Posts

Electrical problem in the house

#1

Electrical problem in the house

J Runchey

>All of a sudden several lights and outlets have gone out on one circuit. A couple outlets are live yet. I cant locate where the feed wire originates in the circuit. I have looked in all the boxes and cant find any loose wires or screws. Its complicated by the fact that the wires are very old fabric covered romex, and the wires are very short in the boxes. What are the possibilities? I've been looking all day and can find no clue.

Re: Electrical problem in the house

#2

Re: Electrical problem in the house

Ray - SW Ohio

>Is it copper or aluminum wiring?

Re: Electrical problem in the house

#3

Re: Electrical problem in the house

J Runchey

>Its copper, done back in the fifties, even though the house dates to 1874

Re: Electrical problem in the house

#4

Re: Electrical problem in the house

Gary Evans Tallassee, TN

>If you are sure the two live outlets are on the same circuit, I would look closely at the outlet that is closest to the rest of the dead circuit. Normally you wouldn't feed lights from an outlet circuit, but no telling what that particular electrician did.

Assuming that the rest of the circuit feeds from the last live receptacle, I'd take a really close look at it. There may be an open in the outlet itself. If the outlet is using the plug-in connections in the back, they could easily be the problem. I'd splice on some longer wires and attach them to the screws on the sides of the outlet.

Also, if those outlets and lights are critically needed, you could always rig a 12 ga. extension cord with two male ends as a temporary jumper until you can locate the problem.

If the outlet isn't the problem, I'm at a loss for other suggestions.

Gary

Re: Electrical problem in the house

#5

Re: Electrical problem in the house

Bill Howatt

>Are you sure the live ones are on the same circuit and it isn't a case of the whole circuit being dead?

Do you have a Ground Fault Interrupter (GFI) receptacle which feeds the downstream outlets and it has tripped. This happened to me once due to moisture from a roof leak at this time of year due to an ice dam. I forgot there was a GFI and there was enough moisture in a ceiling outlet that it tripped.

Have you or anybody else done any work on the circuit that might have resulted in a wire breaking when a receptacle or switch was pushed back into the box. I had a copper wire break inside the insulation near a switch screw terminal after some renovations. Worked for a few days then quit.

Chance of rodents eating through the wire in attic or elsewhere?

If you are doing a visual inspection instead of using a voltmeter you may miss something.

If the live ones are on the same circuit then you can assume they are closest to the main panel but unfortunately you really have to sort out how the circuit is connected to really understand it.

You could measure the dead circuit relative to the safety ground and see if the hot wire is live. This would tell you if you lost the hot or the neutral. A resistance test should show the neutral connection shorted (0 ohms) to the safety ground. Make sure you only do a resistance check with the neutral. Measuring a live hot terminal can damage your meter. This still leaves you with the problem of finding where the discontinuity is though.

Good luck,

Bill

Re: Electrical problem in the house

#6

Re: Check the light fixtures

Kneale Brownson in Northern MI

>I'll bet you have an overheated light fixture that has burned wiring in it. The burning caused a short that broke the part of the circuit that was supplied beyond the fixture but not the outlets ahead of it, especially if the fixture is wired with multiple switches.

Re: Electrical problem in the house

#7

DANGER! DANGER! DANGER!

Jim Swank

>Never ever make a male to male extension cord! That's one of the most dangerous ideas I've ever heard suggested. If you plug one end into a live outlet, the other has live exposed metal parts.

Now first of all, you don't know if it's the hot wire or the neutral that's dead. If it's the neutral, the hot wire is still hot. You don't know which side of the service the hot wire is from, so there's a 50-50 chance plugging such a jumper in will make a dead short across 220 and could even blow up in your hands.

You might even have a very loose connection somewhere that's almost arcing, and this adds just enough oomph to make it a good ignition source.

If it's the same side of the service and everything goes right, it might work, but it's not worth the risks.

Find the problem and fix it, even if you have to pay big bucks to an electrician. Don't screw around with your health and your families.