AlbertaBob

>I am in a temporary set up with my shop and it is difficult to run another 220v line in. I have one to service the lathe but need antoher for my new bandsaw.

Have any of you made an extension cord for this?

I also saw this conversion unit that could solve my problems.

Any experience with these devices?

Bob


110-220 converters

Re: 110-220 converters *LINK*

#2

Re: 110-220 converters

Dan Donaldson

>I would make up a cord rather than try one of the converters. They may work, but I would be leery about handling a large motor load. Extension cords are easy to make. Just get some connectors that match your wall plug and equipment cord, and put them on some wire. Depending on the distance and the current of the motors, either a piece of 12/3 or 10/3 cord would work.

Re: 110-220 converters *LINK*

#3

No need for -3

Rod Peterson -- Ormond Beach

>Unless you're making up a cord for an appliance with 120V functions on it, 12 or 10-2 has all the conductors needed—hot (black), hot (white), ground (green).

Same with plugs and receptacles—the three pin (whichever configuration) should be all that's needed.

A whole lot less expensive, too.

Rod

Re: 110-220 converters *LINK*

#4

Naming convention

Denis Ch�nard, Orl�ans, Ont.

>If I am not mistaken electrical cords count the ground as one conductor. So the equivalent of 12/2 Romex is 12/3 cord.

DC

Re: 110-220 converters *LINK*

#5

Save your $175

Mark Goodall - ATL - tooljunkie

>You can easily make two 120V outlets from one 240V or one 240V from two 120Vs with some electrical cord, electrical boxes and the proper outlets and plugs.

I've got some info and diagrams on my www.happywoodworking.com website.

Just make sure you understand 100% what you are doing. I only get hurt when I THINK I know what I'm doing.

Happy Woodworking!

Re: 110-220 converters *LINK*

#6

Actually…

Rod Peterson -- Ormond Beach

>…I think I was lulled onto the wrong track by Dan's use of 12-3. I went out and checked my cord and it's stamped “12G 3C”, which it is—three conductor. I'll look at some others at the box next time I'm there, but I suspect, as you intimate, the xx-x appellation isn't used for that kind of cord.

Oh well, my advice stands—for another situation.

Rod

Re: 110-220 converters *LINK*

#7

Perhaps, But Be Wary

Garrett in Victoria BC

>The extension cord is no problem.

What the gizmo is doing is plugging into two separate 110vac circuits - not just 2 different outlets - and thereby making up the 2 legs of the single 220vac supply. This requires that the two circuits - do you have two outlets on separately fused circuits close to one another? - be 180 degrees out of phase to avoid a short. Remember, the longer the extension cord, the heavier the wiring gauge required because of line losses. The specs say it has an interlock to shut down instantly if they aren't.

I expect it will work, but I also note that it is not certified by either Canadian or US Standards groups.

Cheers, Garrett

Re: 110-220 converters *LINK*

#8

Re: Save your $175

albertabob

>Thanks Mark:

Way too much there to digest tonight but it sure a keeper!

just in time for the new shop plans too.

Bob

Re: 110-220 converters *LINK*

#9

Re: Be assured.

Al Stokka - Cambridge, Iowa

>"I expect it will work, but I also note that it is not certified by either Canadian or US Standards groups."

The device is recognized by Intertek and carries the ETL mark. ETL is absolutely equivalent to UL. In fact, Intertek uses the standards that are written by UL.

As far as I'm concerned, it is good to see someone give UL a run for their money. UL writes the standards and, in the past, also raked in huge fees evaluating a device to carry the UL mark. See a conflict of interest there?

Al

Re: 110-220 converters *LINK*

#10

Thanks for your help guys-re 220 converter

albertabob

>Looks like the extension cord will be just fine for the time being.

I am still interested in how these converters work if they don't tap a hot from each side of the box as mentioned.

Having had nightmare experiences with CSA In Canada, I would welcome a standard that satisfies all trading partners rather than a myriad of governing bodies all justifying their jobs by being slightly different from each other.

Bob

Re: 110-220 converters *LINK*

#11

Re: Thanks for your help guys-re 220 converter

Al Stokka - Cambridge, Iowa

>"I am still interested in how these converters work if they don't tap a hot from each side of the box as mentioned."

Bob,

The device does tap a hot conductor from two separate circuits. That's why there is an indicator light on the device. If the two source circuits are not 180� out of phase, the indicator will not light, telling the user that the device is not hooked up correctly.

Running wires from a breaker panel with a 230V breaker accomplishes the same thing. If you have two, open, adjacent slots in your breaker panel, you should use that method to gain a 230 circuit. Likely cheaper in the long run than buying the converter.

Al

Re: 110-220 converters *LINK*

#12

Nice website, Mark.

David Sparks

>

Re: 110-220 converters *LINK*

#13

Re: Thanks for your help guys-re 220 converter

aLBERTABOB

>Thanks Al;

I was trying to figure out why I would need the expensive box if it was just as easy to pull another hot from the other side of the box .

Makes sense now but the converter doesn't.

the chances of having 2 adjacent circuts in the vicinity and at 180� is at best a dream.

Even it they were found like this, a new plug in the wall with a hot from each circuit would do the same thing? (thinking out loud without the aid of an electrician.)

Bob

Re: 110-220 converters *LINK*

#14

Re: Two outlets might = one converter

Al Stokka - Cambridge, Iowa

>Yeah, two outlets if, as you said, in the unlikely (50-50 chance, I suppose) event they were out of phase, would do the same thing as the converter. I'm not sure how you would confirm, though, that the outlets were out of phase beyond tracing the conductors back to the panel.

Do you have a couple of adjacent slots open in the panel?

Al

Re: 110-220 converters *LINK*

#15

Re: Two outlets might = one converter

albertabob

>Yep I do. I think I know where you are taking me.

Tag a line off two new breakers and send them up the line to the 220 outlet?

Bob

Re: 110-220 converters *LINK*

#16

Re: One breaker vs. two breakers

Al Stokka - Cambridge, Iowa

>Bob,

You're thiiiiiiis (holds hand up with thumb and forefinger very, very close together) close. ;^)

Actually, use one 230 volt breaker. Using two 120 volt breakers would not tie the breakers together, whereas a single 230 volt breaker will have a tie over both handles, thus tripping both breakers in case of an overload. An overload on one of two 120 volt breakers would only open one circuit, leaving the other circuit live...not a safe situation.

Al

Re: 110-220 converters *LINK*

#17

Re: One breaker vs. two breakers

albertabob

>Eureka!

Finally the light goes on! Thanks Al!

I wondered how those 230 v breakers worked and didn't have a clue until now.

I was thinking 2 x 115 V side by each

Didn't realise they were tapping the other side of the bus.

That don't make me a sparky, but at least a little smarter when I ask them to do a job.

Thanks again for your patience Al.

Bob