Re: Cost
wilbur
>Hi Randy,
I'm tying my shop lights into a preexisting 15 amp circuit that also feeds the lights in my kitchen, which is upstairs from my workshop area. By my calculations, I'm still well within the capacity of the circuit with the addition of my fluorescents:
120V x 15 amps x 75% = 1350 safe watts total on circuit.
Workshop: 7 fluorescent fixtures with 2 T8 32 watt bulbs = 448 watts
Kitchen: 6 75 watt halogens and 3 15 watt compact fluorescents = 495 watts
Total: 943 watts, which gives me an additional 400 watts of headroom for this circuit.
Also, I am using proper BX clamps -- I'm not trying to use Romex clamps on BX wire. THe difference in price was negligible. I also am using the plastic bushings. They came with the wire.
My workshop outlets for tools and machines are all 20 amp circuits, and run off of a separate subpanel. I decided to put the lights on a completely different circuit so that even if the main subpanel breaker trips, I will still have light.
I agree that BX is used far more often in commercial settings than in a residential setting, and may be overkill. But in my case, I figured for an additional $25, and for piece of mind, why not?
Wilbur