#1

Grounding question -- before I electrocute myself

wilbur

>Before I try to wire up the new fluorescent fixtures I've set up in my basement, I thought I'd double check my plan before I turn myself into a French fry.

The wiring in my basement that I will be working off of is old, but in good shape. It's armored cable with two wires in the cable (hot and neutral, no ground wire). The cable is armored all the way back to my main circuit breaker. I'm pretty sure that the cable sheath and the receptacles are grounded. The way I tested this is with a voltmeter:

Hot - neutral = 120V

Hot - receptacle box = 120V

Neutral - receptacle box = 0V

A circuit tester showed that I can get current flowing from hot to the box.

Is this enough to be sure that the cable sheath and boxes can be used as a ground? The cable that I will be wiring my lights with is BX 14/2, with a hot, neutral, and ground cable within the sheath, and I was planning to connect the ground wire to a receptacle box with a ground screw.

Re: Grounding question -- before I electrocute myself

#2

Re: Grounding question -- before I electrocute mys

Bill Howatt

>The BX cable sheath is acting as the safety ground conductor and I think this was intended years ago. If you connect the ground to the first fixture in your circuit and tie to the others then you will have them grounded. However, I don't know if there is any special requirement for tieing the ground wire to the BX or if the bushing which I assume the BX is clamped to at the fixture is sufficient to provide that connection for code purposes.

Bill

Re: Grounding question -- before I electrocute myself

#3

Re: Grounding question -- before I electrocute mys

wilbur

>I don't think there is a special requirement for the ground wire to be attached to the ceiling box that I am planning to work out of -- using a grounding screw should be enough. I just want to make sure that the box itself is grounded. All of my fixtures will be tied into the ground wire of the new 3 wire BX cable that I bought.

This is what I am planning to do for grounding -- hopefully this will be clearer.

Circuit breaker -- old 2 wire armored cable -- old ceiling box -- new 3 wire BX cable with ground wire attached to receptacle box with grounding screw -- new light fixtures tied into ground wire

I guess I'm looking for a foolproof test (I know, I probably am a better fool) that the old ceiling box is adequately grounded. I think it is based on my voltmeter, but this is the first time I've tied new circuits into old.

Re: Grounding question -- before I electrocute myself

#4

Easy test

John in New Mexico

>Confirm that the common is bonded to the ground at some point- probably in your main panel, but not always. Then just meter between your box and common where you plan to install the lights.

John

Re: Grounding question -- before I electrocute myself

#5

Re: Grounding question -- before I electrocute mys

Bill Howatt

>If you measure 120V from hot to the metal box it means it is grounded unless it is erroneously tied to the neutral which should only occur in the main panel box.

Bill

Re: Grounding question -- before I electrocute myself

#6

Thanks!

wilbur

>Thanks for the info. I must have done things right, because I am still here typing this thank you message, and my house isn't on fire.

I did wind up making 3 trips to the local borg to finish the job, though.