>I'm in the process of finishing my basement and I'm having to build a soffit around the main ducts for the heating and cooling. The furnace is at one end of the house and the mains basically run the length of the basement.

The cold air return is located about 1/3 of the distance from the furnace. What's the reason or function of the remaining 2/3 of the ductwork that returns the air to the furnace?? Could it be removed and capped off??

Re: OT Heating/Cooling Question

#2

Re: OT Heating/Cooling Question

Barry Irby

>I sincerely doubt those cheap contractors that installed your system went to all the troubel and expense ff installing a duct for nothing. Do you have a second air return in your house? Maybe upstairs or in the master bedroom. If It is really a duct doing nothing, you could remove it, but I bet it's doing something, or should be.

Re: OT Heating/Cooling Question

#3

Re: OT Heating/Cooling Question

Ray SW Ohio

>There has to be a reason for the length, it should end with the last return. Possibly, there are returns from other parts of the house.

Re: OT Heating/Cooling Question

#4

Re: OT Heating/Cooling Question

Webster Stump

>If there is one central return in the house, then yes, you can cap the end of it once you get past the central return. Make sure that the central return is big enough for the furnace, if theres not enough return, some issues will form. Short cycling, high temp rises and so on.