wiring the circuit for the new lathe

#1

wiring the circuit for the new lathe

Carol Reed - home in Strawberry

>According to the manual I need a 220v 15 amp circuit.

The service entrance is on the other side of the house from the turning shack. I do have a 30 amp 22v circuit for the table saw nearby.

That said, I am resigned to run another wire to get across the house for the new circuit. I don't think it wise or code to run a 15 amp circuit off the 30 amp circuit. Aside from which, that would call for another circuit box - not all that inexpensive! Not that wire is cheap!

15 amp circuits call for 14 Gage wire? For a 220v circuit do I need heavier wire? If so, what, 12 or 10?

Second 15 amp 220v breakers are a real challenge to find. 20 amp 220v breakers are readily available. Should I keep looking for the 15 amp breaker or will a 20 amp be ok?

Re: wiring the circuit for the new lathe

#2

Re: wiring the circuit for the new lathe

Ralph

>Carol

There is no reason for you to run a 2nd 220 circuit to run the lathe. Unless you are running the table-saw and lathe at the same time (or some other loading).

You don't need to run a separate circuit any more then you need to run a separate circuit for a new computer, under normal circumstances.

Yes, you do NOT want to put a 220V/15 amp outlet on that 220/30 amp circuit. But you could put the same type plug on the lathe that is on the table-saw.

If you want, you could run a 10 gauge service from the current table-saw outlet over to where you want the lathe.

Re: wiring the circuit for the new lathe

#3

Re: wiring the circuit for the new lathe

Frederick Nelson

>When I installed the circuit for my new lathe this past summer, I used 12 gauge wire for a run of between 35 and 40 feet. I also had to order a 15 Amp breaker for my distribution box, which was made by a company that has long since been subsumed by another company, which naturally no longer acknowledges the existance of parts for my box. Hope this helps.

Happy Holidays.

Fred

Under complete overcast in Eastern Missouri

Re: wiring the circuit for the new lathe

#4

Re: wiring the circuit for the new lathe

Stephen Mushinski

>Carol,

What needs to be understood is that the circuit breaker is protecting the wiring not the equipment you have plugged in or attached. Your wiring to the saw should be of a size to handle the ampacity of 30 amps. Therefore at the panel you will have a 30 amp breaker. It doesn't care what you have plugged into it.

Now to try an answer your question. If you are asking what is code then it would be my understanding you would need and want the lathe on its own circuit from the panel with its own breakers (which really should not be hard to find at any electrical store - even HomeDepot). I would run 12 gauge wire but in most areas 14 gauge is the size for 15 amp. The lathe is a motor which might be running for long periods of time therefore oversizing the wire will not hurt but help in the long run. Code is the minimum standards not always the best but the very least which is allowed.

Could you add a 220 outlet to the existing wiring - YES - it would also work and not start a fire BUT might not be code in your area. Electrical code is somewhat different in different areas of the Country. There are standards but some areas have higher standards then others.

The best bet is to get a quote for the job then you will have a better idea what you need and what the regulations are in your area.

Hope this helps, I know it is not a definitive answer.

Re: wiring the circuit for the new lathe

#5

Re: wiring the circuit for the new lathe

Carol Reed - home in Strawberry

>Thanks, Ralph. Life just got simpler - and less expensive. I will run some 10 gage wire from the saw outlet to the lathe position. That is easy and accessible. The other required crawling under the house, never a fun thing.

However those 30 amp plugs and outlets are pricey! I am assuming the outlets have to match the breaker rating. Guess I have to bite the bullet someplace. This will also take far less time to do.

Indeed I had forgotten about the wring being protected by the breaker, not the machine. Thanks. There is only me here. Can't run more than one cutting tool at a time. Occasionally the dust collector, the compressor and a cutting tool are on simultaneously, but all on different circuits.

Getting a quote around here would take weeks and would not provide me with the information required for me to do it myself. I have considerable wiring experience, but I am not an electrician. Trying to get code information from the local authorities is met with 'talk to a licensed whatever.'

I am going to try to build a new shop next summer. Won't that be fun?!? Gotta get a permit and all. It should be exciting and it will be but not necessarily in a good way.

Re: wiring the circuit for the new lathe

#6

As Stephen said - distance

Jeff Willaford

>Distance may be a factor if you run a new circuit for the lathe and may require a larger size wire. If you decide to pull a new circuit please consider that.

Re: wiring the circuit for the new lathe

#7

Re: wiring the circuit for the new lathe

GalenV in Iowa

>You can put the 15 amp 220 outlet on the same 30 amp 220 line.

The outlet only need match the equipment spec you are pluggin in.

The pin configuration prevents you from plugging a 30 amp load so there is no way to cause a problem.

You can buy your cheaper 15 amp 220 outlet and plug.

Re: wiring the circuit for the new lathe

#8

Re: As Stephen said - distance

Carol Reed - home in Strawberry

>That I did. Thanks.

Re: wiring the circuit for the new lathe

#9

Re: wiring the circuit for the new lathe

Carol Reed - home in Strawberry

>Thanks, Galen.

I will also have a 2 pole switch next to the outlet. That way when I leave the shack, I can turn off ALL the power to the lathe. We get lots of electrical storms here in the mountains of Arizona. I don't 'do' electronic devises when the sky 'booms'.

Re: wiring the circuit for the new lathe

#10

Re: wiring the circuit for the new lathe

Rick in Colgate, Wi

>Personally, if it were me doing this for a temporary amount of time, I would run a piece of #12 romex from the saw outlet to the lathe and install a plug on each end and treat the circuit like an extension cord.

Re: wiring the circuit for the new lathe

#11

Re: As Stephen said - distance

John Veerkamp, Western Mo

>35-40' is not a problem with voltage drop on a 15 or 20 amp circuit.

Re: wiring the circuit for the new lathe

#12

Re: wiring the circuit for the new lathe

Barry Irby

>Carol,

I think it would be safe to run a No. 10 (30 amp) wire from the existing saw circuit and then put a 15 amp 220 receptacle on the end of it for the lathe. Simple and reasonably safe for a temporary setup.

Or you could by a small breaker panel and use it as a sub panel. Hook the existing wire to it and pull a thirty amp circuit for the saw and a 15 amp circuit for the lathe. This might not be better, as the sub panel would technically require a four wire feed, two hots, a neutral and a ground. You probably have a three wire feed to the saw, so the first idea is better.

Re: wiring the circuit for the new lathe

#13

Ken Vaughan

Re: wiring the circuit for the new lathe

Ken Vaughan

>Local code always wins, but dropping a branch panel into the shop has some long term benefits with the next 220 volt upgrade, and the option to have 110 outlets on 110 breakers.

Note that most main breaker panels are not set up to handle double tap connections and you will need to use split nuts to join the lines below the tap into the main breaker. (many of the breakers that allow double taps hide that info on the back of the breaker too).

Depending on your local code, look at size on your main breaker -- pulling the sub-panel may take you over the code limits and push you to a new main (ouch in the cash flow). Main breaker replacements is a task for the electrician in my view,

The disconnect switch comment suggest you are going to drop a 110 outlet set off the 220 line at the lathe. If you do so, I suggest you put this in as a GFI breaker to make sure any extension cords do protect the user if they head out the door.

Re: wiring the circuit for the new lathe

#14

Re: Question for electrical guys -- why not....

JamieD

>...rig a #10 stranded wire extension cord from existing 220v recepticle for a "temporary" feed for the lathe? This is how we use RV electrical hook-ups, maybe inline a 15 amp breaker box with plug recepticle for lathe?