>I was at the local BORG this morning picking up some extra 14g wire. The guy helping me ending up telling me that I couldn't run my 3520B off of my home panel with the existing 220/20amp power supply. I currently use the 20amp circuit for the 3HP/1phase/15.3amp tablesaw. So can someone tell me why the 3520b with 2HP/1phase/6.2amp cannot use the same 220/20amp power supply? I've plugged it in yet lest the guy be right.
FYI...I have zero electrical skill. But in talking with other 3520 owners, I am amazed this didn't come up earlier. And I scoured the internet but didn't really get a hit this specific.
>I'm only reusing the same plug for the TS and lathe. The 2 machines will never run at the same time. I'll be plug swapping them. I usually unplug my machines.
I'm not sure how to rip lumber and turn a hollow form at the same time. That'd be some serious talent for a one-man shop.
>If your 220/20 amp branch circuit consists of the one outlet then you can run either piece of equipment by plugging in either device. It sounds like the person you talked to thought you were going to put both tools on the same branch circuit at the same time.
I thought you were going to put both on until you clarified you will use one outlet to plug in either machine.
>Having worked at a Lowe's, I can tell you that with your "zero" electrical experience, you are probably more experienced than the one was supposedly answering your question. You've done the research you need and have already determined that the amps you'll pull is well within the amp capacity for that circuit. Have a great time!
Keith Newton------WebKitFormBoundaryV6MZb+tiOpocz6
Keith Newton------WebKitFormBoundaryV6MZb+tiOpocz6
Guest
Yes BUT
Keith Newton------WebKitFormBoundaryV6MZb+tiOpocz6
>If you have not been running this tool on 220 before, you will need to change a few wires in the motor, or it will run really fast before you let the magic smoke out.
Either under the cover where the wires go into the motor or on the motor plate, you should find a diagram showing how to configure the wires for low and high voltage. Make sure that you have it right for the volts.
>It appears that you can get the lathe with either a 240V single phase input or a 3-phase input. So it is not impossible that he may have a 3-phase requirement for the machine. The 3-phase would just power the inverter which is still required to get the variable-speed feature.
It is essential that he checks this out and the type of plug on the cord, if any, might be a clue along with checking out the specifications and determing exactly what they mean.
The on line manual for your lathe agrees with the 220 1 phase you are trying to use. I will copy the lines right from the manual.
From this it seems all you need is a 220 1 phase plug like your existing equipment. The pigtail wires should be conected as they are to the lathe and follow the directions on the plug you purchase to fit your 220 1 phase socket.
The Lathe will operate on single phase or three
phase, 230 volt power supply. The Lathe should
be connected to a dedicated circuit. Make sure
the characteristics of your power supply match
the specifications on the motor plate of the
Lathe.
Single Phase Operation
A three wire pigtail for use on 230 volt single
phase power is attached to the inverter and may
be �hard-wired� to the power source, or
connected to a UL/CSA listed receptacle plug.
Connect the 230 volt supply to the black and
white leads and ground the green lead.
If you are hard-wiring the Lathe to a panel,
make sure a disconnect is available for the
operator. During hard-wiring of the Lathe, make
sure the fuses have been removed or the
breakers have been tripped in the circuit to
which the Lathe will be connected. Place a
warning placard on the fuse holder or circuit
breaker to prevent it being turned on while the
machine is being wired.
Three Phase Operation
If three phase power is used, it will be necessary
>I don't know about Chip, but all of these answers have confused me.
Buy a 220-volt 1-phase plug that matches the one on your table saw, and forget about the 3-phase.
The reason that the lathe does't come with a plug on the end of the electrical cord is because your wall receptacle sould have several different prong arrangements. It's as simple as that. Powermatic assumes the buyer can match a plug to their receptical and put it on the end of the cord. If thay are wrong, then you should be calling Jet/Powermatic in the morning, or hire an electrician. You should not ne asking the question here.
Your 220 wall receptacle could have 3 different orientations - 2 that are straight across horizontal, one horizontal and one vertical, or it could have one horizontal and one that is a "T" shape. There are others, but these are the most common. Plugs are available in all three configurations. To make it simple, use the same one that is on your tablesaw, or use that one because you will never be using the saw again now that you own a lathe.
Yes, the lathe has a 3-phase motor. That how you get the variable speed with the twist of a knob. The speed of a 3-phase motor can be controlled, the speed of a 1-phase motot cannot. The controller converts single phase alternating household current into a controllable 3-phase that goes to the motor. The household current can be either 110 or 220 volt, but I assure you that the converter on the Powermatic 3520 is wired for 220 volt. The directions on using 3-phase power are there so the motor can be wired into the power WITHOUT the converter f0r use in an industrial shop. Ignore that part of the directions. You DO NOT have 3-phase power in your house.
>I hope I did not add to your confusion. Did not mean to.
You indicated your manual only had 3 phase wiring and I therefore included the online manual wiring comments. I would have thought your manual would have been the same. Lathe can be connected to single or 3 phase.
Last electric cloths dryer I bought the clerk ask me what 220 socket I had so he could include the right plug with pigtail wires. Guess it had been long enough I did not realize they now produce more than one style for the same application. Apartment I was in they used two differnt sockets, one for stove and for dryer. Both put in the same time!
>Chip, get your electrician buddy to help install a switch near the lathe for convenience. It must be a double-pole, single-throw type that switches both sides of the 220V circuit. Externally, it looks like an ordinary wall switch. You don't need a big disconnect in a metal box for day-to-day operation.
Don't mess up and get a "four-way" switch that looks similar. If you do, the lathe will be on ALL the time. Your buddy should know about this. Good Luck. ~Doc
"Last electric cloths dryer I bought the clerk ask me what 220 socket I had so he could include the right plug with pigtail wires. Guess it had been long enough I did not realize they now produce more than one style for the same application. Apartment I was in they used two differnt sockets, one for stove and for dryer. Both put in the same time!"
Galen:
It's likely that there were two different current ratings on the 220V circuits for the dryer and the stove. They are not necessarily 'the same application', especially if there are different current requirements, different gauge wire for the runs, and different breakers. There are standard NEMA configurations for outlets and plugs (also referred to as 'caps') that have been established so that there will be compatible and safe use of the voltages and currents needed by equipment. See the link below to understand the different blade configurations and how they relate to voltage and current requirements.
One of the most boring, yet beneficial, undertakings I did about 10 years ago was to actually read the National Electrical Code before I wired my shop. Saved me LOTS of money and time, despite the dry and soporific words on the pages of these regulations.
Keith Newton------WebKitFormBoundaryV6MZb+tiOpocz6
Keith Newton------WebKitFormBoundaryV6MZb+tiOpocz6
Guest
Yes BUT------WebKitFormBoundary+pgP1b3O6HM9D9xX
Keith Newton------WebKitFormBoundaryV6MZb+tiOpocz6
>If you have not been running this tool on 220 before, you will need to change a few wires in the motor, or it will run really fast before you let the magic smoke out.
Either under the cover where the wires go into the motor or on the motor plate, you should find a diagram showing how to configure the wires for low and high voltage. Make sure that you have it right for the volts.
I left most of my library of standards at my old work place when I retired. Guess I was thinking they would never be needed in my old age. Trying to keep up with AISC, SSPC, NACE, OSHA, NEMA, ANSI, AWWA, NSF and Machinery Handbook reference sections in just my fields of need was a lot of somewhat boring reading. I hated the standards that ran in an endless cross reference loop and never really defined clearly the point in question.
I should have peace of mind that I do not really need to keep up with them now!
>Like Russ said; "Buy a 220-volt 1-phase plug that matches the one on your table saw," It's that simple... plug it in when you use it then unplug when done.