Trouble getting re-started

#1

Trouble getting re-started

Thad

>So it's been months since we moved, and I finally got around to running a 220 line to my half of the garage for turning.

I turn on a J.A. Fay & Egan 400 circa 1939. My FIL gave it to me with a rotary phase converter since it still runs off of the original 3 phase motor.

Here's what happens:

Upon throwing the switch, the converter runs, humming as usual.

Upon turning the lathe on, the hum gets quite loud, and the lathe does nothing.

Here's what's interesting/confusing(to me):

I can reverse-wind the lathe with chord, and pull-start it with the converter and the lathe on, and the converter hums quietly (as it used to) as the lathe runs.

I roughed a bowl bottom last night and the motor and converter got a little warm, but not even uncomfortable to the touch.

It was set up and running fine before the move, and now it's not. I did not disconnect anything in the move; just unplugged and lugged it. I've checked all connections, and no loose wires.

I checked the legs coming out of the converter and they read 240, 240, 480. (so the converter is working right?)

Something happens when the lathe is turned on, as evidenced by the very noticeable change in sound; but I don't know what. And it runs once pull-started (so the motor seems ok).

So any thoughts on where or what the problem might be?

Re: Trouble getting re-started

#2

Re: Trouble getting re-started

Rick Allen

>The motor has some sort of starting circuit. It would appear that the starting circuit has failed. I am not sure about 3 phase but on a single phase induction motor there is a starting capacitor. If the capacitor fails then the motor will react the same way as you have described.

I would look for a hump on the motor. If there is one or two humps then you should fine capacitors housed in those humps. Capacitors have specs which indicate the max voltage and the capacity in micro feraids.

There are businesses which deal with electric motor repair and they would be a good place to look for repair. These places are accustom to working on large electric motors and may chase you away. But they should at least be able to give you some idea of where to go.

A word about capacitors. Electrolytic capacitors can go bad. The failure will often occur during periods of inactivity.

Re: Trouble getting re-started

#3

Re: Trouble getting re-started

Sean Troy

>Caps do go bad but be very careful with them as they do hold enough energy to give you quite the bite.

Re: Trouble getting re-started

#4

No Capacitor(s)

Thad

>That was my first thought too, but there are no capacitors on the motor. It is my understanding that the 3rd phase is the starting circuit.

I've looked for a motor repair co. in my area, and all I can come up with are general electricians.

Re: Trouble getting re-started

#5

Re: No Capacitor(s)

john lucas

>Thad I'm definitely not an expert here but is sounds like the motor that creates the 3rd leg is not starting. When you start it manually it runs and creates that leg since you had the voltage out when it was running. There must be something that is causing the motor not to start. That is my non educated guess.

Re: Trouble getting re-started

#6

Motor Repairman in Middle GA

Thad

>John, Sorry for the confusion...and thanks for the reply.

The converter works fine(as far as I can tell). I comes on as soon as the switch is thrown, and produces 240V, 240V, 480V on the 3 legs coming out of it.

It's the lathe that wont start without being pulled-off.

If no one has dealt with this, then I'll try to find someone in middle GA who can take a look at it...of course if I can get the motor off, I'd probably be better off replacing it with a single phase motor

Re: Trouble getting re-started

#7

Re: 480 Volts on a 220v 3ph converter?

Dave Andeson (PacNW)

>This sounds like a RED Flag to me! On a 3 Phase motor all of the windings are the same voltage. To reverse the rotation you just switch 2 leads. It doesn't matter which 2. The line voltage from the power company is 240v on all three legs. I suspect your converter has something major wrong with it and has fried on circuit of your motor. I could be wrong, you should call an electrician to trouble shoot this one

Just 2 cents worth

Dave Anderson (PacNW)

Re: Trouble getting re-started

#8

Re: 480 Volts on a 220v 3ph converter?

Thad

>Those volt readings were with the lathe disconnected, just to see what was coming out of the converter. I thought the produced phase was the starting phase, and as such supposed to be higher.

I KNOW I'm wrong about something...'cause what I'm doin' ain't workin'.

Re: Trouble getting re-started

#9

Re: 480 Volts on a 220v 3ph converter?

Dave Andeson (PacNW)

>After reading up on phase converter, there is no waqy that you should be getting 480v. on one lead. I repeat, this is one for a licensed electrician

Good Luck

Re: Trouble getting re-started

#10

Re: 480 Volts on a 220v 3ph converter?

Thad

>Thanks Dave...I'll seek professional help

Re: Trouble getting re-started

#11

Re: 480 Volts on a 220v 3ph converter?

arkie

>I believe you have an open winding or similar defect on your 220v 3 ph converter. The 480 V reading is a pretty good clue that your 3 ph converter is only producing 2 phases.

This would also explain why your lathe would not start of its own accord, but would keep running once started.

A motor repair shop or a good industrial electrician may be able to help you out.

Re: Trouble getting re-started

#12

I gotta believe it's your phase converter.

Al Crandall

>We have two rotary phase converters in our shop. The nature of the beast is that it has one wild leg which will always produce more voltage than the other two. You have to switch the wires around and check the output voltage after each change to find the most balanced voltage. It will never come ut perfect. Thank god there were instructions with the converters covering this proceedure, because I'm not an electrician. Our best setup gave us 240, 240, and maybe 270, I don't remember exactly. I do remember that the instructions said that we should be able to get the third leg within 10% of the other two. If you have a leg in the 400+ volt range, get help before you fry the lathe motor also.

Re: Trouble getting re-started

#13

Re: Trouble getting re-started

Thad

>Thanks for the replies. You give me hope that I can have this resolved soon.

I'll let you know when...and what it took to fix.