Oneway Electrical Info

Posts

Oneway Electrical Info

#1

Oneway Electrical Info

jwoodwright

>What plug is on the 2436?

I'm having an Electrician install a 220 volt 20 amp outlet and he wants to know which receptacle to install.

I appreciate your help.

Re: Oneway Electrical Info

#2

Dick Hines

Re: Oneway Electrical Info

Dick Hines

>If they come like the Powermatics there is no plug on the lathe. You can picl the plug you need.

Re: Oneway Electrical Info

#3

Re: Oneway Electrical Info

Barbara Gill, Remlik VA

>It comes with a plug and I assume it is the same as my 1640. I took a picture of the plug for someone who posts here maybe he will see the question and re-post the pic. I am at the store right now but will look for the picture when I get home in sever hours.

Re: Oneway Electrical Info

#4

Dick Hines

Re: Oneway Electrical Info

Dick Hines

>Dan fixing breakfast for you?

Re: Oneway Electrical Info

#5

LOL!

Barbara Gill, Remlik VA

>Not a chance. I am the only one here until the staff shows up.

Re: Oneway Electrical Info

#6

Re: Oneway Electrical Info

George Van

>I installed a 30 amp circuit and breaker for my 3hp model 2436. I was concerned following the recommendation of a 25 amp breaker on a 20 amp circuit. The small difference in #12 vs. #10 and plug cost was not a concern.

From Oneway:

If you put in a 15 Amp breaker, you will get what we call "nuisance tripping". This is why we recommend a minimum of a 20 Amp breaker (see below).

Note: Also please keep in mind that the drive takes care of electricity that comes out of it. It will shut down if there is a short circuit on the motor side of the wiring. The breaker on the wall is there strictly to protect you.

* Breaker Recommendations

1� HP Drive - use a 20 Amp Breaker

2 & 3 HP Drives - use a 25 Amp Breaker

Re: Oneway Electrical Info

#7

Re: Oneway Electrical Info-220 plug

Barbara Gill, Remlik VA

>Here is the picture of my plug.


img

Re: Oneway Electrical Info

#8

Re: Oneway Electrical Info-220 plug

Mark Wollschlager

>Thats a nema 6-15p (plug) the matching receptacle would be 6-15r

You could also get a L6-15p and L6-15r locking plug and receptacle.

Mark.

Re: Oneway Electrical Info

#9

Re: Oneway Electrical Info

jwoodwright

>Thank you for the quick assist and photo of the plug. John

Re: Oneway Electrical Info

#10

You Are Welcome

Barbara Gill, Remlik VA

>

Re: Oneway Electrical Info

#11

Re: LOL!

Eddie Pacheco; San Jose, Ca.

>Barbara, just the mention of your store got my mouth watering. Too bad you're not within 1/2 hr. driving distance. I hope you, Dan, and the staff are doing fine.

Re: Oneway Electrical Info

#12

Re: LOL!

Barbara Gill, Remlik VA

>Thanks Eddie; everyone is just fine. I hope you will be back to VA some time soon.

Re: Oneway Electrical Info

#13

That would be me, Barbara...

Allen Neighbors

>but I no longer have the pic. My son (an ME)installed the electrical system and installed a locking plug on my 1640, and a 240v receptacle for it.

He said the plug that came on the machine was not up to code for 240v AC.

If I were to do it again, I'd still get him to do it.

Re: Oneway Electrical Info

#14

Re: That would be me, Barbara...

Barbara Gill, Remlik VA

>I knew that Allen but didn't want to put you on the spot. I posted the picture this morning. Thanks. :-)

Re: Oneway Electrical Info

#15

Re: That would be me, Barbara...

Stephen Mushinski

>Allen,

What is an ME ? :)

The plug that is pictured is up to code if you are using a 220v 15amp circuit. As long as the wiring to the panel is of the size to carry 15amps (14 guage, I like to use 12guage in the shop). What your son used is just a twist lock plug/receptacle. Which is used where to do not want them disconnected by accident. There are times I believe they might be mandatory but not for a wood lathe.

Folks, I have mentioned a few times that all electrical wires and fuse panels are rated to protect the wires not the equipment. If you want to protect the equipment then you need fuses/breakers at the equipment end of the wires.

In the above case, the label on the plug means it is rated to an maximum of 15amp. Anymore and damage could occur.

Re: Oneway Electrical Info

#16

Re: Oneway Electrical Info

Stephen Mushinski

>John,

The picture is of a 15amp plug, I am not sure what motor you order so it is hard to say what if any plug will come with it.

Give them a call at Oneway and they will tell you exactly what you need.

Re: Oneway Electrical Info

#17

Re: That would be me, Barbara...

DickL

>>>What is an ME ?

That would be a Mechanical Engineering graduate.

Re: Oneway Electrical Info

#18

25 amp breaker, 15 amp plug?

jwoodwright

>Stephen, Called Oneway and found out on 3 hp they want a 25 amp breaker. This to prevent nuisance tripping. So, if using a 25 amp breaker, why only a 15 amp plug?

Then there was the 2 - 3 amps while the lathe is just spinning and up to 150% (max 200%) while actually cutting.

I appreciate your help. John

Re: Oneway Electrical Info

#19

Jay...

Barbara Gill, Remlik VA

>If you go back to my original post I told you I have a 1640. You said nothing about a 3 HP motor at the time. I don't have a three HP motor.

Re: Oneway Electrical Info

#20

Re: Oneway Electrical Info

Bill Hale / The Wood Spinner

>3 hp on 220 vac will draw only about 10 amps running. I do not know about start current on a motor with ramp up start but I know it will be less than 20 amp.

Run a #12 wire from a 20 amp 240 breaker and you will be fine. This is exactly what I have on my Oneway 3 hp and It has never tripped the breaker.

Good turning and be safe

Bill in CG, AZ.

Re: Oneway Electrical Info

#21

Re: Oneway Electrical Info

jwoodwright

>Thank you Bill.

Did you get the Braking Resistor?

Re: Oneway Electrical Info

#22

Re: Jay...

jwoodwright

>Sorry Barbara. I should have been more clear. I appreciate your help. John

Re: Oneway Electrical Info

#23

Re: 25 amp breaker, 15 amp plug?

Steve Mushinski

>Hello John,

Sorry for the late reply but I was on the road for the last 3 days and didn't get a chance to view WC.

A little math for you.

1 hp = 746 watts

3 hp = 2238 watts

Now the total watts divided by the voltage will give you the current, meaning -

2238/220 = 10.17 amps

There is more to the ratings then this but all we need to know it the basics not all the power factors and efficiency ratings. I am sure someone smarter then me can figure all that out should you wish. :)

Now the general rule of thumb for motors is 125% full load current for fuses. Using a breaker may or may not trip faster then proper fusing as some fuses have a delay for starting and in rush currents.

This is why Oneway says to have a larger breaker for the times the motor need just a little greater current for short periods of time without damaging anything. The VFD looks after protecting the motor and itself from damage.

Therefore:

10.17 * 125 = 15.9 amps

Meaning on should use a 220 volt 20amp plug and receptacle. Now the breaker is back to what I said before. What ever the wire used the breaker needs to be sized to protect the wires. Nothing gets under sized is the key.

Long winded but I hope it help not only yourself but others too!