#1

Need Electrical Info

jwoodwright

>House service is 200a. Main breaker is out back. Inside panel is small and full. House is 10 yrs old.

Is it easier to remove some full size 20a and replace with 20a half-size breakers, thus making space for a 220v / 20a circuit?

The panel is sheet rocked into a chase.

The laundry room is on the other side of the garage. Electric dryer with a 30a receptacle. One idea I had was to connect a dryer appliance cord to an electrical disconnect box equipped with a 20a breaker. #10 4-wire sj cord would be connected to the disconnect and run to the lathe with a 20a / 220v receptacle.

Another idea was to surface mount, the current flush mount dryer receptacle, and run conduit through the garage wall. Connected to the surface mount box and a disconnect box with a 20a breaker on the garage wall.

Another option is to run a new line from the back main breaker. There is space for another line...

Any help will be appreciated. John

Re: Need Electrical Info

#2

Re: Need Electrical Info

Stephen Mushinski

>John,

One misconception I am reading in your question is what is protecting what. The breakers in the panel protect the wire not the equipment. They are sized for the current carrying capacity of the wire not the load of the machine.

The half breakers that you put into one slot can be used to open up room for another two slots for 220. The half breakers just tap one leg of your 220volt circuit meaning you have the same 120 on both breakers not 220. I hope that make sense. Then you can run a dedicated line to your lathe with 20Amp 220Volts. You might have to bust some of the dry wall to do what you want. One reason I would not finish around an electrical panel. Build a cabinet yes but not dry wall.

Your dryer idea doesn't sound legal to me but I could never know what the regulations are everywhere. You would be best to call in someone and get an estimate on the cost to do what you want then you will have a good idea what is needed in your area.

Re: Need Electrical Info

#3

Re: Need Electrical Info

jwoodwright

>Thanks Stephen. I spoke with several Electricians. One wanted to replace the panel and rewire the house as some wires would be too short for the new panel.

#2 wanted $900.00 to put a sub panel next to main panel, trade some breakers over and run 220v line. (10' run)

They expect oil field wages. I don't mind spending cash for a job... just don't want to be taken...

So if you put four 1/2 size breakers, you have space for a full size 220a. Does a 220 breaker attach to two buss bars? If I understand you, any breakers attached to only one buss bar are 110v.

So, the 220v coming into the panel is split.

Ok, time to call another Electrician...

Thank you. John

Re: Need Electrical Info

#4

Re: Need Electrical Info

Stephen Mushinski

>John,

Wow, $900 to run a pony panel and set you up with a 220 volt line to your lathe. Is your lathe in a different county? Where the heck do you live? I think I should move if them's the wages.

You have it right now! A 220 breaker has to hook up to two separate buss bars.

A pony panel is the best way to go so that you can then add circuits at a latter date but not at that price. Contractors must be very busy where you live right now. Sight unseen, I would guess you should be able to get a 10 circuit pony panel put in and the line to the lathe done for well under $500. It is only half a days work at the most and no more then $100 bucks in material.

Good luck,

Steve

Re: Need Electrical Info

#5

Re: Need Electrical Info

Barry Irby

>In order to create enough room for a 220 breaker, you will have to install two half sized beds and mover four existing circuits onto them. That will leave you with two slots open and you can install either a full sized 220 breaker or if you want a "half sized" version of the breed that will give you two 220 circuits. The half sized or mini breakers come in various combinations. Both "sides" can be the same or they can be different. That is, they could be both 15 amps or both 20 amps or it could be one 15 and one 20 amp. Same is true for the 220 version. This option still leaves you with the problem of running the wire to the shop.

I ran my TS for years tapped into the dryer circuit. It was a PITA on laundry day. Firing off the TS would trip the breaker. The panel was in the shop, but I had to walk back into the house to restart the dryer. Does not make you popular when you forget to start the dryer.

Re: Need Electrical Info

#6

Re: Need Electrical Info

Steve Russell

>Hi Steve,

Sounds about right to me... I paid almost $900.00 to an electrician to get a line run from my main breaker box to a new 4-ton A/C unit, plus an outside power breaker box at the compressor. The run was about 25' long. The main copper wire (from the utility company meter to my main 200 amp circuit breaker) in the master circuit box was also replaced at the same time. This wire was around 3' long. With wages like these, maybe I should go to school to be an electrician... :-)

Steve Russell

The Woodlands, Texas

Re: Need Electrical Info

#7

Re: Need Electrical Info

jwoodwright

>Thanks Stephen, that's what I thought, about $500.00. I priced a sub panel and breakers at Home Depot and all came under $60.00. I figured he could do better at the electrical supply and thus everything would be under $100.00. Then $400.00 for labor.

I measured again, the panel is 20 ft from where I want the outlet. The chase stands out from the wall the depth of the panel. So the sub can virtually be side by side. Just cut away a section of sheet rock on the side.

Thanks guys. Monday, I'll call some other electricians. John

Re: Need Electrical Info

#8

Re: Need Electrical Info

Gary Evans Tallassee, TN

>I like the idea of coming off the main breaker unless it is a long way from the garage. That way you could put a subpanel in the garage with lots of circuits available. Since it looks like the garage is in the process of being converted into your woodshop, you'll probably need more circuits. 8^]

Gary

Re: Need Electrical Info

#9

Re: Need Electrical Info

jwoodwright

>Thanks everyone. Gary, it's a little over 50 feet to the outside main breaker. In the garage, the panel is 20 ft away. I have a Thomas and Betts panel and breakers. Best plan is a sub-panel. Pull off sheet rock on side and connect them up. This will give me the required outlet and as was suggested, additional power for the shop.

Be nice to have some "drop" outlet cords. Reach up and plug in for portable tools... John

Re: Need Electrical Info

#10

Re: Need Electrical Info

Bill Hale / The Wood Spinner

>Do it yourself.

Change 4 of the breakers in your panel to twins, easy. Add a 100 amp 220 vac breaker, easy. Run conduit or easier armored flex cable to a new 100 amp panel in the shop and do your shop stuff from there. If you have a Lowe's or any good electrical store they can direct you how to do it. Home Depots have a display that shows how to do it.

Ask friends if any of them have done electrical. If you have local city etc. electrical inspectors ask them for help and get it inspected. These guys are there to help you and to be sure what you do is safe. On a sub panel the ground bars must be split and the white wires to one side and the bare copper wire to the other.

It is not all that hard.

Good turning and be safe

Bill in CG, AZ.

Re: Need Electrical Info

#11

Re: Need Electrical Info

Gary Evans Tallassee, TN

>In that case I agree with the consensus. A sub-panel off your main box is the way to go.

Gary

Re: Need Electrical Info

#12

Re: Need Electrical Info

Jerry Whitaker

>John.....buy everything you need (sub-panel, breakers, outlete boxes & wire)at one of the box stores. Install the sub-panel and run all the wires and hook them up. You can hardly go wrong doing this. Just make sure you have the ground wires in the right place, hook the white wires to the silver terminals, the black wires to the gold terminals. You will need 3 with ground for the 220. If you feel uncomfortable about hooking the sub-anel to the main panel, then call an electrician to do that and have him inspect your work before he does this. I don't know about where you live but here, the city building inspector knows nothing about electricity. When I had my house built, I was on site when the electrical inspector came to check everything before the dry wall was installed. I asked him some questions and he could not answer them. The city is just intrested in their building permit fees. Scary....... If you have a university where you live, I'll bet you can call the maintenance department and get a certified electrician there to do it for you after hours for a lot cheaper. That is what I do when I am not sure about something. Good luck on keeping the price in check.

Re: Need Electrical Info

#13

Re: Need Electrical Info

Fog Tanner

>I went through the same thing when I built my model airplane workshop. I added a quad 60amp breaker on the main service panel on the house and went underground to a my model airplane workshop to a sub panel.

When I later built a garage/workshop/studio (depending on the price of the piece), I had need for a lot more power to it. I added a sub panel off the main service panel, replaced the 60 amp quad with a 100 amp to the subpanel. I then ran underground to my GWS to another subpanel. All the wiring is more to code than the local contractors would do, and a whole lot less. Last time I had an electrican run any wire I had to follow up and fix his shortcuts and mistakes. Will never make that mistake again.

Took about a day to add the subpanel, dig the trench for the conduit and run the wire. The most expensive part is the copper wire, it was spot prices when I bought mine. The subpanels and breakers are the cheapest part of the whole deal. And the total was a lot cheaper than the $900, plus I got to spend a day with my daughter so it was worth a lot mroe than that.

All my 220 machines are on dedicated circuits, except for the mig weleder and plasma cutter. But only one of those is on and in use at a time.

Re: Need Electrical Info

#14

Re: Need Electrical Info

jwoodwright

>Thank you Bill and Jerry. Some great idesa. The breakers are Thomas & Betts and are no longe available.

Did look at Home Depot and Lowes and looks simple enough. Just have an Electrician tie it in... John