What size circuit breaker do I need for a 3520?

Posts

What size circuit breaker do I need for a 3520?

#1

What size circuit breaker do I need for a 3520?

Ron in Drums PA

>Just curious?

Re: What size circuit breaker do I need for a 3520?

#2

Re: What size circuit breaker do I need for a 3520

Bill Hale / The Wood Spinner

>Ron I don't know what size the motor is but follow as below.

1 - 2 hp 110 vac 20 amp 12 wire

1 - 3 hp 220 vac 20 amp 12 wire 3 conductor

Bill in CG, AZ

Re: What size circuit breaker do I need for a 3520?

#3

Re: What size circuit breaker do I need for a 3520

Bruce McElhaney

>I use a 20 amp breaker on my 3520a.

Re: What size circuit breaker do I need for a 3520?

#4

Thanks

Ron in Drums PA

>

Re: What size circuit breaker do I need for a 3520?

#5

Future Gloat?

Dennis Yoder

>

Re: What size circuit breaker do I need for a 3520?

#6

Re: Extra Wire

Mark Mandell - Gone Round In Jersey

>Bill,

There is no reason for pulling a 3-conductor wire for a 220 machine circuit unless you will be pulling a 110 branch off at the end. In a regular 220 circuit 2 conductors plus ground is correct wiring as both conductors are hot, and a third (the white - common lead with black & red as hots) must be capped off at both ends.

At the price of copper these days, there's no point in putting more $$ in your wiring than you have to.

mm

Re: What size circuit breaker do I need for a 3520?

#7

Re: Extra Wire

Ron in Drums PA

>Unless of course its code.

Re: What size circuit breaker do I need for a 3520?

#8

Re: Future Gloat?

Ron in Drums PA

>I don't want you to think I'm ignoring you.

I've been trying to email you, AOL has me blocked and has promised 3 times to remove the block.

Re: What size circuit breaker do I need for a 3520?

#9

Re: Code

Mark Mandell - Gone Round In Jersey

>Ron,

If somebody's telling you that PA code requires 3-conductors plus ground on all 220 circuits, you'd best check with your Inspections office and ask for a copy of the Code section. Unless PA has changed its code on residential wiring, there was no such requirement when last I looked.

mm

Re: What size circuit breaker do I need for a 3520?

#10

Re: Code

Ron in Drums PA

>The code is in the process of being rewritten and will change next year. Might as will do it the new way. Besides, the difference between 12-2 and 12-3 is not that big a jump, maybe $20 at the most.

Re: What size circuit breaker do I need for a 3520?

#11

Re: Code

Allen Neighbors

>I have 12-2 with Ground on my 240v AC circuit. Our code calls for a 30Amp circuit.

Mark, I believe on 12-3 the extra wire acts as either an additional neutral or ground... I've never seen them capped off on both ends.

Re: What size circuit breaker do I need for a 3520?

#12

Re: Code

Mark Mandell - Gone Round In Jersey

>Allen,

It is, in fact a neutral (or "common") insulated conductor, but is not used in a 220 application. It is not used as a ground which is the bare wire, just as the ground wire is never to be used as the common; one is an insulated conductor that carries current back to the box, whereas the other is not. A common or neutral is only used in a 3-wire 220 circuit when a 110 branch is split off using one of the hot leads (red or black) and the white wire. Unless that is done, "code" requires that any unconnected wire (the white) be capped both at the outlet box and in the service panel so that the wire cannot make contact with energized wire or terminals.

Why PA is changing its code to require an unused conductor to be included in the cable is beyond my limited understanding as there is nothing to which it can be connected unless they're going to be requiring that all 220 motors be rewired in some fashion to use another conductor and then also change all the plugs and sockets to 4-wire devices. A 220 circuit uses only two hot leads and the ground wire. Normal installation is thus to "reflag" the white wire in a 2-wire (B/W)+ ground cable to be a black hot lead.

mm

Re: What size circuit breaker do I need for a 3520?

#13

Re: Code

eaglesc

>Electricity is akin to magic to me but IIRC aren't some of the newer dryer(220) recepticles 4 prong?

That might be the reason for the fourth wire.

Hey I am only a pen turner,what do I know?:>)

Re: What size circuit breaker do I need for a 3520?

#14

Re: 4-wire

Mark Mandell - Gone Round In Jersey

>Eagle,

I'm told the 4-wire units (3 conductors + ground) use the 220 circuit for the heating element and drum motor, and a 110 branch for the timer. Hense you need the 3rd conductor as described to get 110 for that clock.

Besides, I'll take your pen-turning knowledge over my electrical savy any day.

mm

Re: What size circuit breaker do I need for a 3520?

#15

Re: 4-wire

eaglesc

>"Hense you need the 3rd conductor as described to get 110 for that clock."

But they used to run a clock on 220 plugs (3 prong) without the 4th wire.

as I said I am not even a neophyte in this field.I know enough to be dangerous.

I work in construction and these are things I have noticed.

The electricians are not usually there when the HVAC guys are.

These new plugs are some I have noticed in the electrical Dept at the Borgs.

Re: What size circuit breaker do I need for a 3520?

#16

Re: What size circuit breaker do I need for a 3520

Jerry Whitaker

>Me too using 12-2 wire