>I have wired up many 15 and 20 amp circuits on my own. Even added a sub panel for a 30 amp circuit in my old home without killing anyone. Trying to do that again in my garage so I can run my tablesaw which requires 220v/30a service. Wanted to run this by you to make sure I have it right.

The distance is not long, maybe 75 feet total and there will be only a single receptacle on this circuit. I ran 12/3 wire. I purchased a double pole 30 amp breaker. The ground and the white neutral wire both go into the neutral/ground bus bar in the panel. The black and red each go to one of the poles on the breaker.

The tablesaw has a 3 wire cord running out of it, white/black/green.

The receptacle is a 3 prong type. The bare ground gets wired to the metal box. The white neutral goes to the ground terminal in the receptacle. Red and black each go to one of the other prongs as they are hots.

From the tablesaw; black and white are both hot and go to the hot terminals matching the receptacle. Green goes to the ground prong.

I'm no pro at this - you won't hurt my feelings by telling me I have something wrong, and you may save my life! I think if anything I have backwards are the neutral and ground but you tell me, please. Thank you.

Re: Electrical question if you don't mind please

#2

Whoops. Intended for main messages forum

Mike Schwing from Md.

>But you guys know your stuff, too, so I'll leave it here. Thanks!

Re: Electrical question if you don't mind please

#3

Re: Electrical question if you don't mind please

Don Evans

>I see two things right off the bat!

First, you have the wrong size wire mated with the wrong size circuit breaker. Number 12 wire should have 20 amp breaker NOT 30.

If you need 30 amp supply you'll need to pull new wire #10.

The other thing is the white and ground wires, in a 220 circuit like you are doing the white wire is NOT used, so you should disconnect it at both ends and put wire nut on each end. Just leave them in the box at both ends not connected, the wire nuts are to insure it doesn't touch anything.

The ground wire should be brought into the receptical box and 2 pigtail's wire nutted to it, one of them will goes to the ground prong on the receptical and other will go to the box that is holding the receptical. If this box is plastic, then you don't need to ground it and you can just run the bare ground wire to the receptical only.

Yes, the black and red are both hot and sounds like you have them correct.

Make sure the breaker used is for 220. Not 2 110 breakers.

Re: Electrical question if you don't mind please

#4

Re: Electrical question if you don't mind please

Mike Schwing from Md.

>Thanks Don. I have read in two electrical books recently that 12/3 can be used for up to 30 amp service. I'm no expert though, as stated. I'll go with your directions on the ground/neutral, and thank you for the reply. This saw doesn't need 30, in fact I called Jet and they said its max draw was 20. The only other thing I may run on this is a lathe, but of course not concurrently.

Re: Electrical question if you don't mind please

#5

Re: Kick It Up A Notch

Mark Mandell - Gone Round In Jersey

>Hey Mike,

12/3 is too light for a 30 amp circuit, especially 75 feet long. Code calls for #10 wire above 25 amps. Since this is a "home run" single outlet circuit, check your motor's draw; 25 amp and #12 wire might be enough. Also, don't forget you need to run that wire in conduit where it is "outside the structure" (not enclosed in the wall).

Make sure that your plug and receptical are rated for the circuits' amp rating and that they match.

On a single-use 220 circuit, you can save yourself a few bucks by running 10/2 with ground [3 wires - black, white, bare]; ground goes to ground, black and white go to your breaker. Just to be a good god, reflag your white wire with black tape at both ends. The only time I use 3+ ground wire on 220 is when I might pull a subservient 110 circuit off the end and so need that extra common wire in the terminal box.

Hope this helps

mm

Re: Electrical question if you don't mind please

#6

Re: Electrical question if you don't mind please

Don Evans

>Mike:

I went back and read you message and I see you did state you need 30 amp.

So you'll need to replace the wire but you don't need 10/3 with ground, you can get by with purchasing 10/2 with ground. This will have a black, white and bare ground wire. You use the white in that case as a hot wire. Just put black tape about an inch of it on the white insulation at both ends. The tape indicates that it is now a black wire and runs from one of the breakers to one of the hot prongs on the receptical.

Don

Re: Electrical question if you don't mind please

#7

Re: Kick It Up A Notch

Mike Schwing from Md.

>Well since both of you are questioning the wire choice I'll re-pull with 10/2 and keep the 12/3 in place for 110 service on that side. Fortunately I have 10/2 in house or this would be getting expensive! I was hoping to save it for a future project.

Thanks men!

Re: Electrical question if you don't mind please

#8

PS - Wrong Wire

Mark Mandell - Gone Round In Jersey

>Just reread your post. You DO NOT WIRE THE WHITE TO A GROUND TERMINAL!! The bare ground does connect to your box, but it also connects to your receptical's grounding stud. As mentioned, a white insulated conducter is not used in this application; must be capped at both ends.

mm

Re: Electrical question if you don't mind please

#9

Re: Electrical question if you don't mind please

Gerry Meekins

>Mike,

You�ve got good advice on the wiring so I won�t chime in on that.

I�m glad to see you getting your table saw up and running and I sure hope you plug that lathe in and start doing some spinnie stuff again�

Gerry

Re: Electrical question if you don't mind please

#10

What Lathe?

Charlie Anderson

>

Re: Electrical question if you don't mind please

#11

Re: Electrical question if you don't mind please

Mik eSchwing from Maryland

>Thanks Gerry. Charlie's right - what lathe? I need to get another. But I had to get the tablesaw running so I could build out some shop benches so that I could have a place to put my lathe! Step by step I get closer.

Re: Electrical question if you don't mind please

#12

Stubby's don't take much room Mike!

Gerry Meekins

>

Re: Electrical question if you don't mind please

#13

Re: Electrical question if you don't mind please

Bill Hale

>All are correct. Per your note 20 is all you will draw it will work.

The problem comes in if you have a fire for any reason electrical or not. The Insurance inspector can come in and see a #12 to a 30 amp breaker and tell you you get nothing because it was not wired to code.

It is that simple ! Use a # 10

Good turning and be safe

Bill in Show Low AZ.