seeking electrical advice

#1

seeking electrical advice

john pickett

>This sounds logical to me. However I have only done basic wiring.

My shop is in an underpowered garage in my rented home. I have a lathe, shop smith, grinder mini late, and hand power tools. So far I have been able to get by, but I really need a dedicated circuit for my shop smith.

There is a 220 dryer outlet in the utility room. Since I don�t have an electric dryer, it is not being used.

I was thinking that I could get a dryer plug & cable, wire each hot into a separate outlet and have two extra circuits to pull to the shop.

What do you think?

Re: seeking electrical advice

#2

JL

Re: seeking electrical advice

JL

>How many amps is the drier circuit? You could alway just use the circuit to power a small sub panel.

Re: seeking electrical advice

#3

Re: seeking electrical advice

phil in NJ

>Caveat: not an electrician.

A few things though:

- the circuit will be a 2-pole ciruit with a common trip breaker. What this means is that if either hot leg's breaker trips, it trips both.

- the receptacle may or may not have a neutral. If the receptacle has 4 pins, you at least have a neutral. If it doesn't, you certainly can't split it (don't be tempted to use the ground as a neutral!)

- it is likely the breaker is a 30A 2 pole breaker. Meaning that the breaker isn't going to trip at a low enough setting to protect

20A or 15A receptacles or cords you plug into it.

I can't say if it technically violates code, but certainly doesn't sound like a good idea.

-Phil

Re: seeking electrical advice

#4

Re: seeking electrical advice

Ralph

>It can be done...

How I would do it:

1) Get your property owner to buy off on the work.

2) Get your property owner to pay for the parts.

3) Buy a sub-panel, wires, breaker, etc

4) Run the two hot and neutral wires from the outlet to the sub-panel.

Note the sub-panel neutral must be isolated from the ground/box.

5) Run a ground wire from the sub-panel, to a real ground.

6) Put two 20amp/110 breakers in the sub-panel and wire your circuits from there.

This will not pass code, but it will be as close as you can get, without running the circuit direct from main-panel.

Re: seeking electrical advice

#5

Re: seeking electrical advice

Bill Hale / The Wood Spinner

>John

Yes what you say does violate code.

What you could dp is to buy a small sub pannel that has spaces for multipal breakers. Turn off the power to the dryer plug It should be a 30 amp double pole breaker. Mount the pannel over the old plug location and pull the wires in to the pannel and attach to the proper lugs. If the old plug does not have 4 wires you will need to pull a ground wire.

Now you can mount your duplexes under the pannel and wire them to single 20 amp breakers. If you are the only one using the shop you should be OK with 3 120 20 amp circuits.

Bill

Re: seeking electrical advice

#6

Re: seeking electrical advice

Brent English

>Don't do it unless you do the subpanel idea with 110 volt breakers rated at less than 1/2 the 220 volt breaker size. Even then you'll need the extra neutral, which is an extra wire to pull. But then, since the outlet is probably a hardwire back to the main panel and not a conduit run, you won't be able to do that anyway.

As a former renter who once set up a blacksmith shop in an attached garage - running the smoke stack out the window and pi$$ing off my landloard big time - I feel your pain.

Anyway, play it safe while you rent, plug and unplug stuff. Save your dough and get your own place, or have a qualified electrician come in and do it right - running some new 110 volt to the shop space. Clear it with your landlord or you might be looking for a new place....Not that I'd know anything about that...

Re: seeking electrical advice

#7

Re: seeking electrical advice

Ralph

>"Don't do it unless you do the subpanel idea with 110 volt breakers rated at less than 1/2 the 220 volt breaker"

Brent, I assume you mean power and not amps..

30amp@220 is 6600 watts

2 each 20amp@110 is 4400 watts

My 60amp shop sub-panel has 1 each 30@220V, 1 each 20@220V and 2 each 20@110V, and I am still in code (the code assumption is that not all the circuits are at max, at the same time, or why you can have way over 200amps of circuits on a 200 amp service entry)

Re: seeking electrical advice

#8

Dick Hines

Re: seeking electrical advice

Dick Hines

>Why not replace the 220 breaker with 2 110 breakers. Then you could run a couple of GFR's off each breaker.

Since it's not your house be very careful. Your land lord may get reall pi---d if you burn his house down.

Re: seeking electrical advice

#9

Re: seeking electrical advice

Bob Fawcett

>IF you have a 4 wire plug, this is what I would do.

1. Get a small breaker box with space for 4 or more breakers.

2. Get a 4 wire drier plug to match the outlet.

3. Get a lenght of 10/4 SJ cable from the borg or other local supply.

4. Wire your drier plug to one end and the breaker box to the other.

5. Get 120 outlets if that is what you want and mount them in the single outlet aluminum outdoor boxes which you attach to the breakere box with short conduit or outdoor connectors. Wire these to the 2 new 120 breakers you intall in the breaker box.

You now have a 2 circuit 120 box that you can just plug into the drier outlet and use with proper 120 breakers for each circuit.

I would not do this if the plug is not 4 wire.