>Yesterday I noticed my power strip LED was flickering so I got my multi-meter and began to monitor my line voltage. At 5 pm my voltage was down to 107. A little while later it was down to 105; then at about 9pm it was down to 101. I called the power company and they are coming out to check the lines to this area. Does anyone know how low the voltage can get before damaging motors and such? We are dealing with 100 degree temps for at least 2 more days.
>.... is the concern when voltage drops. I remember many times during my RVing days that the AC would shut off (hopefully or not!!) when voltage dropped to 105 or below, and you run the chance of overheating most motors under load at 105 v. according to several makers.
>Check a bunch of other outlets when you notice a low reading at one. The idea is to get one on the other side of the neutral. If it is very high when the other is very low, then you have a bad neutral problem.
You can also check the 240V. It should be around 240V and if it is it points to a bad neutral. If it is only double the low reading, then the supply to your house is likely faulty.
>After a nearby lightening strike several years ago, I went through 3 burglar alarm panels, a HVAC transformer, and several AC adaptors before I was smart enough to check the line voltage.
The strike had damaged the power company's transformer, and I was getting over 140 volts on each 110 volt leg. It was then that I realized that many things that did not die from the strike itself and that did not normally buzz were buzzing and the lights in the shop were definitely brighter.
I was not as bright as my lights. I thought that lightening only killed transformers.
Power company fixed the transformer quickly, but I had to foot the bill for my losses. Live and learn.
>Bill, can an unbalanced load be checked at the breaker box? Between neutral and either one of the hots? Or does it have to be at an outlet. I am not an electrician, but it seems it would be easier to check at the panel if it's possible.
>Both lines measured 101 volts and the 230 was also very low. I called the power company and reported it and they came out immediately. The voltage this morning was 112 but it starts dropping when everyone gets home and kicks the A/C to high and turn the stoves on. The power company replaced my transformer but they said the problem is at the substation and they are looking into what has to be done there. He said the transformer feeding my area is at max. Too many new houses have been built recently and the electric company has not kept up with the growth but the tax assessor has been right on top of it.
>Checking at the breaker box would tell you if the problem came from the utility company (or the service entrance or the breaker box itself). If that was OK and the outlet was not, the problem is in the house wiring. However, if the breaker box reads fine and the outlet has reduced voltage, I'd look quick for a bad connection with high resistance (poor contact somewhere) in the house wiring since that connection is likely overheating and could start a fire. However, low voltage is more likely to be coming from outside the house.
BTW, when high demand such as daytime air conditioning use during a heat wave stretches the capacity of the utility (hydro and steam generators around here), ESPECIALLY when accompanied by equipment failure which unfortunately is more likely during extreme loads, they have two options. One, if the excess load is minor or of short duration they can reduce the frequency from 60 cycles per second (in the US) to something less. In that case, they "catch up" later such as at night when the load is less - this keeps things like clocks that sync to the frequency on time. The average frequency over the day will be correct. The other option is to reduce the voltage, resulting in a so-called "brownout". If the load demand is severe, the brownout the only recourse short of a blackout. (I am certainly no expert but this is the way it was explained to me years ago.) At the national laboratory where I worked until I retired, banks of huge generators stood by to automatically pick up the load to critical computing and laboratory systems if needed.
>JKJ, pretty well explained it. I said receptacles because I wasn't sure if the OP would be comfortable pulling the cover off the panel. The result would be the same if the main neutral was bad however by checking at the plug you are measuring the effect of any bad connections. However, to get the picture of what is going on in that case you would have to check both at the panel and the receptacles to see the difference. Hope this makes sense.
>Hey TD, I retired from Georgia Power and what they say is ok is 120 volts phase to ground + or - 5% the same goes for 240 volts phase to phase + or - 5%. 114 to 126 phase to ground and 228 volts to 252 volts phase to phase. They also say 6% flicker or inrush is ok but I would not want to have that much. If it's Ga Power they should fix it for you if it's out side these guide lines
>I am on EMC. I have 114 volts in the mornings and down to 101 by bedtime. At 5 today I had 214-216 on the 230 buss and 107-108 on the outlets. They are coming in the morning to install a regulator to boost my voltage. Until the voltage is above 110/220 I do not plan to run any motors other than one small (6000btu) A/C unit. Thanks for your help.