Re: New Jet lathe question
Rick Christopherson
>Hi Alfred,
Ellis Walentine asked me to stop over here and look into your question. The reason why your lathe is tripping the GFCI outlet is most likely due to the starting capacitors. The capacitors are kind of like a battery in that they store some electrical energy for a short period and release it a short time later (so is the motor too). Because a GFCI outlet works by comparing the current in the two wires feeding the motor, there is an instantaneous time period where the two currents are not exactly equal. This causes the GFCI to trip.
GFCI�s are there to protect the operator when he/she is plugging/unplugging the device. They are not necessarily there to protect the operator while the device is running. Granted, GFCI�s in bathrooms and such are in fact intended to protect the user even after the tool is plugged in, but when it comes to larger tools, this is not necessarily the case.
Your best bet is to remove the GFCI protection from this single outlet, however, I believe I also read that you were not able to isolate this single outlet without removing all of the GFCI protection in the whole shop. So that may not be a good choice.
More modern and sophisticated outlets can actually account for these conditions and hold off on their trip point until they are sure the cause is not from a motor-type load. Your next solution would be to buy a better quality GFCI outlet and replace the original. Try to locate one that is rated for light motor loads. I don�t know if you can find these at home centers, so you may have to go to an electrical supply outfit.