>I need a special plug. Here's a picture of the outlet that's on the wall and one of the cord for the General.
I know I need a new plug plate (or whatever it's called), can I use this outlet? Is there any wiring change I need to do? I have no idea what this outlet was used for but am assuming it will work.
>Ruth, Take a look at this site. It looks like your plug is a NEMA 6-15P and the receptical is 6-50R. I don't think you want change a 50 amp circuit to 15/20 amp unless you change the breaker.
>First, I didn't realize how blurry the picture of the plug is, sorry about that.
Stuart, does that mean I can't or shouldn't do it myself? I know Dinyar said he just got someone but I'm in a hurry (as usual!). Of course, I don't want to be in such a hurry that I burn my shop down before it's even built!
>ruth, since you are in a hurry, go to hd or lowes or whatever you have around. get a plug to fit the wall socket and a socket to fit the plug on the general. also pick up 2 feet of 10/3 wire make a short extention cord with socket and plug. then they fit together and nothing has to be modified.
>The socket was probably for a dryer. You could use it for the General, but a 50 amp circuit (if it is) is too big. You could change the breaker at the panel to 15 amp and be safe for the General. If someone plugs a dryer in later, it will just kick the undersized breaker.
>Ruth....I would first get a voltage meter to see if you do in fact have power there unless you already know for sure. The hole in the middle is the ground and the other two are the 120v leads. When you connect the meter, one probe to the ground and the other to one of the 120v leads, each one should register approximately 120v. I cannot tell from the picture of the plug but if it is a nice moulded plug on your lathe, I would replace the receptical to match even though this is probably not the most economical way to do it. Then, like someone else mentioned, switch out the breaker to a 20 amp. Was good to see you at SWAT.....hope to see you there again next year with a bunch more of the WC folks.
>The lathe motor isn't going to draw more power than it needs, so using a 50 amp service won't do any harm. The electricity is the same whether it goes through a 15 amp or a 200 amp breaker, it's just a matter when the breaker trips.
>I am no electrician but the breaker is to protect the wires not a motor etc. The breaker is matched to the guage wire.
be real careful when you put the VOM meter in that socket 220V can really hurt or kill you. Unless you are familiar with the meter and electricity you should find at least a friend that has some experiance. The best of course is an electrician.
If you have some skills the easiest thing is to buy a pigtail for a dryer at HD and wire a female plug that matches your lathe. I have made an extension cord like this. Expect the pigtail to be $10 and the plug $5.
>Ken, Couldn't the motor draw more than it should if it is stalled? I'm actually guilty of using a 50 amp circuit with a homemade extention box and have not had any problems.
>If you are comfortable working with electical outlets I don't see any reason why you can't do it yourself. You need to make certain just what is coming into the outlet and then be sure the breaker is off before you do anything.
I do my own electrical work but I turn off the breaker and then test the line just be be sure. I've been know to turn off both the line breaker and the main breaker. I do wear a belt and suspenders.
>> I don't think you want change a 50 amp circuit to 15/20 amp unless you change the breaker.
There is no need to change either the wire or the breaker. Just cobble together an interface (safely).
Every single person uses 15 and 20 amp 120V circuits every day with loads that are often much less than even 5% of the capacity of the circuit (3 HP motor on 50A circuit is about 30%)—e.g., clock radios, reading lights, toothbrush chargers, etc.
>Ruth I tend to agree with Bob, Stuart Adrien, if you have a problem with the lathe under load or whatever it wont pop the breaker till it hits 50amps. That could be to late for the motor, just a thought. Also if your messin with any wires make sure each leg of the 220 isn't on a sepperate breaker, mine is.
>Lan's suggestion is a good one. Make an extension cord with a male plug to fit the existing outlet and a female plug to match the General and you are in business. Your lathe has overload protection built in so don't worry about the size of the breaker.
>A friend of mine, who is not at all PC, calles this tyep plug a "Jap" plug because of the horizontal blades. You can get them at the big box stores. Of course you need both the male and female parts. I am not sure if they are 115 or 230
Ruth's plug (the thing on the end of the cord attached to the General) is a 6-15P. That means 15A. (Prefix of "5" means 120V, "6" means 240V)
6-15P
A 6-20P has one blade horizontal and the other vertical…
6-20P
…much like a 5-20P, except the opposite blade. (note the "W" which indicates the blade with the white, or neutral, wire attached. There is no neutral on three wire 240V circuits)
5-20P
The receptacle, as has previously been stated, is a 6-50R
>I use the 20 amp receptacle which will accept either the 15 amp or the 20 amp plug. Ruth's is as you stated, a 15 amp. She can use the 20 amp receptacle as it will accept the 15 amp plug or a 20 amp.
>Every single person uses 15 and 20 amp 120V circuits every day with loads that are often much less than even 5% of the capacity of the circuit (3 HP motor on 50A circuit is about 30%)�e.g., clock radios, reading lights, toothbrush chargers, etc.
True enough Rod but may I suggest an experiment.
Take the cover off of any 50A receptacle. Next take a single piece of #12, either from a scrap of romex or a short piece of THHN stranded a foot long or so and strip the ends as you would if you were going to attach them to a light fixture or switch or whatever. Now touch one end to either of the hot sides and another end to ground. My guess is that long before the oversize (for #12 wire) breaker pops, the insulation on the wire is going to start to burn.
I think this is the first time I've disagreed with one of your responses to an electrical question but I REALLY disagree with it. I see no difference in saying an oversize breaker is okay than saying that none are needed along as there is a main. From a mechanical standpoint the ONLY advantage of circuit breakers over fuses is that the average homeowner can not solve the problem of a constantly tripping overloaded 20A breaker by replacing it with a larger size. In the days of residential fuse panels this was SOP. When the largest fuse available still blew it was time to call on the assistance of Mr. Lincoln.
Anyone who uses a 50A breaker for a circuit requiring only a 20A or 30A breaker is, for all practical purposes, sticking a penny in the fuse box. As long as everything works as it should there will be no problems but if something goes wrong it will be time to break out the marshmallows and hot dogs.
Addy protocol: unlicensed (not required in Indiana)electrician with thirty years of experience in residential and commercial wiring as well as over four years as maintenance supervisor for a 160 bed long term healthcare facility.